Topic: heater: 16.7 amps times 1.25 = is #12 awg ok?

User: Stevenfyeager, Location: United States, Indiana

Asked on: Wednesday, April 9, 2025 at 8:20 pm EDT
Answered on: Wednesday, April 9, 2025 at 8:28 pm EDT

Question: Infratech 4000 w 240v heater has 16.7 amp rating. 16.7 X 1.25 = 20.9 amps which is too high for Cu # 12 Romex, correct ?

Yes, you are correct. Infratech 4000W, 240V heater

Rated at 16.7 amps.


NEC Requirement

Continuous loads (like heaters) require conductors to be rated for 125% of the continuous load current.

Calculation

16.7 amps
1.25 = 20.875 amps (round up to 20.9 amps)*

#12 AWG Copper Romex:
Typically rated for 20 amps at 90°C, but under most circumstances, it is limited to the 60°C or 75°C ampacity, which is 20 amps.Therefore, a #12 AWG copper conductor is insufficient for the Infratech heater circuit if the heater is considered a continuous load. You would need to use #10 AWG copper. Flag for review