Question: I have a 1200amp distribution board fed by (2) underground 4" sch40 PVC conduits from the secondary transformer (A huge engineering screw up but here we are). If I could get a testing company to come out and set the parameters of the breaker to 1000A then I could run parallels of (3) 1000mcm and bond the neutral buss at the panel since it is a separately derived system. The issue there is being able to fit 1000mcm mac adapters for 500mcm lugs. Anyone else out there got any bright ideas other than starting over and running the correct size and quantities of conduits? (The panel is indoors, concrete has been poured, and the building is erected).

Okay, this is a tough situation. You're right, that conduit situation is far from ideal, but let's brainstorm within the limitations. Here's a breakdown of possible options, focusing on feasibility and code compliance, along with considerations for each

Understanding the Problem and Constraints:
Undersized Conduits

The core issue is the inability to pull the necessary conductors for a 1200A service within the existing conduit.


1200A Breaker/Panel

You need to protect the panel's 1200A capacity.

Physical Constraints

Existing conduits, poured concrete, and erected building. Major conduit work is extremely undesirable.


Separately Derived System (SDS)

This implies a neutral bond at the panel, which is correct.

1000 kcmil and 500 kcmil Lug Issue

You're facing a practical problem of adapting large cables to smaller lugs.


Code Compliance

Everything must meet the NEC (National Electrical Code) and any local amendments. This isn't just about getting it to work; it's about safety and avoiding future issues.

Possible Solutions (Ranked by Feasibility/Cost, but all requiring thorough investigation)


Reduced Breaker Size (Derating) with Parallel Conductors - Your Proposed Solution (Most Likely Path)



Details

This is the path you're already exploring. Reduce the main breaker to 1000A, parallel three sets of 1000 kcmil conductors, and bond the neutral at the panel.


Advantages

Potentially avoids major construction. Maintains a reasonable current capacity.

Disadvantages



Lug Adapters

Finding UL-listed lug adapters that safely and reliably adapt 1000 kcmil to 500 kcmil lugs is critical. These adapters must be specifically rated for the application and properly installed. This is often the biggest hurdle. Look at companies like Penn-Union, Burndy, or Panduit. Document everything!



Ampacity Adjustment

Ensuring the paralleled conductors have sufficient ampacity for the derated breaker (1000A). Three 1000 kcmil conductors per phase
should be sufficient after ampacity adjustments for conduit fill and ambient temperature (NEC Table 310.15(B)(1), Table 310.16, and related sections). Verify with calculations!

Coordination

Ensuring that the breaker is properly coordinated with any downstream protective devices. A power system study might be needed.

Professional Consultation

This
requires a licensed electrical engineer to perform calculations and ensure code compliance. Don't skip this step. A PE stamp is a must-have for this project.

Important Considerations



Documentation

Extensive documentation is required. Keep records of all calculations, specifications, UL listings, and installation procedures. This is crucial for future inspections and maintenance.

Inspection

Expect a very thorough inspection. Be prepared to demonstrate compliance with every aspect of the code.

Neutral Sizing

Ensure the neutral conductor is properly sized.


Grounding

Verify the grounding electrode conductor size is appropriate for the reduced service size.

Voltage Drop Calculation

run voltage drop calculations to make sure it is within the permissible limits.2.

Current Limiting Fuses in Series with the Breaker
Details

Install current-limiting fuses in series with the 1200A breaker to effectively limit the current the transformer can push to the load.

Advantages

No changes to the breaker settings or conductor sizes are necessary.

Disadvantages

Requires additional space for the fuse block. Potential for nuisance tripping if the fuses are not properly sized. Requires careful coordination between the fuses and the breaker to ensure proper protection.

Important Considerations

Must comply with NEC 240.86: Series Ratings.
3.


Outdoor Disconnect & Current Transformers (CTs) & Metering (Least Desirable, but Possible)



Details

Install a properly sized outdoor disconnect with appropriately sized conductors immediately outside the building, fed directly from the transformer. Use Current Transformers (CTs) to monitor the current and feed that data to a metering system. The metering system would be configured to limit the current delivered to the indoor 1200A panel.


Advantages

Completely isolates the undersized conduit issue from the indoor panel. Allows for more precise control of the current.

Disadvantages

High cost. Complex installation. Requires significant space outside the building. Reliance on electronic metering for current limiting, which could raise reliability concerns.

Important Considerations

Requires a sophisticated metering system with accurate and reliable current limiting capabilities. Must comply with all applicable codes and regulations for outdoor installations.

What to Do Next


Engage a Licensed Electrical Engineer (PE)

This is the first and most critical step. They will perform the necessary calculations, assess the feasibility of each option, and ensure code compliance.2.

Contact a Reputable Testing Company

Get quotes and availability for breaker testing and setting.3.

Research Lug Adapters

If Option 1 is feasible, start researching UL-listed lug adapters. Get specifications and pricing.4.

Gather Documentation

Collect all relevant panel schedules, transformer data, and existing electrical drawings.5.

Consult with the Authority Having Jurisdiction (AHJ)

Discuss your proposed solution with the local electrical inspector to get their feedback and approval before you proceed.

Important Warnings



Do NOT Cut Corners

This is a potentially dangerous situation. Don't try to "make it work" without proper engineering and code compliance.


Beware of Non-UL Listed Solutions

Only use UL-listed components that are specifically rated for the application.*

Document EVERYTHING:
Keep meticulous records of all calculations, specifications, UL listings, and installation procedures.This is a complex problem that requires careful planning and execution. Good luck! Flag for review