Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Does the Panelboard bus rating have to be higher?

User: Isaiah, Location: Baton Rouge

Asked on: Saturday, March 29, 2025 at 11:25 am EDT
Answered on: Saturday, March 29, 2025 at 11:25 am EDT

Question: If I have a 100 branch CB and the Panelboard is rated only 100A, is this going to be an issue since it’s a bare minimum, 100A bus rating ?

Yes, it's potentially a significant issue. Here's why: Overload Risk

The 100A panelboard rating means the

maximum
continuous current that can safely flow through the panel's busbars and main breaker is 100 amps. Having 100 breakers does not mean you are using 100 amps.
Continuous Load Calculation

The NEC (National Electrical Code) dictates how to calculate the load on a panelboard. Continuous loads (loads that operate for 3 hours or more) are multiplied by 125%. The total calculated continuous load on a panelboard must not exceed 80% of the panelboard's rating. So, for a 100A panelboard, the calculated continuous load should not exceed 80A.

Diversity

The key assumption allowing for many breakers on a panel is diversity. The assumption that all 100 circuits will never be loaded to their maximum capacity at the same time. However, relying on diversity alone is risky without proper load calculations.

Breaker Size vs. Load

It's also very important to understand that the size of the breaker is not a measure of the actual load on the circuit, only the safe amount of load to carry.

What to do
1. Load Calculation (NEC 220)

This is crucial. You need to perform a detailed load calculation for
each circuit connected to the panel. Include: Lighting load (VA per square foot for general lighting, plus any specific lighting loads) Receptacle load (VA per square foot, plus any specific receptacle loads like appliances) Fixed appliances (nameplate ratings) Motor loads (FLA, including starting requirements) HVAC equipment2.

Determine Continuous vs. Non-Continuous Loads

Identify which loads are continuous (3 hours or more) and factor those accordingly (125%).3.

Sum the Calculated Loads

Add up all the calculated loads, including the continuous load factor.4.

Compare to Panelboard Rating

The total calculated load MUST be less than or equal to the panelboard's rating (100A), and the total calculated

continuous
load MUST be less than 80A. If the calculated load exceeds the panelboard rating, you have a problem.

Potential Solutions
Upgrade the Panelboard

The most reliable solution is to replace the panelboard with one that has a higher ampacity rating (e.g., 125A, 150A, 200A). This can be expensive, as it might also require upgrading the service entrance conductors and possibly the utility meter.

Load Shedding/Management System

Install a system that automatically turns off non-critical loads during periods of high demand. This is complex and requires careful planning.


Move Circuits to Another Panel

If available, move some circuits to another panelboard to reduce the load on the overloaded panel.

Reduce Breaker Sizes (Maybe)

While you might be able to downsize some breakers if you know the actual loads are significantly lower than the breaker rating, be extremely careful and ensure this doesn't create an undersized and unsafe circuit.
This requires professional evaluation. You can't just arbitrarily reduce breaker sizes.

Careful Circuit Planning

Re-evaluate the placement of loads on circuits. Can you consolidate low-draw devices onto fewer circuits? Can you ensure that high-demand devices are on separate circuits?

Important Considerations



Safety

Overloading a panelboard is a fire hazard. Don't take shortcuts or assume everything will be okay.


Code Compliance

All electrical work must comply with the NEC and local electrical codes.

Professional Help:
Consult with a qualified electrician or electrical engineer for a proper load calculation and to determine the best course of action. This is not a DIY project.In summary, while having many breakers doesn't automatically mean the panel is overloaded, a 100A panelboard with 100 breakers is* a red flag. A detailed load calculation is essential to determine if the panel is adequately sized. If the calculated load exceeds the panel rating, you need to take corrective action to avoid overloading the panel and creating a safety hazard. Flag for review

Previous Question Next Question