Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Cat6 cable run in conduit with THWN-2.

User: solarken, Location: Hudson, OH, USA

Asked on: Tuesday, April 8, 2025 at 3:50 pm EDT
Answered on: Tuesday, April 8, 2025 at 3:50 pm EDT

Question: I have seen a few references to this before but with conflicting info. I cannot find any clear information that suggests cat6 ethernet cabling carrying TCP/IP communications is considered class 1 or 2 or 3 circuits. THere is some verbiage that suggests that if Power over ethernet (POE) is enabled it may be considered class 2 or 3 power limited circuits. Without POE, it seems like it is just a communication circuit, which I believe is covered by article 800. I have a single 2-inch conduit that is buries to run a 10AWG 208V AC circuit in along with an ethernet cable and I am trying to figure out what is required as far as separation/protection within the conduit. For example, put the cat 6 in 1/2-inch ENT conduit and pull in with the THWN? Use MC cable for the power conductors and pull in ethernet with it? I don't want to damage the cat6, and it is probably at least a 50-foot run underground with a few 90's. Any code references would be helpful. 800.47(A) says Underground comm wires and cables, ...., in a raceway, handhole, ...., containing power conductors shall be in a section separated from such conductors by means of brick, concrete, or tile partitions, or by means of a suitable barrier.

You've hit on a complicated area where electrical and data cabling regulations intertwine. Let's break this down to clarify what the code says and suggest a compliant approach.

Understanding the Code (Based on NEC - National Electrical Code)



Article 800 (Communications Circuits)

You're correct. Non-PoE Ethernet (Cat6 carrying TCP/IP data) falls under Article 800. This article governs the installation of communication circuits.


Article 725 (Class 1, 2, and 3 Remote Control, Signaling, and Power-Limited Circuits)

PoE changes the game. If you are transmitting power through the Ethernet cable (PoE, PoE+, etc.), the circuit is considered a Class 2 or 3 power-limited circuit if it meets the voltage and current limitations defined in Article 725. PoE voltages are typically around 48V DC.

Article 300 (Wiring Methods)

This general article covers basic rules for wiring methods, including when different voltage systems are run in the same raceway.


800.133 (Installation of Communications Wires, Cables, and Equipment)

Specifically deals with separating communication cables from power conductors.

Your Specific Scenario: 2" Conduit with 208V and Ethernet


You have a 2-inch conduit containing a 10 AWG 208V circuit and a Cat6 cable. This is where the issue arises:1. Without PoE

If your Cat6 cable is only carrying data (no PoE), then you must adhere to 800.133.
2.


With PoE

If your Cat6 cable is carrying PoE, the conduit needs to be treated as a mixed system, with both power and communication circuits.

Code-Compliant Solutions (Assuming you are NOT using PoE)


Because of the wording in 800.133(A), the best solution would be to run two separate conduits, that way there is not question of whether you comply with NEC. However, if you need to run this cable together in the same conduit, here is the next best thing.Based on 800.133(A), here are a few compliant options: Option 1: Innerduct/Raceway

Run the 10 AWG THWN wires as is inside the 2-inch conduit. Place the Cat6 cable inside a separate innerduct (flexible conduit) or a rigid PVC conduit (small diameter) within the larger 2-inch conduit. This creates the required physical barrier. The innerduct/conduit must be secured within the larger 2-inch conduit to prevent movement and maintain separation.

Option 2: Shielded Cable and Grounding (Less Recommended, Consult Local Inspector)

Use a shielded Cat6 cable (STP - Shielded Twisted Pair). Properly ground the shield of the Cat6 cable at both ends, according to manufacturer instructions and applicable grounding requirements. This might satisfy the "suitable barrier" requirement, but you need to confirm this with your local electrical inspector. Grounding is critical for this method to work effectively. Without proper grounding, the shield could make the problem worse.

Code-Compliant Solutions (Assuming you ARE using PoE)


If PoE is enabled, it is far more complicated, but again, here are a few options:
Option 1: Separate conduits. Run the 10 AWG THWN wires in one conduit, and the POE enable CAT6 in a seperate conduit, This would clearly be the "safest and compliant way". Option 2: Innerduct/Raceway, with class 2 and 3 rated cable Run the 10 AWG THWN wires as is inside the 2-inch conduit. Place the Class 2 and 3 rated POE enabled Cat6 cable inside a separate innerduct (flexible conduit) or a rigid PVC conduit (small diameter) within the larger 2-inch conduit. This creates the required physical barrier. The innerduct/conduit must be secured within the larger 2-inch conduit to prevent movement and maintain separation. Option 3: Shielded Cable and Grounding (Less Recommended, Consult Local Inspector)

Use a shielded Cat6 cable (STP - Shielded Twisted Pair). Properly ground the shield of the Cat6 cable at both ends, according to manufacturer instructions and applicable grounding requirements. This might satisfy the "suitable barrier" requirement, but you need to confirm this with your local electrical inspector. Grounding is critical for this method to work effectively. Without proper grounding, the shield could make the problem worse.

Important Considerations



Manufacturer's Instructions

Always follow the cable manufacturer's instructions regarding bend radius, pulling tension, and other installation guidelines for both the power cable and the Cat6 cable.


Derating

When multiple conductors are in the same conduit, you may need to derate the ampacity of the 10 AWG conductors. Refer to NEC Table 310.15(C)(1). Make sure the 2-inch conduit has enough capacity for the derated conductors.

Fill

Ensure the conduit fill (the percentage of the conduit's cross-sectional area occupied by the wires and cables) does not exceed the limits specified in the NEC.


Local Codes

Always check with your local electrical inspector for any specific local codes or interpretations that may apply to your installation. They have the final say.

Physical Protection

Protect the Cat6 cable during the pull. Use pulling lubricant specifically designed for data cables to minimize friction and prevent damage to the cable jacket.


Testing

After installation, test the Cat6 cable to ensure it meets the required performance standards (e.g., using a cable analyzer).

Recommendation

The safest and most clearly code-compliant option is to use separate conduits. If that's not feasible, using an innerduct or conduit within the larger conduit to physically separate the power and data cables is the next best choice.

Disclaimer:
I am an AI chatbot and cannot provide legally binding electrical advice. This information is for educational purposes only. Always consult with a qualified and licensed electrician for any electrical work. They can assess your specific situation, ensure compliance with all applicable codes, and perform the installation safely. Flag for review

Previous Question Next Question