Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Refrigeration/HVAC Loads Diversity Factor

User: blake1008205, Location: Powder Springs, GA

Asked on: Tuesday, March 25, 2025 at 2:55 pm EDT
Answered on: Tuesday, March 25, 2025 at 2:56 pm EDT

Question: Hello everyone, I have a job that's getting push back right now on the way I sized the refrigeration/condenser/HVAC loads that need to be backed up by the generator set. I sized all of the loads based on the nameplate on the motors. I used MCA × sqrt 3 x 480 for the 3 phase motor loads and used the MOCP for the breaker sizes. They're telling me I need to use a diversity factor for the loads but I have never used a diversity factor for emergency backed refrigeration/HVAC equipment. I can't find anything in the NEC about it (I did see where it talks about lighting and receptacles but not motor loads), can anyone help me

You're right to be skeptical. Using a diversity factor for emergency backup refrigeration and HVAC loads is generally not best practice, and here's why: Life Safety & Preservation

Refrigeration and HVAC systems, especially in emergency backup scenarios, are often critical for life safety, food preservation, or critical process maintenance. If they lose power during an emergency, relying on a diversity factor that assumes they won't all run at the same time can lead to catastrophic failure. Think: hospitals needing to maintain stable temperatures for medicine or vulnerable patients, data centers needing to cool servers to prevent data loss, food storage relying on consistent cooling.


Emergency Operation vs. Normal Operation

Diversity factors are typically applied during normal operation where loads are known to cycle and not always be fully loaded simultaneously. Emergency power systems are meant to handle peak demand under the worst-case scenario. If you're sizing a generator for peak demand, you need to assume everything will be running at (or near) its full nameplate load.

Starting Current

Motors, particularly large ones, draw significantly more current when starting than when running at full load. This is called "inrush current" or "locked rotor current" (LRA). Your generator needs to be sized to handle this starting current in addition to the running load of all the other equipment. Using a diversity factor drastically underestimates the generator's required capacity to handle these simultaneous starts.

Here's a breakdown of why your approach is generally correct and how to defend it


Code Requirements (NEC)

While the NEC (National Electrical Code) does allow diversity factors for certain applications (like dwelling unit service calculations or feeder calculations for general lighting and receptacles - Article 220), it's far more cautious when it comes to emergency systems.

NEC 700 (Emergency Systems), 701 (Legally Required Standby Systems), and 702 (Optional Standby Systems)
are the relevant articles. These sections emphasize reliability and the ability to supply the entire connected load. Look for language that prioritizes ensuring proper operation during outages. There will be no mention of using diversity factors in these sections of the code. Focus on Full Load Current

The code mandates you consider the full load current of motors. You are correct using the MCA.

Generator Sizing

The NEC guides generator sizing, but it doesn't give a simple formula. It focuses on making sure the generator can handle the load and starting currents.


IEEE 446 (Recommended Practice for Emergency and Standby Power Systems)
is another resource. It also leans heavily toward full load consideration and safe generator sizing.2. Your Calculation Method



Using Nameplate Data

Basing your calculations on the motor nameplate data (MCA and MOCP) is the
most conservative and generally safest approach for emergency backup. It ensures the generator can supply the maximum possible load.

MCA

The Minimum Circuit Ampacity (MCA) accounts for the motor's full load current plus any safety factors required by the code.

MOCP

The Maximum Overcurrent Protection (MOCP) rating helps ensure the circuit breakers are adequately sized to protect the motor from overload and short circuits. It's not directly used in generator sizing (the MCA is more relevant), but it gives you an idea of the circuit's capacity.


Three-Phase Formula

Your calculation of MCA × sqrt(3) × 480V is correct for determining the total current for a three-phase motor load.3.

Defending Your Design



Justify the Criticality

Emphasize the
critical nature of the refrigeration and HVAC loads. Explain why these systems must operate reliably during an emergency. Refer to potential consequences of failure (e.g., food spoilage, medical equipment malfunction, data center overheating).

"Worst-Case Scenario" Rationale

Explain that you're designing for the "worst-case scenario," where all refrigeration and HVAC equipment is running simultaneously at full load during the emergency. This is the safest approach.

Code Compliance

While the code doesn't explicitly
forbid diversity factors, you can argue that your method is more conservative and ensures compliance with the spirit of NEC 700, 701, and 702, which emphasize reliability and full load capacity.

Starting Current/LRA

Show how you've considered the starting current of the largest motor(s). This is crucial. The generator needs enough capacity to handle the inrush current without voltage sag that could trip other loads.

Manufacturer Recommendations

Consult the generator manufacturer's literature for guidance on sizing for motor loads. They often have specific recommendations on derating factors or oversizing to handle motor starting.


Redundancy (If Applicable)

If your system includes any redundancy (e.g., multiple refrigeration units where only some are essential), you might be able to justify a small diversity factor, but only for the non-essential redundant units. The essential units should be sized for full load.4.

What to Ask the Push-Back



"What diversity factor are you suggesting, and what is the
basis for that diversity factor?"
Make them justify their number. Where did it come from? What data supports it? "What is the acceptable risk of failure if the diversity factor is incorrectly applied?" Put the onus on them to own the potential consequences. "How does the proposed diversity factor account for motor starting current?" They will likely have a hard time answering this. "How does using a diversity factor ensure reliable operation of critical equipment during a prolonged power outage?"Example Scenario and Argument

"We are backing up refrigeration equipment in a hospital pharmacy. These units store temperature-sensitive medications vital to patient care. A power outage could compromise the medications, leading to delays in treatment, potential patient harm, and significant financial losses. Therefore, it is critical to ensure these units operate continuously at full capacity during an emergency. Using nameplate ratings provides a conservative approach that accounts for the maximum possible load, ensuring the generator can supply the necessary power without risking equipment failure or medication spoilage. While NEC allows diversity factors under certain circumstances, the emergency system's reliable operation takes precedence here. Our design minimizes risk, aligns with best practices for critical environments, and prioritizes the safety and well-being of patients."

In Conclusion:


Stick to your guns. You are on solid ground using nameplate data for emergency backup of critical refrigeration and HVAC equipment. Focus on the criticality of the loads, the importance of reliable operation, and the potential consequences of failure. Make sure you've addressed motor starting current. Force the people pushing back to justify their suggested diversity factor with data and a clear understanding of the risks involved. Flag for review

Previous Question Next Question