Question: I am a PE with 25 years experience, but don't yet understand a nuance here. I understand "available fault current" and the need to brace equipment with an SCCR that is higher than than the AIC. I understand how arc flash is a function of both how large the fault current is, and how long it is allowed to continue before clearing. So there are a couple basic concepts you probably don't need to walk me through.What I don't understand is, what exactly is the SCCR getting you? I have read that for equipment with appropriate SCCR "damage may occur, but it must not present a shock hazard, fire hazard, or expel projectiles from the equipment". So say if you calculate 45.4k available fault current, you would rate the panel at 65kAIC. But then the perfect storm of a fault happens, and an arc flash event occurs. On an intuitive level I would think the SCCR would mean the equipment is built more "heavy duty" or with bussing further apart so that when the short circuit occurs it does not turn into a ball of flame. Obviously, I know, that is not how it works - the ball of flame may still be coming. So what level of safety are you getting with the increased SCCR? Is it "when the arc flash occurs the panel blows up a little bit less", or what?I am not articulating this perfectly, but would appreciate you taking stabs at answering what you think I am asking and maybe that will help me ask it better. Thanks in advance!
You're asking an excellent and insightful question. It gets to the heart of what SCCR actually protects against, beyond simply complying with code. Here's my attempt to break it down and clarify what that higher SCCR really buys you
What SCCR Isn't:
Arc Flash Mitigation
You're absolutely right. SCCR does not directly reduce the severity of an arc flash. It doesn't change the incident energy, boundary distances, or PPE requirements directly. A higher SCCR doesn't mean a smaller arc flash. It's possible, that by allowing the use of a faster clearing device that an incident can be cleared quicker and thus limit the arc flash event duration. That being said, that is usually incidental.
Complete Protection from Damage
As the definition you cited highlights, damage is expected during a short circuit exceeding the equipment's withstand rating. The goal is not to prevent damage entirely, but to control what kind of damage occurs.
What SCCR Is (and What You're Paying For)
Containment of the Failure
This is the core benefit. A higher SCCR is intended to ensure the equipment:
Doesn't Catastrophically Explode
It's about preventing the enclosure from disintegrating, sending shrapnel flying, and creating a much larger, uncontrolled fire.
Maintains its Enclosure
Prevents the enclosure from bursting open, exposing energized components, and significantly increasing the risk of electric shock to anyone nearby.
Limits the Spread of Fire
The enclosure should contain the arc, preventing it from easily igniting surrounding materials.2.
Reduced Risk of Secondary Hazards
By containing the failure, a higher SCCR minimizes:
Electric Shock
Even after a fault event, the integrity of the enclosure should be maintained, reducing the chance of coming into contact with energized components.
Fire Spread
Containing the arc flash within the enclosure buys time for fire suppression systems to activate and prevents the immediate ignition of surrounding combustible materials.
Projectiles
Critical! Preventing the enclosure from exploding reduces the risk of metal fragments, molten material, or other debris being ejected at high velocity.3.
Predictable and Controlled Failure (to a Degree)
A higher SCCR aims to ensure that the equipment fails in a predictable manner. The idea is that you would rather have a localized arc flash event inside a panel than have that arc flash lead to a chain reaction of equipment failures and a widespread fire.
Think of it this way
Imagine two identical panels, one with a lower SCCR and one with a higher SCCR, both exposed to the same fault current exceeding their withstand ratings.
Lower SCCR Panel
The panel might literally explode, with doors blown off, bus bars melted, and a large fireball erupting from the enclosure. Pieces of the panel and molten metal could be thrown significant distances.
Higher SCCR Panel
The panel will likely sustain internal damage. There will be an arc flash inside the enclosure, potentially melting components and causing internal arcing. However, the enclosure should remain intact, containing the fire and preventing projectiles. The fault should be localized.
Your "Blows Up a Little Bit Less" Intuition is Valid
Your intuition about the equipment being "more heavy duty" is also generally correct. Achieving a higher SCCR often involves: Stronger Enclosures
Thicker metal, better welds, robust latching mechanisms.
More Robust Bus Bar Support
More secure bracing to withstand the immense electromagnetic forces generated during a fault.
Components with Higher Withstand Ratings
Choosing components that can tolerate higher fault currents for a short duration.
Proper Spacing and Insulation
Minimizing the risk of flashovers between components.
The Bottom Line
SCCR is a critical safety feature, but it's about controlling the consequences of a fault, not preventing the fault itself. It's about transforming a potentially catastrophic event into a more localized, manageable incident. It's not a guarantee of perfect safety, but it significantly reduces the risk of injury, fire, and widespread damage.
To summarize your question:"So what level of safety are you getting with the increased SCCR? Is it "when the arc flash occurs the panel blows up a little bit less", or what?"Yes, you are correct! By requiring panels with higher SCCRs, you reduce the chance that they blow up entirely, or spray projectiles, or start fires more readily.I hope this helps clarify the purpose of SCCR. It's a crucial concept often misunderstood. Let me know if you have more questions! Flag for review