Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 110.14 90/310.16 Degree column

User: Joseph Alexander

Asked on: Wednesday, April 30, 2025 at 9:44 am EDT
Answered on: Wednesday, April 30, 2025 at 9:44 am EDT

Question: WHY DO ELECTRICIANS THINK THEY CAN USE THE 90 COLUMN FOR 100 AMPS OR LESS? SEE 110.14 WHIC DOES NOT ALLOW GENERAL USE OF THIS COLUMN

You're right to question this! Using the 90°C column for terminations rated 100A or less is a common point of confusion, and misunderstanding it can lead to unsafe installations. Let's break down why this is a misconception and how 110.14(C) actually works.

The Core Issue: 110.14(C) and Termination Temperature Limitations 110.14(C) (Ampacity Correction/Adjustment and Conductor Termination Temperature)

This is the KEY section. It states that conductor ampacities are selected based on the

termination temperature rating
. It's not about the conductor's insulation rating (like THHN).
Why 60°C/75°C Dominance

Most termination devices (circuit breakers, switches, receptacles, etc.) rated 100A or less are marked with temperature ratings of 60°C or 75°C. This is the limiting factor. Even if the conductor insulation is rated for 90°C (e.g., THHN), you must use the ampacity corresponding to the lowest temperature rating of any termination point.

Why Electricians Sometimes Get Away With It (Or Think They Can)


Oversizing

It's tempting to think, "I'm using a THHN wire, so it can handle more amps." This is dangerous thinking. Even if the wire insulation can handle higher temperatures, the breaker, receptacle, or other termination device may not. If the wire is too small for the current, the terminal will overheat and melt, creating a hazard.2.

Misinterpretation of Correction Factors

Some electricians mistakenly believe that using correction factors for ambient temperature or conduit fill automatically allows them to use the 90°C ampacity. Correction factors are applied after selecting the initial ampacity based on the termination temperature rating.3.

Code Interpretation (Rare Exceptions)

There are very specific, limited circumstances where using the 90°C column might be permissible, but these are not general practice:

Equipment Specifically Marked

If the equipment is specifically marked and
listed for use with 90°C conductors, then you can use the 90°C ampacity. This is rare for 100A and less devices.



Derating/Adjustment Only

You can use the 90°C column only for applying ampacity adjustment or correction factors (e.g., for conduit fill or ambient temperature). You still have to base your initial ampacity selection on the 60°C or 75°C column. This means selecting a conductor that has an ampacity higher than what you need. Then apply all the adjustment and correction factors. The final value has to be equal to or exceed the overcurrent protection.

The Practical ExampleLet's say you need to run a 20A circuit. You're using THHN wire. The breaker and receptacle are rated for 75°C.1.

Incorrect (and Dangerous) Approach

"THHN is 90°C, so I'll use a 12 AWG, which is good for 30A in the 90°C column."

WRONG!2.

Correct Approach

Look at Table 310.16 for the 75°C column. To get a 20A circuit, you need a 12 AWG wire.3. Derating/Adjustment approach:

Look at Table 310.16 for the
90°C column. To get a 20A circuit, you need a 14 AWG wire. The ampacity for 14 AWG is 25. However, it must be derated due to conduit fill. With 7-9 current-carrying conductors, the derating factor is 70%. This means that the ampacity has to be multiplied by .7, meaning it is capable of 17.5 amps. This value is not equal to or greater than 20. In this case, a 12 AWG wire will need to be used instead.

Key Takeaways



Always Check Termination Temperature Ratings

Look for the temperature markings on your breakers, receptacles, and other equipment.

Start with the Lowest Temperature

The weakest link determines the chain's strength. The lowest temperature rating of any termination point determines the ampacity you use from Table 310.16.


90°C is Rarely Directly Applicable

Using the 90°C column directly for circuits rated 100A or less is almost always incorrect in typical residential and commercial wiring.*

Safety First

When in doubt, consult a qualified electrician or electrical engineer. This is a common mistake that can lead to dangerous situations.

In Conclusion


While THHN or other 90°C-rated conductors offer advantages like better resistance to heat aging and voltage drop, their higher temperature rating is often irrelevant because of the termination temperature limitations of the equipment they're connected to. Understanding 110.14(C) is crucial for safe and compliant electrical installations. Flag for review

Previous Question Next Question