Question: I have procedure room with procedure table that is general care space. It is served from critical circuit and one from normal circuit.Patient Bed Location definition in NEC 2017 Article 517.2 is patient bed location critical space. However NEC 2017 Article 517.18(A) is about patient bed location which is under General Care Space. I have engineer say patient bed definition is patient table in critical care but NEC 2017 Article 517.18(A) is under General Care Space about patient bed location.So my question is would NEC 2017 Article 517.18(A) apply or not to the procedure room?
This is a tricky situation that requires careful consideration of the NEC definitions and the intent of the code. Here's a breakdown to help you determine if NEC 2017 Article 517.18(A) applies to your procedure room
Key Considerations:
1. Definition of Patient Bed Location (NEC 2017 Article 517.2)
The NEC defines "Patient Bed Location" as:> "The location of a patient sleeping bed, or the room or area that normally contains a sleeping bed, in a patient care area."Your procedure table is NOT a sleeping bed. The crucial part of the definition is the intent of "sleeping bed". The code is geared towards locations where patients are intended to be lying for extended periods for rest and/or recovery.2.
General Care vs. Critical Care
This is the core of the confusion.
General Care Space (NEC 2017 Article 517.2)
"Areas in health care facilities in which it is intended that patients would be provided with only basic treatment and monitoring."
Critical Care Space (NEC 2017 Article 517.2)
"Those special care units, intensive care units, coronary care units, angiography laboratories, cardiac catheterization laboratories, delivery rooms, operating rooms, and similar areas in health care facilities where patients are intended to be subjected to invasive procedures and connected to line-operated equipment."3.
Context of NEC 2017 Article 517.18(A)
This section focuses on the specific requirements for receptacles at patient bed locations in general care areas. It aims to ensure sufficient power and redundancy where patients are normally resting/recovering.
Analysis and Application to Your Situation
Given the above, here's how to approach your scenario:
Your Procedure Room's Primary Function
The crucial question is the primary use of the room. Is it a space where patients are primarily placed for procedures (even if invasive) or for recovery/rest after a procedure? It seems like you mentioned procedure room with a procedure table, so it is primarily for procedures.
The Procedure Table vs. a "Patient Bed Location"
Your procedure table, while supporting the patient, is not a "Patient Bed Location" as intended by the definition. It's a piece of equipment used during a procedure, not a bed for rest.
Why the Engineer Might Be Confused
The engineer might be focused solely on the fact that you have a critical circuit in the room, leading them to apply the requirements for critical care spaces. However, having a critical circuit doesn't automatically make the entire room a critical care space in the way the NEC defines it.
517.18(A)'s Intent
517.18(A) is about receptacle redundancy and reliability at bedside. This is critically important where a patient is continuously connected to life-support or monitoring equipment during recovery or rest. This is not the case for the procedure table during a procedure, where the medical staff actively manages the equipment and the patient.
Conclusion
Based on the information provided, it's unlikely that NEC 2017 Article 517.18(A) directly applies to the procedure table location in your procedure room.Justification
The procedure table isn't a "sleeping bed" or a location where patients are normally placed for rest or recovery. The intent of 517.18(A) is to ensure power reliability for life-support equipment connected to patients at the bedside in a general care setting. Your procedure room falls outside of this specific scenario.
Important Considerations and Recommendations
AHJ (Authority Having Jurisdiction)
The definitive answer always comes from your local AHJ. Present your reasoning and documentation (room drawings, procedure descriptions) to them for a formal determination.
Risk Assessment
While 517.18(A) might not strictly apply, consider conducting a risk assessment. Are there specific procedures performed on the table that could be improved by having receptacle redundancy?
Good Engineering Practice
Even if not required by 517.18(A), consider the benefits of providing extra receptacles and circuit redundancy. This could be justified for patient safety and operational reasons. It may be beneficial and is not against NEC requirements.
Documentation: Document your decision-making process, including your reasoning for not applying 517.18(A) and the consultations you had with the AHJ (if applicable).In summary, while you have a general care space with a critical circuit, and a procedure table, NEC 2017 Article 517.18(A) is intended for patient beds. It does not appear the procedure table can be defined as patient bed since the purpose is for procedures, not recovery or rest. You need to confirm your decision with the AHJ or Authority Having Jurisdiction. You could implement the NEC code anyway if beneficial to the patient safety and operational reasons. Flag for review