Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NF Panelboards, E-frame breakers

User: PanelGuy1315, Location: Louisville

Asked on: Thursday, April 3, 2025 at 5:31 pm EDT
Answered on: Thursday, April 3, 2025 at 5:31 pm EDT

Question: Wanted to get the experts opinion on this single line...Planning to use Schneider NF Panelboard with 30A E-Frame breakers. From my understanding, in this design, the E-Frame breakers are not the branch circuit breaker because each downstream panel has it's own circuit breaker. For some reason I'm getting some hesitation from our material vendor that these E-Frame breakers are not rated for this. Something about motor loads, but these are HACR breakers made for motor loads. Plus most all loads are on the other side of a VFD.

Okay, let's break down this situation. Your understanding is likely correct, but the devil's in the details. Here's a structured approach to analyzing the concerns

Understanding Your Intended Design:
NF Panelboard (Schneider)

This is a standard branch panelboard.


30A E-Frame Breakers

Schneider Electric's E-Frame breakers are common and cover a range of amperages and interrupting ratings. They are designed for various applications.

Downstream Panels with Their Own Circuit Breakers

This is key. You are essentially using the E-Frame breakers in the NF panel as
feeders to downstream panels, not directly as branch circuit overcurrent protection for specific equipment (motors, lights, etc.).

VFDs on Most Loads

Very important. VFDs significantly change the nature of the load seen by the upstream breaker.

Why the Vendor Might Be Hesitating (And How to Address It)

The vendor's hesitation likely stems from one or more of these potential issues:1.

Misunderstanding of the Application

The vendor might be thinking the E-Frame breakers are directly protecting motor loads without the VFDs in the picture. That scenario requires careful selection considering motor inrush currents.2.

Interrupting Rating Concerns

The vendor needs to ensure the AIC (Ampere Interrupting Capacity) rating of the E-Frame breakers is sufficient for the available fault current at the panelboard location. If the available fault current is high (common near transformers and service entrances), a standard E-Frame breaker might not have a high enough AIC rating. Upgrading to a higher AIC version of the E-frame or changing to a series rated system may be necessary.3.

Selective Coordination

This is a more advanced design consideration. If you need selective coordination (meaning the downstream breaker always trips before the upstream breaker for a downstream fault), you need to carefully coordinate the time-current curves of the E-Frame breakers with the downstream breakers. This involves more than just selecting the right amperage. Selective coordination ensures that the closest breaker to the fault trips first. A non-selective trip will cause an outage of more than just the faulted circuit.4.

Code Compliance (NEC and Local)

The vendor may be concerned about strict interpretation of the NEC relating to feeder taps, protection of conductors, and other regulations.5.

Upstream Overcurrent Protection

The breaker in the NF Panelboard needs to be appropriately sized to protect the conductors that feed the panelboard.

How to Overcome the Vendor's Concerns (and Ensure a Proper Design)


Clearly Define the Application

This is the most important step. Explain, in detail, that the E-Frame breakers are feeding downstream panels, each with its own circuit breakers. Emphasize the presence of VFDs on most loads. Provide a single-line diagram if possible.2.

Provide Load Calculations

Give the vendor the actual (or estimated) load calculations for each downstream panel. This will prove that the 30A E-Frame breaker is adequately sized to carry the continuous load. Remember to include the VFD derating factors (if applicable).3.

Verify AIC Rating

Determine the available fault current at the NF panelboard location. The electrical engineer/designer must calculate this. The AIC rating of the E-Frame breakers must be higher than the available fault current. If the standard E-Frame breakers don't have a high enough AIC rating, specify higher-rated breakers or consider series ratings.4.

Consider Selective Coordination (If Required)

If selective coordination is a requirement for your installation, explicitly state this. Work with the vendor (or a consulting engineer) to choose breakers with appropriate time-current characteristics. This usually involves comparing the TCC curves of the upstream and downstream breakers.5.

Specify HACR Breakers

Since you mentioned HACR ratings, reiterate that you are specifically requesting HACR-rated E-Frame breakers. This is important for handling motor loads, even with VFDs.6.

Address Tap Rules

Double-check any tap rules that might apply under the NEC or local codes. If the conductor to the downstream panel is considered a "tap," ensure it complies with all applicable requirements (length limitations, overcurrent protection, etc.).7.

Consult with a Qualified Electrical Engineer (Strongly Recommended)

For a project of any significant size, it is best practice to consult with a qualified electrical engineer. They can review your design, perform load calculations, determine fault current, and ensure that your electrical system meets all applicable codes and standards. An engineer can provide stamped drawings that will expedite the approval process with the AHJ.

Example Communication to Vendor:
"We are using a Schneider NF panelboard with 30A E-Frame breakers to feed downstream panels, each with its own set of branch circuit breakers. The E-Frame breakers are acting as feeder breakers to these subpanels. Most loads in the downstream panels are driven by VFDs. We need HACR-rated E-Frame breakers. Please verify the AIC rating meets or exceeds the available fault current at the NF panelboard, which is [State Available Fault Current] at [Voltage]. Here are the load calculations for each downstream panel [Provide Load Calculation Information]. Selective coordination is/is not a requirement for this project. Can you provide breakers suitable for this application?"By addressing these points, you should be able to clarify your needs, alleviate the vendor's concerns, and ensure that you get the correct breakers for your application. Remember, safety and compliance are paramount. Consulting with a qualified electrical engineer is always a prudent step. Flag for review

Previous Question Next Question