Question: Can FP be fed out of (2) separate diesel generators via fire pump transfer switch/controller? The first generator also serve building egress emergency panel. The second generator is dedicated to fire pump. Thought NEC requires FP to be fed out of a reliable power source?
You're right to be cautious and question this configuration. Here's a breakdown of the NEC requirements and why your proposed setup needs careful consideration
NEC Requirements for Fire Pump Power
The NEC has specific requirements for the power supply to fire pumps, primarily found in Article 695 (Fire Pumps). Key points include: Reliability
The core principle is that the fire pump power source must be reliable and capable of delivering the necessary power for the pump to operate under fire conditions. This reliability is paramount.
Independent Service or Separate Service
Typically, fire pumps are fed from either: A
service dedicated solely to the fire pump, or A separate service widely separated from the other building service. Emergency Power Acceptance
The NEC does allow for an emergency power source (like a generator) to power a fire pump,
BUT with strict conditions.
Analysis of Your Proposed Configuration
Let's dissect your proposal and see where it might fall short:1. Generator #1 (Emergency Panel & Maybe Fire Pump)
This generator feeds the building's egress emergency panel. This means it's likely sized to handle lighting, exit signs, and perhaps some minimal life safety loads.
Problem
Putting the fire pump on the same generator as other emergency loads can compromise the reliability and capacity dedicated to the fire pump. If the building experiences a fire and the normal power fails, this generator will be heavily loaded. The fire pump's critical load might not get the priority it needs, potentially leading to reduced pressure or failure.2.
Generator #2 (Dedicated Fire Pump)
This generator is dedicated to the fire pump. This is good and aligns with the "reliable power source" principle.
Issue
You mention a "fire pump transfer switch/controller". The critical question is:
How does the system know to switch over to Generator #2 and only supply the fire pump? The transfer switch needs to isolate the fire pump from the main building's normal power and potentially from Generator #1, ensuring it only gets power from its dedicated generator.
Why This Could Be Problematic Under NEC Load Calculations and Capacity
NEC 695 requires specific load calculations to ensure the generator dedicated to the fire pump has sufficient capacity. If the generator is undersized or has other loads connected to it, it could be a violation.
Coordination
The operation of the transfer switch needs to be carefully coordinated. It must switch to the fire pump's generator quickly and reliably.
Testing
The entire system, including both generators, the transfer switch, and the fire pump controller, must be thoroughly tested under load to ensure proper operation. NEC 695 has specific testing requirements.
Signage and Documentation
Clear signage is required to identify the fire pump power source and any associated equipment.
Automatic Starting
Fire pumps should start automatically on loss of normal power. The generator system needs to accommodate this.
What to Do1. Consult with a Qualified Electrical Engineer
This is not a DIY situation. You need an engineer experienced in fire protection systems and NEC requirements. They can perform the necessary load calculations, design the system correctly, and ensure compliance.2.
Review NEC Article 695 Carefully
Understand the specific requirements for fire pump power.3.
Consider a Dedicated Service
The best and most reliable option is often a dedicated electrical service solely for the fire pump. This eliminates the complexities of generators and transfer switches.4.
If Using Generators, Ensure Proper Transfer Switch Operation
The transfer switch must isolate the fire pump from other loads and the main service when the generator is running. It should also be designed to prioritize the fire pump load.5.
Get AHJ Approval
The Authority Having Jurisdiction (AHJ) must approve the fire pump power system. They will have the final say on whether your design meets code.
In summary, while using a generator for a fire pump is possible under the NEC, it's complex and requires strict adherence to the code. Your proposed configuration raises concerns about reliability and capacity, especially with the first generator also serving the building's emergency panel. Seek expert engineering advice to ensure a code-compliant and reliable fire pump power system. Flag for review