Question: Would like to use DLO cable on the Panelboard. The MCBS call for 37 strand cable. Do I replace cage lugs with bolt on lugs and crimped connector? Or can I use the DLO in the standard cage lugs

Let's break down the situation and the best course of action

Understanding the Issue
DLO Cable (Diesel Locomotive Cable)

DLO is highly flexible, fine-stranded cable designed for demanding applications like locomotive wiring and battery connections. It's often used where flexibility and high current capacity are needed.


Panelboard MCBs and Cage Lugs

Most panelboard Miniature Circuit Breakers (MCBs) and their associated cage lugs are designed for standard building wire (THHN, THWN, etc.). These wires have fewer, thicker strands.

Strand Count Mismatch

Your MCBs are rated for 37 strand cable and DLO has significantly more strands. The issue is whether the cage lug can adequately clamp down on the finer strands of the DLO cable and maintain a secure, reliable, and safe connection.

Why Directly Using DLO in Cage Lugs Can Be Problematic
1. Poor Contact

The many fine strands of DLO can spread out within the cage lug. The clamping force might not be evenly distributed across all strands, leading to:
Reduced contact area. Increased resistance at the connection. Overheating (a major fire hazard). Voltage drop.2.

Strand Breakage

The sharp edges of the cage lug's clamping mechanism can damage or break the fine strands of the DLO over time, further reducing the connection's integrity.3.

Code Compliance

Using a connector or termination method not specifically listed or tested for the application could violate electrical codes (like the NEC in the US).4.

MCB Listing

The MCB is designed to be listed with specific terminal configurations. Changing this by forcing a different termination could nullify it's listing.

Possible Solutions


Here are the best options, in order of preference:1. Preferred: Use Listed Connectors (Most Reliable and Code-Compliant)
Option A: Pin Terminals (Ferrules)

Use insulated pin terminals (ferrules) specifically designed for fine-stranded conductors. Crimp the ferrule onto the DLO cable using a proper crimping tool that provides the correct pressure and shape for the ferrule and the DLO wire size. Insert the ferrule into the cage lug of the MCB.

Key Advantages

Provides a solid, secure, and gas-tight connection. Protects the DLO strands from damage. Distributes clamping force evenly. Most likely to meet code requirements.Use an uninsulated ferrule where the metal is exposed to the screw or lug.



Option B: Listed Wire Lugs

These are small set-screw lugs designed to accept fine-stranded wire. Crimp DLO into lug with set-screw. Screw lug into panelboard terminal with screw.

Important Note

Always use a crimping tool that is designed for the specific type and size of ferrule or lug you are using. Using the wrong tool can result in a poor connection that is just as bad as using the DLO directly.2.

Acceptable: Bolt-On Lugs with Crimp Connectors (If Space Allows)

Replace the cage lugs on the panelboard with bolt-on lugs that are specifically designed for the DLO cable size and strand type. Use crimp connectors (like barrel connectors or butt splices) to transition from the DLO cable to a short length of standard building wire (THHN/THWN) that is suitable for the bolt-on lugs. Crimp the connectors properly. Ensure the connectors are listed for the conductor sizes you are using.

Important Considerations

This adds complexity and more connection points, increasing the potential for failure. Make sure you have enough space in the panelboard to accommodate the additional connectors and wiring.3.

Not Recommended: Directly Inserting DLO into Cage Lugs (Generally Unsafe and Non-Compliant) This should only be considered if you have verified through the MCB and lug manufacturer that this is an acceptable practice and that the connection is listed.

Even then, it's still a less reliable and less robust solution.

Never simply jam the DLO into the cage lug and hope for the best.

Steps to Take


Consult the MCB Manufacturer's Documentation

This is the
most important step. The manufacturer's data sheet or installation instructions for the MCB will specify the acceptable wire types and sizes, and may list acceptable termination methods for fine-stranded wire.2.

Consult with a Qualified Electrician

A licensed electrician is the best person to assess your specific situation, recommend the best solution, and ensure the work is done safely and in compliance with all applicable codes.3.

Check Local Electrical Codes

Local codes may have specific requirements for terminating DLO cable in panelboards.4.

Document Everything

Keep records of the connectors, crimping tools, and procedures used. This will be helpful for future inspections and maintenance.

In summary:
*Using DLO cable in standard cage lugs is generally not recommended due to poor contact, potential strand damage, and code compliance issues. Using pin terminals (ferrules) or listed wire lugs crimped onto the DLO cable is the preferred method to ensure a safe, reliable, and code-compliant connection. Always consult with a qualified electrician and follow the manufacturer's instructions. Flag for review