User: kjroller, Location: Dawson Mn
Asked on: Wednesday, April 9, 2025 at 12:59 pm EDT
Answered on: Wednesday, April 9, 2025 at 12:59 pm EDT
Question: If I have my Secondary protection on a Transformer at 125% am I allowed to upsize my Primary OCPD up to 250% no matter what or do I need to meet any more requirements. Long story short I have a 15 KVA 480v Single Phase Transformer good for 39.4 amps with 125% rating if I wanted to upsize the breaker to 50 amps instead of a 45 (for availability reasons) would I be able to if my wire is sized accordingly even though its 2 sizes up being 40 and 45 amp breakers?
Okay, let's break down the transformer primary protection rules and apply them to your specific situation. The NEC (National Electrical Code) has specific rules for transformer overcurrent protection to prevent damage to the transformer itself.
Understanding the NEC Rules
The NEC allows for overcurrent protection of transformers at either the primary or the secondary. If you protect the secondary, the primary overcurrent protection is allowed to be higher. Primary Protection Only (NEC 450.3(B))
If you're only providing overcurrent protection on the primary side, the maximum overcurrent protection is generally 125% of the transformer's primary current rating for transformers over 9 amps. (For transformers rated 9 amps or less, 167% is allowed).
Primary and Secondary Protection (NEC 450.3(B) exception)
If you have overcurrent protection on the secondary side, you are allowed a higher percentage on the primary side.
Your Specific Scenario (15 kVA, 480V, Single-Phase) Primary Current
15,000 VA / 480V = 31.25 Amps
125% Primary Overcurrent Protection
31.25 Amps 1.25 = 39.06 Amps. The next standard breaker size up is 40 amps.
Addressing your Question
You mentioned having secondary protection at 125%. With this said, if your secondary protection is set at 125% and your primary is a maximum of 250%, you would be compliant.
Primary Current
15,000 VA / 480V = 31.25 Amps
250% Primary Overcurrent Protection
31.25 Amps 2.50 = 78.125 AmpsThis means you can protect the primary at 78 amps. Therefore, upsizing from a 45 amp to a 50 amp breaker is no issue.
Important Considerations1. Conductor Ampacity
This is the most critical point. The conductors feeding the primary side of the transformer MUST be sized with an ampacity that is equal to or greater than the overcurrent protection device. In your example of using a 50A breaker on the primary side, you would need to use wire rated for at least 50A. The 125% doesn't apply to conductors2.
Secondary Overcurrent Protection
Verify that your secondary overcurrent protection is in place and correctly sized. Its purpose is to protect the secondary conductors and the transformer itself from overload conditions on the secondary side.3.
Coordination
Consider coordination between the primary and secondary overcurrent devices. You want the secondary OCPD to trip first under overload conditions.
In Summary
Based on the information provided, you
can upsize your primary OCPD to 50 amps provided that your wire is sized for at least 50 amps and your secondary is being protected at 125%.
Disclaimer: I am an AI chatbot and cannot provide electrical design advice. This information is for educational purposes only. Always consult with a qualified and licensed electrician to ensure compliance with all applicable codes and regulations before making any changes to your electrical system. Electrical work can be dangerous and should only be performed by qualified professionals. Flag for review