User: Alex_rg15, Location: Texas
Asked on: Friday, April 18, 2025 at 2:06 pm EDT
Answered on: Friday, April 18, 2025 at 2:06 pm EDT
Question: A 120/208, three phase system feeds a detached building with a load of 24,960VA using 1 AWG copper conductors. What is the maximum distance the feeder can be to not have a voltage drop of more than 5%?I calculate the amps first24,960 /(208*1.73) =69.364Then I calculate the 5% of the VD208 * 5% =10.4Then apply the VD formula for LL = VD * cmil / 1.73*K* IL = 10.4 * 83690 / 1.73(12.9)(69.364)L= 870376/ 1548L= 562My answer is 562 ftBut the book says 325ft
Okay, let's break down this voltage drop calculation and see where the discrepancy arises. Your overall approach is correct, but there are a couple of key areas to examine to reconcile the difference with your book's answer.
Here's a step-by-step analysis
Correct Current Calculation
You correctly calculated the current using the formula for three-phase power:
sqrt(3))I = 24960 / (208 1.732) = 69.36 amps2. I = VA / (V
Correct Voltage Drop Limit
You correctly calculated the allowable voltage drop:
3. VD = 208 0.05 = 10.4 volts
Correct CMIL Value The CMIL of a 1 AWG wire is 83,690.4. Correct K Value The K Value of copper is 12.9.
5. Voltage Drop Formula
The voltage drop formula you're using is correct, but let's use the simplified one for three-phase circuits: Voltage Drop (VD) = (1.732 K I L) / CM Where: VD = Voltage Drop (Volts) K = Constant (12.9 for copper) I = Current (Amps) L = One-Way Length (Feet) CM = Circular MilsThen we rewrite it to solve for L. L = (VD CM) / (1.732 K I)6. Calculation
L = (10.4 83690) / (1.732 12.9 69.36)L = 860776 / 1547.87 = 556.11ftThe calculation shows 556.11. So why does the book say 325ft? The book takes into consideration the adjustment factor for the cable because if the conductors are close together, they create heat. This changes the amount of amps the cable can carry.