Topic: Energy metering - Tenant

User: aelec84, Location: Los Angeles

Asked on: Wednesday, April 16, 2025 at 6:32 pm EDT
Answered on: Wednesday, April 16, 2025 at 6:33 pm EDT

Question: Hello forum,I have a question regarding tenant metering. If I need to measure the energy consumption of certain circuits from a panel board, I would install emon dmon meter or some kind of different energy monitoring meter on those circuits. My question is does that need to tie back to a building management system or is it a wireless type of connection that the landlord knows how much kilowatt consumption has happened and can charge the tenant accordingly. How does that occurs? Please advise. Thank you.

You're on the right track! Here's a breakdown of tenant metering configurations and how the data gets to the landlord for billing

Two Basic Approaches to Tenant Metering:

1. Wired Connection to a Building Management System (BMS) or Data Acquisition System (DAS)



How it works

Each meter (e.g., Emon Dmon or similar) is wired to a central data collection point. This could be a dedicated BMS server, a DAS system, or a simpler Modbus gateway. The meters communicate their energy consumption data (kWh, kW, voltage, current, etc.) using a standard protocol like Modbus RTU, Modbus TCP/IP, BACnet, or even sometimes simple pulse output. The central system (BMS/DAS) stores the data, usually in a database. Software then processes the data, calculates tenant consumption based on meter assignments, and generates reports that can be used for billing.

Advantages



Centralized Management

All metering data is in one place, making monitoring and reporting easier.


Scalability

Easily add more meters as needed.

Integration

Can integrate with other building systems (HVAC, lighting, etc.) for more comprehensive energy management.


Potential for Advanced Features

Real-time monitoring, automated alarms, demand response.

Disadvantages



Higher Initial Cost

More complex hardware and software.

Installation Complexity

Requires running wiring and configuring network connections.


Maintenance

Requires ongoing maintenance of the BMS/DAS system.2.

Wireless Metering (Cloud-Based)



How it works

Each meter communicates wirelessly (typically Wi-Fi, Zigbee, LoRaWAN, or cellular) to a cloud-based platform. The meter transmits its data directly to the cloud. The cloud platform stores the data, performs calculations, and provides a user interface (usually web-based) for the landlord to view consumption reports. Often, there is also an API available to allow integration with third-party billing services or accounting software.

Advantages



Easier Installation

Reduced wiring complexity.

Lower Initial Cost

Potentially less expensive than a full BMS/DAS.


Remote Access

Landlord can access data from anywhere with an internet connection.

Automatic Updates

Software updates are handled by the cloud provider.


Disadvantages



Reliance on Network Connectivity

Requires reliable Wi-Fi or cellular coverage.


Data Security Concerns

Security of cloud data is a consideration (choose reputable providers).

Subscription Fees

Cloud platforms typically charge monthly or annual subscription fees.


Limited Integration

May have limited ability to integrate with other building systems.

How the Landlord Gets the Data and Bills Tenants

Regardless of the system chosen, the landlord (or their property manager) uses the collected data to generate tenant bills. The process generally involves:1.

Meter Assignment

Each meter is associated with a specific tenant space or unit.2.

Data Collection

The system automatically collects energy consumption data from each meter at regular intervals (e.g., hourly, daily, monthly).3.

Consumption Calculation

The system calculates the total energy consumed by each tenant for the billing period (typically monthly).4.

Billing Rate

The landlord establishes a billing rate (price per kWh) for electricity. This rate should comply with local regulations and may include costs like the utility's charges, plus any administrative fees for the landlord.5.

Bill Generation

The system generates bills for each tenant, showing their energy consumption, the billing rate, and the total amount due.6.

Bill Delivery

Bills are delivered to tenants electronically or by mail.7.

Payment Processing

Tenants pay their bills. Some systems can integrate with online payment platforms.

Important Considerations



Submetering Regulations

Many jurisdictions have specific regulations regarding submetering, including requirements for meter accuracy, billing practices, and tenant rights. You
must research and comply with all applicable local and state regulations.

Meter Accuracy

Choose meters that are certified for accuracy (e.g., ANSI C12.1 or equivalent). Accuracy is critical for fair billing.

Data Security

Protect the metering data from unauthorized access. Use strong passwords and encryption.


Tenant Notification

Inform tenants about the metering system and how their energy consumption will be measured and billed. Transparency is key to avoiding disputes.

Legal Review

It's highly recommended to have a lawyer review your submetering agreement to ensure compliance with local laws and to protect the landlord's interests.

Which System is Best for You?


The best system depends on factors such as:
Number of Tenants

For a few tenants, a wireless system might be sufficient. For a large building with many tenants, a BMS/DAS might be more scalable.

Budget

Wireless systems typically have lower upfront costs, but cloud subscription fees can add up over time.


Existing Infrastructure

If you already have a BMS in place, it might be easier to integrate the meters into that system.

Technical Expertise

Wireless systems are generally easier to install and maintain, but a BMS/DAS requires more technical knowledge.

In summary:
You don't necessarily need a full-blown BMS, but you do* need a system that accurately measures energy consumption, securely transmits the data, and provides a way for the landlord to generate accurate bills. Wireless, cloud-based systems are a popular choice for many applications because of their ease of installation and use. However, you must always comply with local regulations and prioritize data security. Always research and compare different options before making a decision. Flag for review