Topic: Do we have to follow 2017 NEC 240.21(B)(2) for the supply side connection per 705.31?

User: Frank6172, Location: Maryland

Asked on: Wednesday, April 9, 2025 at 9:15 pm EDT
Answered on: Wednesday, April 9, 2025 at 9:15 pm EDT

Question: Hi all,Any help will be greatly appreciated! Here is the scenario:We interconnected our solar system through a supply side connection made at the utility service entrance conductors of a 1200A MSP with 1200 MCB. The conductor run from the fused PV system AC disconnect(OCPD) to the point of interconnection is 14' so we plan to use the cable limiters per the Exception of 705.31 to work around the 10' rule. However, the inspector is saying we need to comply with the 25' tap rule per 240.21(B)(2) which will result in increasing our conductor size to not less than 1/3 of the rating of MCB. In my understanding, 240.21 is for the tap conductors that receive their supply, not for conductors that backfeed the utility. Also, I believe supply side connection has the different definition to "tap" so 240.21 does not really apply to the supply side connection for solar photovoltaic. Am I right? Has anyone encountered this situation during the inspection?Thanks!

You are correct. Your understanding of the NEC is accurate in this scenario. The inspector is misapplying 240.21(B)(2), the 25-foot tap rule. Here's a breakdown of why and how to address it

Why 240.21 Doesn't Apply:
240.21 is for Load Side Taps

Article 240.21 specifically deals with tap conductors that
supply a load from a larger overcurrent protective device. It's about protecting the smaller conductors that are feeding downstream equipment.

Supply-Side Connections are Different

A supply-side connection, as you have, is where the solar system feeds power into the existing electrical system, not draws power from it. Think of it as a small generator feeding into the grid. The current flow is reversed.

705 (Interconnected Electric Power Production Sources) Governs

Your installation falls under Article 705, which addresses the specific requirements for interconnected power production sources like solar PV. 705.31(A) allows the use of cable limiters for a supply-side connection under certain conditions, specifically to avoid the restrictive sizing required without them.


"Tap" Doesn't Equate to Supply Side

The word "tap" has a general meaning, but in the context of the NEC, a tap is typically understood to be a load-side connection as defined in 240.21. A supply-side connection, as described in 705, is a distinct scenario.

Why the Exception in 705.31 (Cable Limiters) Exists

The exception in 705.31(A) allowing cable limiters for short runs (10 feet, with exceptions up to your 14 feet with limiters) exists precisely to avoid the onerous conductor sizing requirements that would otherwise be required for a supply-side connection to a large service. Without this exception, almost all supply-side connections would become prohibitively expensive and difficult to implement.

How to Address the Inspector's Concerns


Respectfully Explain Your Reasoning

Clearly and respectfully explain to the inspector your understanding of the NEC and how Article 705 applies to your situation. Point out the specific language in 705.31(A) and its exception for cable limiters.
2.


Cite the NEC Articles

Provide the inspector with the specific NEC article references:

Article 705

Interconnected Electric Power Production Sources. Emphasize that this is the primary article governing your installation.


705.31

Supply Side Source Connections.

705.31(A)

Specifically mention the cable limiter exception for conductor ampacity.


240.21

Explain why this article doesn't apply, because it addresses load-side taps, not supply-side connections.3.

Provide Diagrams/Calculations

If possible, provide clear diagrams showing the system configuration and calculations demonstrating that the cable limiters are properly sized and that the installation complies with all applicable requirements of Article 705. Ensure your AHJ approves of your engineering judgment and calculations.
4.


Escalate if Necessary

If the inspector is unwilling to change their position, you may need to escalate the issue to a more senior inspection official or the AHJ (Authority Having Jurisdiction). Before doing so, make sure you have your documentation in order and a clear understanding of the NEC requirements.5.

Consider a Second Opinion

If you're still unsure, consider consulting with another licensed electrical engineer or a qualified electrical contractor with experience in solar PV installations and NEC compliance.6.

Documentation

Make sure you thoroughly document all interactions with the inspector and any code interpretations discussed. This documentation may be helpful if you need to appeal the inspector's decision.

In Summary:


You are correct in your interpretation of the NEC. The inspector is incorrectly applying the 25-foot tap rule. Focus on Article 705 and the exception for cable limiters in 705.31(A). Be prepared to explain your reasoning clearly and respectfully to the inspector. Good luck! Flag for review

Previous Question Next Question