Topic: festival temp power

User: rostrander, Location: new york

Asked on: Sunday, May 18, 2025 at 6:47 pm EDT
Answered on: Sunday, May 18, 2025 at 7:59 pm EDT

Question: Hi allBeen searching for a bit online I keep getting hits from this forum so I figured I would post here maybe yall can help.I am part of a non profit that puts on a festival in a village center that is a part. We have food trucks that need power. This power has ran acroos the road on the ground while road is closed. With obvious issues of a large amount of cables, ie damaged cables constant breakers tripping and …. This has also left the area people walk a dangerous mess trips and falls. Last year we had several preventable accidents in our small 3 day festival.This year I want change Power reliability and ZERO accidents. The main run across the road is 75 ft. I acquired a 175 ft roll of 4/4c so cable. The idea :fill 3 55 gallon barrels with quickcrete and set 4x6x 14ft pt posts in them.Then when set in place tie the tops together with 20ft 2x8s ( I would donate them also).I would have the cable in 1.5 inch loops attached to the 2x8 to support it .At the end of the 75 ft mount a outdoor breaker box to a plywood board,install gfci breakers and weatherproof boxes for our food trucks to plug in.The supply side would have a pin and sleeve with a breaker installed in panel.Does anyone have thoughts on this?Thanks for the input

Okay, this sounds like a well-intentioned plan with some good ideas, but also some areas that need serious scrutiny for safety, code compliance, and practicality. Let's break it down

Things I Like:
Addressing the Danger

The biggest win is recognizing the hazard of ground-level cables and taking steps to eliminate it. That's absolutely paramount.


GFCI Protection

GFCI protection for outdoor receptacles used by food trucks is a must. This significantly reduces the risk of electrical shock.

Pin and Sleeve Connection

A pin and sleeve connection is good choice for a high-current, temporary connection. These are industrial grade connectors that are made for this type of use.


Adequate Cable Size

4/4 cable should be sufficient for a reasonable load over that distance (we'll need to verify this further, see below).

Areas for Serious Concern and Refinement



Electrical Permitting and Inspection

This is non-negotiable. Any electrical work, especially temporary power distribution like this for a public event, requires a permit and inspection by your local electrical authority (city, county, or state). They will have the final say on what is acceptable and what isn't. Failing to get permits can lead to fines, shutdown of the event, and liability if something goes wrong.

Start here.
Contact your local building department or electrical inspector immediately to discuss your plans. Code Compliance (NEC - National Electrical Code)

The NEC dictates how electrical installations must be done for safety. Your plan touches on several areas where NEC compliance is critical:

Overhead Clearance

The NEC specifies minimum heights for overhead conductors above roads and pedestrian areas. Generally speaking, the minimum height for power lines over roads is 18 feet. Since you are going to tie the tops together the cables are going to be in the middle so the posts are going to need to be very tall and that's going to make them very unstable, especially for a temporary setup.


Cable Support

How you attach the cable to the 2x8 needs to be code-compliant. The cable must be properly supported to prevent strain and damage. Using loops may not be the best method; you'll want to use cable cleats or similar hardware designed for this purpose.

Weatherproof Enclosures

Using weatherproof boxes is good, but ensure they are UL-listed and rated for outdoor use (NEMA 3R or better). The breaker box enclosure needs to be the same.


Grounding

Proper grounding is absolutely essential. You'll need a grounding electrode system (ground rod driven into the earth) at the supply side, and everything must be bonded correctly according to code.

Working Space

NEC requires adequate working space around electrical equipment (like the breaker box). This is to ensure safe access for maintenance and troubleshooting.


Structural Stability



Post Height and Stability

14-foot posts are quite tall. Burying them in concrete-filled barrels
might not provide enough stability, especially in windy conditions or if someone bumps into them. You may want to consider a wider base or additional bracing. Also, 14 feet in the air plus a buried amount, plus a 2x8 might still not reach the minimum clearance requirement.

Tying the Posts Together

Tying the tops with 2x8s will help with lateral stability, but consider the weight of the cable and potential wind load. Make sure the connections are strong and well-fastened. The boards need to be rated for outside use.

Consider a Professional Structural Assessment

If you're unsure about the structural integrity, it's wise to consult with a structural engineer or experienced contractor. They can assess the site conditions and recommend a safe and stable design.


Load Calculation and Cable Sizing Verification



Total Load

You
must calculate the total electrical load (in amps) that the food trucks will draw. This means knowing the amperage requirements of each truck's equipment (appliances, lights, etc.).

Voltage Drop

Over 75 feet, voltage drop can be a concern, especially with high loads. Voltage drop causes equipment to run inefficiently and can even damage it.

4/4 Cable Capacity

While 4/4 cable is hefty, you need to
verify that it can handle the calculated load at 240V (or whatever voltage you're using) for the distance involved, including accounting for voltage drop. Online voltage drop calculators are available.

Barrel Weight and Placement

55-gallon drums filled with concrete will be very heavy. How will you move them into position? Think about the logistics of placement and removal. Make sure the ground can support the weight.

Alternative Solutions to Consider



Trenching

While more involved, trenching the cable underground (in conduit) is a very safe and permanent solution. It eliminates the overhead hazard and protects the cable from damage.

Utility Poles (If Available)

If utility poles already exist near the road crossing, you might be able to work with the utility company to run the cable overhead. This is usually the safest and most reliable option.

Here's what I recommend as your next steps


Contact Your Local Electrical Authority

This is the
most important* step. Discuss your plans with them and get guidance on permitting, code requirements, and acceptable solutions.2.

Calculate the Total Electrical Load

Get accurate amperage requirements from each food truck that will be using the power.3.

Verify Cable Sizing and Voltage Drop

Use a voltage drop calculator and consult the NEC to ensure your 4/4 cable is adequate for the load and distance.4.

Consult with a Licensed Electrician

Get a professional electrician involved in the design and installation of the electrical components. They can ensure code compliance, proper grounding, and safe connections.5.

Consider Professional Structural Assessment

Have a structural engineer or experienced contractor assess the stability of your proposed post and barrel system.6.

Explore Alternative Solutions

Evaluate the feasibility of trenching the cable or using existing utility poles.

Important Safety Reminder:
Electricity is dangerous. Do not attempt any electrical work that you are not qualified to do. Hire a licensed electrician for all electrical installations.Good luck with your festival! Safety first! Flag for review