User: Sparky2791, Location: Northeast, PA
Asked on: Wednesday, May 21, 2025 at 10:23 am EDT
Answered on: Wednesday, May 21, 2025 at 10:24 am EDT
Question: Hello!I am working on a project for a client which is a large commercial building with 2 separate tenant spaces. There is a 3-hour firewall between the 2 spaces. Each space has its own electric service, separate POCO pad mounted transformers feeding each space, and an electric room with service equipment. One service is 2500A the other is 1000A, both are 277/480V 3-phase.The tenant in each space is the same company and the service in space #1 has lots of spare load based on electric bills peak demand history, they want to take 1000A feeder from Tenant Space #1 and feed equipment in Tenant space #2. Ignoring the fact that there will be an electric feed metered from space #1 in space #2 because the buildings landlord is OK with it, this seems like it is in violation of NEC, but I cannot nail down what section to cite or if anything would allow this as an exception, like a sign at each service or something. I was going to research this tonight but thought I would start here first to get some code back up before a meeting we have regarding this.Thanks for the replies!
You're right to be concerned. While not a clear-cut violation in every single case, drawing power from one tenant space's service to supply another tenant space's equipment is generally problematic under the NEC, especially with the distinct service equipment and fire rating between the spaces. Here's a breakdown of the relevant code sections and potential issues, along with possible (but unlikely) scenarios for acceptance
Primary Concerns & Relevant NEC Sections:
1. Article 220 - Load Calculations
This is the foundation. Each service is sized based on the calculated loads within that space. Taking 1000A from the 2500A service to supply the other space significantly alters the load calculation basis. Even if the existing service appears oversized now, future tenant additions could easily overload it if this 1000A is not accounted for.
Violation
Failure to properly calculate the total load served by the 2500A service after this 1000A feed.2.
Article 225 - Outside Branch Circuits and Feeders
This article applies because you are running a feeder outside the confines of the original tenant space where the service is. You're essentially feeding one building (or part of a building) from another.
225.30 Number of Supplies
"A building or other structure shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E)." This is a very strong limiting factor. The exceptions are quite specific and unlikely to apply to your situation. They mainly relate to:
(A) Special Conditions
Where reliable power is crucial (e.g., fire pumps, emergency systems, hospitals). This doesn't sound applicable to your situation.
(B) Capacity Requirements
Where the load requirements exceed the capacity of a single feeder. Possible but unlikely given your situation and the presence of an existing adequate service.
(C) Different Characteristics
Different voltages, frequencies, or phases are required. Not relevant.
(D) Documented Switching Procedures
This applies to installations under single management where a written procedure prevents overload. This may not be what you are considering since the landlord is ok with it, meaning it might not be a single management.
(E) Integrated Electrical Systems
Coordinated electrical system with a zone equipment distribution system under a single management. Requires a written coordinated procedure, so if this is a consideration it may be a lot more work.
Violation
Highly likely violation of 225.30 unless one of the very specific exceptions can be demonstrated.
3.
Article 230 - Services
This reinforces the idea of a single service for a building or structure, and the service equipment must be designed for the entire load served.
230.2 Number of Services
Similar restriction to 225.30. "A building or other structure shall be supplied by only one service unless permitted in 230.2(A) through (D)." The exceptions are similar to 225.30, but even less likely to apply in your case because you already have two services.
Violation
Likely violation of 230.2, further solidifying the single-service rule.
4.
Article 300 - Wiring Methods
You will have to ensure all the wiring methods from space 1 to space 2 are in compliance with Article 300.
Why it's Problematic
Safety
The biggest concern is safety. The 2500A service may appear oversized now, but future load additions could overload it. The existing overcurrent protection scheme for that service isn't designed to protect the wiring within another tenant space with its own potential hazards. Coordination issues could arise.
Future Changes
What happens when Tenant #1's needs change and they need more power? Now you have a complex situation where Tenant #2 is dependent on Tenant #1's service. This complicates future lease agreements and building expansions.
Liability
If a problem arises in Tenant Space #2 that's related to the power feed from Tenant Space #1, who is liable? This creates a significant liability issue for the building owner.
AHJ Approval
This kind of installation is highly unlikely to be approved by the Authority Having Jurisdiction (AHJ). They will likely cite the above NEC violations and concerns.
Possible (But Unlikely) Scenarios for Acceptance
These are very difficult to achieve and will require extensive documentation and AHJ approval:1.
Completely Redo Load Calculations
You would need to perform very detailed load calculations for both tenant spaces, taking into account: The existing loads. The 1000A feed to the other space. Maximum potential future loads for both spaces. Prove, beyond any doubt, that the 2500A service is adequately sized even with the 1000A feed and even with future load growth in both spaces. This would require sealed calculations by a qualified professional electrical engineer.2.
Dedicated Overcurrent Protection & Coordination Study
The 1000A feeder would need dedicated overcurrent protection at the 2500A service. A full coordination study would be required to ensure that the new breaker and the downstream overcurrent protection devices in Tenant Space #2 are properly coordinated to prevent nuisance tripping and ensure selective coordination. This is expensive and requires specialized expertise.3.
Emergency or Standby Power System Transfer
700.12(I) permits feeders from a standby or emergency system to extend to a remote building, so as long as it complies with all of Article 700 or 701.
4.
Extensive Documentation & Agreement
A legally binding agreement between the building owner, both tenants, and the utility company outlining: Responsibility for the 1000A feed. Metering arrangements. Liability in case of problems. Procedures for future load changes. Termination clauses for the feed.5.
AHJ Approval
Even with all of the above, the AHJ has the final say. They may still reject the proposal based on safety concerns or code interpretations.
Recommendation
Strongly advise your client against this approach. The potential code violations, safety risks, liability issues, and the difficulty in obtaining AHJ approval make it a very risky proposition.The proper solution is to either:
Upgrade the 1000A service in Tenant Space #2 if it's inadequate.* The landlord could add capacity to the transformer feeding tenant space #2.
While the initial cost might be higher, it's a far safer, more reliable, and code-compliant solution that avoids future headaches. Flag for review