User: Jimmy7, Location: Boston, MA
Asked on: Wednesday, April 9, 2025 at 7:28 am EDT
Answered on: Wednesday, April 9, 2025 at 7:37 am EDT
Question: I have a customer who wants some recessed lights replaced. Someone dropped the housings to refinish the wood ceiling and the housings got destroyed. In any case the housings are 5” shallow housings. I wasn’t going to install wafer lights because one fixture has three cables going to it, and I thought the wafer lights junction box would be too small. There are three lights, but one has two 14-2, and one 14-3 going to it (Drawing attached). I did not see a cubic inch on the junction box, so I measured the inside dimensions of the housing’s junction box which were 1.5 x 2.5 x 3.75 =14.0625. Two 14-2 and One 14-3 have wire fill of 16 cu in. Am I looking at this right? If so, what is the best way out of this? The owner wouldn’t want me cutting a junction box into the ceiling..
You're on the right track in thinking about box fill. You are correct that the scenario you described would be a violation of the NEC regarding box fill.Here’s a breakdown of the issues and some potential solutions, keeping in mind that I am an AI and cannot provide code-compliant solutions and that it's always essential to consult local codes and a qualified electrician for the final decision and implementation.
The Problem: Junction Box Fill Calculation Your Calculation
Your calculation of 14.0625 cubic inches for the box is correct based on the dimensions you provided.
Wire Fill Calculation
You're slightly off on the wire fill calculation. Here's the breakdown based on NEC (National Electrical Code) for 14 AWG conductors: Each 14 AWG conductor = 2.0 cubic inches
Two 14-2 cables
Each 14-2 cable has two current-carrying conductors and one equipment grounding conductor. 2 cables x (2 conductors + 1 ground) = 6 conductors x 2.0 cubic inches = 12 cubic inches
One 14-3 cable
The 14-3 cable has three current-carrying conductors and one equipment grounding conductor. 1 cable x (3 conductors + 1 ground) = 4 conductors x 2.0 cubic inches = 8 cubic inches
Device Fill (if any)
If there are devices such as a dimming module mounted in the box, you have to add the double volume allowance for a number of conductors from the device
Total Fill
12 + 8 = 20 cubic inches minimum
You are
well over the box fill capacity.
SolutionsHere are several possible approaches to consider, ranked roughly in order of desirability (least invasive to most invasive, assuming that is the customer's desire), but also considering safety and code compliance:1.
Inspect The Existing Junction Box Thoroughly
Check for Listed Cubic Inch
Ensure that the junction box is not marked in a way you've overlooked, and look at other similar boxes.2.
If Using Shallow Housing Recessed Lights. Some shallows come with a larger junction box that may accommodate the wires.3.
Remote Junction Box
Description
This involves installing a larger junction box above the ceiling (in the attic or accessible space) and extending wires from that box down to the recessed light.
Pros
Solves the box fill issue without cutting into the finished ceiling. Provides easier access for future maintenance. Allows for use of standard, readily available junction boxes.
Cons
Requires access to the space above the ceiling. Adds more labor and materials. May require running additional conduit or cable protection if the wiring runs through inaccessible spaces.4.
Larger Recessed Housing
Description
Find a different 5" recessed housing that is rated to accept a higher box fill
Pros
Solves the box fill issue without cutting into the finished ceiling.
Cons
May not exist.5.
Install a Junction Box Into the Ceiling
Description
Cut a hole in the ceiling to install a larger junction box closer to the recessed light location.
Pros
Solves the box fill issue.
Cons
Requires cutting into the finished ceiling (which the owner doesn't want). Aesthetically undesirable.
Important Considerations
Accessibility
Any junction box you install must be accessible. That means you can't bury it in the ceiling without a cover that can be removed.
Local Codes
Always check with your local electrical inspector about what is allowed in your jurisdiction. Local codes can be more restrictive than the NEC.
Professional Help
If you're unsure about any of these steps, or you run into complications, it's best to consult with a licensed electrician.
Recommendation:*Start with the least invasive options, like inspecting the original box. If those don't work, move to a remote junction box in the attic. While the remote junction box requires more labor and access, it generally provides the most code-compliant and maintainable solution while minimizing disruption to the finished ceiling. Flag for review