Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Not sure if cable sizing is right

User: JunLang123, Location: Canada

Asked on: Saturday, April 12, 2025 at 6:26 pm EDT
Answered on: Saturday, April 12, 2025 at 6:40 pm EDT

Question: My uncle runs a farm and has the 3ph, 460V, 20 HP submersible pump fed from a 3ph 480V panel. Between the pump and panel, there is a junction box and motor starter enclosure with 60 A breaker. Here’s the setup and cabling:Panel (70 A branch breaker) —— (1/0 AWG cable) ——> Junction Box ——(8 AWG cable) ——> Motor Starter Box 60 A breaker ——(8 AWG cable)——> some receptacle ——(idk what size cable with a plug connected to receptacle)——> PumpNow, I questioned him about the 8 AWG cable sizes. My initial thought was that the 8 AWG cables seems to be undersized for the breakers he has. Those cables will probably fail before the breakers trip since 8 AWG max allowable amp is 50 A (Table 2). He said they are sized fine and he sized them based on the voltage drop and pump size. Said I should listen more in my classes (I’m a first year electrical engineering student. We don’t even talk about the code and stuff)Am I wrong about my justification?

You are absolutely correct to be concerned about the #8 AWG wire being protected by a 60A breaker. Your uncle's reasoning is flawed, and relying solely on voltage drop calculations without considering ampacity is dangerous. While voltage drop is important, it's a secondary consideration to the basic safety of the wiring.Here's a breakdown of why you're right and where your uncle's logic falls short: Ampacity is King

The primary concern in electrical wiring is the ampacity of the conductors. Ampacity is the maximum current a conductor can carry continuously without exceeding its temperature rating. NEC (National Electrical Code) Table 310.16 (which you referenced as Table 2 - likely from a simplified source) dictates the ampacity of conductors based on insulation type, temperature rating, and installation conditions. For #8 AWG copper wire with common insulation types (like THHN, THWN), the ampacity is typically around 50 amps (or less, depending on the temperature rating and how it's installed).

Running more current than the ampacity allows causes the wire to overheat, potentially melting the insulation and causing a fire.
Overcurrent Protection

Breakers are designed to protect the wiring from overcurrent situations, not primarily to protect the motor (though that's a secondary benefit). A 60A breaker will not trip until the current through the #8 AWG wire exceeds 60 amps. By then, the #8 AWG wire could be severely overheating and creating a fire hazard.

Motor Protection vs. Branch Circuit Protection

Your uncle might be confusing motor
overload protection with branch circuit protection. Motor starters do contain overload protection (often adjustable) that is sized to protect the motor itself from overheating due to mechanical issues. However, this overload protection is separate from the breaker protecting the wiring of the entire branch circuit. The starter's overload protection may not trip until the pump is drawing a significant amount of current (exceeding the 50A limit), which again will damage the #8 AWG.

Voltage Drop

Voltage drop is important, especially for motors. Excessive voltage drop can cause the motor to run hotter, draw more current, and reduce its lifespan. However, voltage drop calculations are used to ensure acceptable performance, after the wiring is properly sized for ampacity and overcurrent protection. You use the appropriate size cable to meet the ampacity requirement, and then check voltage drop. If it's too high, increase the wire size, even if the ampacity is already sufficient.

The NEC (National Electrical Code)

While you may not be studying the NEC in detail yet, it's the foundational standard for electrical safety in the US. It's what electricians use to ensure installations are safe and compliant. The NEC always prioritizes ampacity and overcurrent protection.

Here's a more detailed breakdown of what the NEC would require (General guidance, consult with a professional electrician)


Motor Full Load Amps (FLA)

You need the motor's FLA (full load amps) from the motor nameplate. A 20 HP, 460V, 3-phase motor will draw approximately 27-30 amps.2.

Branch Circuit Conductor Sizing (NEC 430.22)

The branch circuit conductors supplying a single motor must have an ampacity of not less than 125% of the motor's FLA. So, if the FLA is 30A, you'd need conductors rated for at least 30A
1.25 = 37.5A. #8 AWG might be sufficient if the FLA is below 32A and the conditions are right.3.

Overcurrent Protection (NEC 430.52)

The maximum rating or setting of the branch circuit short-circuit and ground-fault protective device (the breaker) depends on the motor's design letter (found on the nameplate) and the type of breaker. For a typical motor, you can use an inverse time breaker set at up to 250% of the FLA. However, if that value doesn't allow the motor to start, you may need to go higher.

Example: If the FLA is 30A, then 250% of the FLA is 75A.
However, the breaker should still not exceed what the conductors can handle.4.


Motor Overload Protection

This is handled by the motor starter and is separate from the branch circuit overcurrent protection.

In Summary



You are correct

The #8 AWG wire is likely undersized for the 60A breaker.


Your uncle's logic is flawed

Voltage drop is a secondary consideration to ampacity.

Immediate Action

Your uncle should consult with a qualified electrician to assess the situation and correct the wiring to comply with the NEC. This is not a "DIY" project.

Advice for Your Uncle:
*Explain your concerns to your uncle using the principles of ampacity and overcurrent protection. Emphasize the safety implications of undersized wiring and the potential for a fire. If he is insistent, strongly encourage him to get a professional opinion from a licensed electrician. It's not worth risking a fire or damaging equipment.You're on the right track with your electrical engineering education. Keep asking questions and learning the fundamentals! This is a great real-world example of why understanding the code is so important, even if you're focusing on design and analysis in your courses. Flag for review

Previous Question Next Question