Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Generator Voltage Drop

User: Archimedes1988, Location: New York

Asked on: Monday, April 21, 2025 at 9:42 pm EDT
Answered on: Monday, April 21, 2025 at 10:02 pm EDT

Question: Howdy partners,I just looked at a job today. There is a diesel generator that serves as backup power. They want to move the generator about 500' due to how loud it is. It is only a 10KW generator, so my calculations put me at 1 AWG wire should be sufficient.My question is: are there any adjustment factors for this since the source is a generator, or is it still the same calculation and principle?Thanks, dudes and/or dudettes.

Alright, partner! Let's wrangle this generator wiring situation.You're right to be thinking about voltage drop and ampacity over that 500-foot run. A 10kW generator powering a 120/240V single-phase system is going to be pulling a fair bit of current.Here's the breakdown, and where we need to consider factors

1. Initial Calculation and Voltage Drop:
Current Calculation

Let's assume the worst case: the generator is primarily supplying a 240V load. 10,000 Watts / 240 Volts = 41.67 Amps (approximately).


Voltage Drop Target

The NEC (National Electrical Code) recommends limiting voltage drop to 5% for feeders. For a 240V system, that's 12 Volts. Some might say 3% is preferable.

Voltage Drop Calculation

You'll need to use a voltage drop calculator or formula. There are tons online. Be sure to factor in the wire type (Copper or Aluminum) and insulation type.


Wire Size Adjustment

Based on that initial voltage drop calculation, 1 AWG may be a reasonable starting point. But verify using the actual load and wire specifics.

2. Ampacity and Code Considerations



NEC Ampacity Tables

Look up the ampacity of 1 AWG wire in NEC Table 310.16 (or the equivalent in your local code). Make sure the wire is rated for at least 41.67 Amps (plus a safety margin).


Adjustment Factors (Ambient Temperature and Number of Conductors)

Ambient Temperature: If the wire is run in a hot environment, you'll need to apply a correction factor from NEC Table 310.15(B)(1). If your ambient temperature is higher than 86°F (30°C), the wire will need to be derated. Number of Conductors in Raceway: If you're running more than three current-carrying conductors in a raceway or cable, you'll need to apply a derating factor from NEC Table 310.15(B)(3)(a). This is less likely to be an issue with a generator circuit, which typically only has 2 hots, a neutral, and a ground.

3. Generator-Specific Considerations



Generator Output Voltage

Crucially, confirm the generator's actual output voltage under load. Generators often have a voltage regulation curve. If the voltage drops significantly under load, your current draw will be higher, and voltage drop will be worse. You need the real-world voltage to calculate correctly.

Starting Current

Generators can have trouble with large inrush currents from loads like motors. Make sure your load is truly only 10kW and doesn't have any crazy starting demands.

Generator Wiring Diagram

Carefully consult the generator's wiring diagram and manual. It may have specific requirements for wiring gauge, grounding, and overcurrent protection.


Overcurrent Protection

Ensure appropriate overcurrent protection (circuit breaker or fuses) is sized according to the wire ampacity and the generator's specifications. This is critical for safety.

Grounding

Proper grounding is
essential. Follow the NEC's guidelines for grounding generators, including bonding the generator frame and potentially providing a grounding electrode system at the generator location (if required by local codes or if the generator is considered a separately derived system).

4. Other Considerations



Wire Type

Use the appropriate wire type for the environment (THHN, XHHW, etc.). If the wire is buried, you'll need to use underground-rated cable.

Conduit or Raceway

Protect the wire in conduit or a raceway for physical protection, especially if it's exposed or underground. PVC, EMT, or rigid conduit are common choices.


Terminations

Use properly rated lugs and connectors at the generator and the connection point. Torque them to the manufacturer's specifications.

Is it different because it's a generator?


The fundamental calculations (voltage drop, ampacity) are the same. However, the generator's specific output characteristics and wiring requirements are what make it unique. Don't treat it like a standard panelboard connection. Read the documentation, confirm the voltage under load, and ensure you're meeting all NEC and local code requirements. The NEC covers generators specifically in Article 445.

Recommendation


Double-Check Load Calculations

Be absolutely certain about the actual load the generator will supply. Overestimating is better than underestimating.2.

Measure Generator Voltage Under Load

This is essential.3.

Use a Reputable Voltage Drop Calculator

There are good ones online.4.

Consult a Licensed Electrician:
Given the distance and the potential for safety hazards, it's always a good idea to have a licensed electrician review your plans and perform the final connection. They can ensure everything is up to code and safe.Good luck with the project! Stay safe out there! Flag for review

Previous Question Next Question