Question: I'm reviewing test results from a contractor who claims to have done a fall-of-potential test at a ground test well. The readings are taken at ten foot intervals, from 10ft to 100ft, with results starting at 1.10 ohms (10ft), a bunch of 1.00 ohms (20ft-80ft), then 0.90 ohms at 90ft and 100ft. These results aren't like any I've ever seen for a fall-of-potential test. I typically see a sharp upward curve in resistance values around 60ft or so. Is it just me, or do these results seem dubious?
You're right to be suspicious. Those results are highly irregular and suggest a problem with the test, the setup, or potentially even fabricated data. Here's a breakdown of why, and what you should consider
Why the Results Are Dubious:
Lack of a Characteristic Curve
A proper fall-of-potential test should exhibit a distinct curve. Near the ground rod under test, the soil resistance is high. As you move further away with the test probe, the resistance decreases rapidly until you reach a point where the probe is effectively outside the influence of the ground rod. Beyond that point, the resistance should plateau. The 61.8% or 62% distance method helps find that plateau. Your results, with almost identical readings between 20ft and 80ft, completely lack this characteristic curve.
Extremely Low Resistance
A ground resistance of 1 ohm is generally considered excellent, even in ideal conditions. To have that reading, and consistently for 60 feet, suggests very low soil resistivity and a very effective grounding system. While possible, it's statistically unlikely unless the soil is saturated with conductive salts or you're testing in a highly conductive environment (like a salt marsh). Furthermore, the very slight decline at the end (0.90 ohms) suggests that 1 ohm isn't the true resistance of the grounding electrode, but is rather resistance introduced by the test equipment.
Unrealistic Consistency
Soil is rarely homogeneous. Variations in moisture content, soil composition, and buried objects (like rocks or utilities) will usually cause fluctuations in resistance readings at different distances. The extremely consistent 1.00 ohm readings are highly unlikely.
Implausible Drop-off
The drop from 1.10 ohms to 1.00 ohms at 20 feet is also questionable. You'd expect a more significant drop initially and then a gradual flattening.
Possible Explanations for the Strange Readings (assuming no deliberate fraud)
Bad Connections
Loose, corroded, or improperly made connections in the test circuit can introduce resistance that masks the actual ground resistance.
Insufficient Test Current
A weak test current might not be able to overcome the resistance of the soil, leading to inaccurate readings.
Probe Too Close
The auxiliary current probe might be too close to the ground rod under test or the auxiliary potential probe. The 61.8% method is important!
Probes Aligned
The auxiliary probes may not have been arranged in a straight line with the ground rod.
Incorrect Meter Settings
The meter may have been set to the wrong range or have a faulty auto-ranging function.
Nearby Underground Conductors
Buried metallic objects like pipes, fences, or utility lines can create a parallel path for the test current, skewing the results. This is particularly likely if the probes were placed near these objects.
High Soil Moisture
Very high soil moisture (after heavy rain, for example) can lower soil resistivity, but it wouldn't explain the consistent readings.
Faulty Meter
The meter itself could be malfunctioning.
Improper Probe Depth
Probes should be driven deep enough to make good contact with the soil but not so deep that they contact buried objects.
Unusually Low Soil Resistivity
While unlikely, the soil at the test location could have unusually low resistivity. Investigate the soil composition and moisture content.
What You Should Do
1.
Question the Contractor Directly
Start by asking the contractor about the specific test setup, procedures, and equipment they used. Ask for detailed explanations of any deviations from standard testing practices. Ask them to show you their field notes and calibration records for the test equipment.2.
Witness a Retest
The best approach is to require the contractor to re-perform the test while you (or a qualified representative) are present to observe and verify the procedure. Pay close attention to:
Probe Placement
Ensure proper spacing (use the 61.8% method) and linear alignment.
Connection Quality
Verify that all connections are clean, tight, and properly made.
Meter Settings
Confirm that the meter is set to the correct range and function.
Test Current
Ensure that sufficient test current is being injected into the ground.*
Probe Depth
Observe that the probes are properly inserted into the ground.3.
Independent Verification
If you have persistent doubts, consider hiring a different contractor to perform an independent ground resistance test.4.
Check for Buried Utilities
Before any testing, perform a "one-call" locate to identify any buried utilities in the area. This will help avoid damaging them and can also help explain unusual readings if utilities are near the test area.5.
Examine Soil Conditions
While not always definitive, try to get a sense of the soil composition and moisture content in the area. Is it sandy, clayey, rocky, or saturated?6.
Review Project Specifications
Review the original project specifications to ensure that the test results meet the required ground resistance values.
In Conclusion:
Your skepticism is justified. The reported results are highly unusual and warrant a thorough investigation. A retest, properly witnessed and documented, is the best way to determine the actual ground resistance and the validity of the contractor's claims. Don't accept these results at face value. Flag for review