Question: My company recently took our PPE Arc flash protection (level 4) suit away and informed myself and another licensed electrician in NJ that we can't work on high voltage electrical equipment until we have ARC flash suit certification to even wear the equipment. Is this a NFPA requirement or just my company being over cautious ?

This is a nuanced situation, and the answer likely lies somewhere between a strict NFPA requirement and your company being extra cautious. Here's a breakdown

1. NFPA 70E (Standard for Electrical Safety in the Workplace):
NFPA 70E is the primary standard addressing electrical safety in the workplace, including arc flash protection. It outlines requirements for training, hazard assessment, selection of appropriate PPE, and safe work practices. NFPA 70E does require training on arc flash hazards and the proper use of PPE. It specifies that employees must be trained to understand the hazards, select the correct PPE, inspect it, and use it properly. This is the key requirement that applies to your situation.

NFPA 70E
does not mandate a specific certification program for wearing arc flash PPE. It does not say you must have a specific "arc flash suit certification" from a particular organization. The standard focuses on the competency of the employee to understand the hazards and use the PPE correctly.

High Voltage Consideration

While NFPA 70E covers electrical safety broadly, it doesn't specifically have a cut and dry definition of High Voltage. However, in general in the industry, High Voltage is considered anything over 600 volts. This is a generalization and your company may have different parameters in place.

Hazard Risk Assessment: Employers are also required to conduct a Hazard Risk Assessment to understand the potential hazards and voltage levels of the electrical equipment that you will work on.2. The "Certification" Question



No Mandated Certification

There isn't a universally recognized or mandated "Arc Flash Suit Certification" required by NFPA 70E.

Training Programs Exist

There
are various training programs offered by organizations and manufacturers that focus on arc flash safety and PPE use. These programs can provide valuable knowledge and hands-on training. Examples include courses from: NFPA (itself) Eaton ABM University

Employer Responsibility

Ultimately, it's the
employer's responsibility to ensure that their employees are adequately trained to safely perform their job duties, including the proper use of arc flash PPE. This training must be documented.

3. Company Policies and Legal Considerations



Employer Discretion

Companies have the right to implement safety policies that exceed the minimum requirements of NFPA 70E. They can choose to require specific training or even certifications as a condition of employment or for performing certain tasks.

Due Diligence

By requiring "arc flash suit certification," your company may be trying to demonstrate due diligence in ensuring worker safety and reducing their liability in case of an accident.


OSHA (Occupational Safety and Health Administration)

OSHA enforces NFPA 70E (through the General Duty Clause and specific electrical safety standards). If OSHA were to investigate an arc flash incident, they would likely scrutinize the employer's training program and the employees' understanding of arc flash hazards and PPE use.

4. Specifics of Your Situation in New Jersey



State Regulations

New Jersey follows federal OSHA regulations regarding electrical safety. There are no specific NJ state-level requirements that mandate arc flash suit certifications
beyond the requirements of NFPA 70E and OSHA.

Licensed Electrician

Being a licensed electrician in NJ means you've met certain educational and experience requirements. However, the state license doesn't automatically equate to being qualified to safely work on energized electrical equipment and utilize arc flash PPE. Specific training on arc flash hazards and PPE is still required.

In summary



NFPA 70E mandates training on arc flash hazards and the proper use of PPE, but it does not require a specific "arc flash suit certification."


Your company is likely being cautious and implementing a policy that exceeds the minimum requirements of NFPA 70E, likely to demonstrate a commitment to safety and reduce liability.

This policy is within their rights, as employers can set stricter safety standards than those mandated by NFPA 70E and OSHA.

Recommendations


Clarify with your company

Ask them specifically
what "arc flash suit certification" they require. What training or certification programs do they approve? What are the specific competencies that the certification aims to demonstrate?2.

Inquire about the training

Understand the training provided by the company, is it hands on or virtual? Is the training provided by qualified individuals?3.

Express your experience

While acknowledging their policy, you can mention your experience as a licensed electrician and inquire if there's any way to expedite the process (e.g., if your existing training and experience can be considered in lieu of the certification).4.

Embrace the training

Even if you feel you already know a lot about arc flash safety, approach the training with an open mind. It's an opportunity to refresh your knowledge and learn about new best practices and PPE technologies.5.

Documentation:
* Ensure your training is properly documented by your employer. This documentation is crucial for demonstrating compliance with safety regulations.By understanding the relevant standards, company policies, and your own qualifications, you can have a productive conversation with your employer and work towards a safe and compliant work environment. Flag for review