Question: Hello all,Mulling over an upcoming job and coming to an item that has me concerned. The client is planning to install some stainless steel framing and strut supports. This is for esthetic purposes only. We are planning to run standard EMT conduit with standard EMT compression fittings. For esthetic purposes we were thinking of using stainless steel for strapping purpose to match the rack etc. Our concern is of course galvanic corrosion. It’s not a corrosive environment, but there will be some moisture and humidity at times. Will the stainless steel straps in contact with the galvanized EMT cause problems down the line? What about the galvanized EMT in contact with the clients stainless strut? There also are plans for powder coated steel enclosures to be mounted to a stainless steel frame. I know the codebook talks about powder coated enclosures when referencing dissimilar metals though. Just worried about the future and want a rock solid install.Any experienced advice would be appreciated. Thanks
You're right to be concerned. Galvanic corrosion is a real issue, especially when combining dissimilar metals in environments with moisture. Here's a breakdown of the risks and potential solutions for your specific scenario
Understanding the Galvanic Series
Before diving in, remember the galvanic series is a ranking of metals based on their electrochemical potential. The further apart the metals are on the list, the greater the potential for corrosion. In your case: Stainless Steel
Generally very noble (corrosion resistant)
Powder Coated Steel
Steel with a protective coating. The integrity of the coating is key.
Galvanized Steel (EMT Conduit)
Steel coated with zinc. Zinc is sacrificial, meaning it corrodes before the steel does.
Your Specific Concerns and Mitigation Strategies
Stainless Steel Straps on Galvanized EMT Conduit
Risk
This is a high-risk scenario. Stainless steel is much more noble than galvanized steel. The galvanized coating (zinc) on the EMT will act as the anode and corrode preferentially to protect the stainless steel (cathode). Moisture will accelerate this process.
Mitigation
Best Option: Avoid Stainless Steel Straps. This is the easiest and most reliable solution. Use galvanized steel straps with a paintable or powder-coated finish to match the aesthetics. Second Best: Use Insulating Barriers. If you absolutely must use stainless straps, use a non-conductive, durable, and waterproof insulating material between the strap and the conduit. Think thick plastic shims, rubber gaskets, or specialized insulating tape specifically designed for this purpose. Ensure complete separation. The barrier has to be durable enough to withstand vibration and movement without wearing away. Third Best: Zinc-Rich Paint on EMT Conduit. Coat the section of EMT conduit that will be in contact with the stainless steel strap with a good quality zinc-rich paint. You will need to routinely monitor and repair this coating as it is sacrificial and will degrade over time.2. Galvanized EMT Conduit on Stainless Steel Strut
Risk
Similar to above, but potentially less severe depending on the surface area of contact. The galvanized coating on the EMT will corrode over time.
Mitigation
Insulating Barriers
Again, the best approach is to use insulating materials. Use plastic or rubber spacers between the strut and the conduit. Consider using stainless steel bolts with insulating washers and sleeves where they pass through the EMT.
Protective Coatings
Apply a protective coating to the stainless steel strut where it will contact the EMT. This won't prevent the EMT from corroding, but it can reduce the impact on the stainless.
Sacrificial Anode
While not a practical solution in this case, you could theoretically attach a small, replaceable zinc anode near the point of contact. However, maintaining this would be difficult.
Avoid direct contact
Depending on your design, you could use a strut with channels and use stainless steel fasteners that will not come into direct contact with the EMT conduit.
Avoid Stainless Steel Strut
As an alternative, you can opt for galvanized steel strut instead of stainless.3.
Powder Coated Steel Enclosures on Stainless Steel Frame
Risk
The risk here depends entirely on the quality and integrity of the powder coating. If the coating is flawless and remains intact, it acts as an excellent barrier, minimizing galvanic corrosion. However, any scratches, chips, or breaks in the coating will expose the steel beneath, creating a galvanic cell with the stainless steel.
Mitigation
High-Quality Powder Coating
Specify a high-quality, durable powder coating specifically designed for outdoor or potentially moist environments. Consider a two-layer system (primer + topcoat).
Careful Handling
Take extreme care during installation to avoid scratching or damaging the powder coating.
Insulating Washers/Spacers
Use insulating washers and spacers (e.g., nylon or rubber) under the mounting hardware to further isolate the enclosure from the stainless steel frame.
Regular Inspection
Regularly inspect the powder coating for any signs of damage, and repair any chips or scratches promptly with touch-up paint designed for powder-coated surfaces.
Stainless Steel Fasteners
Opt for stainless steel fasteners.
Important Considerations
Environment
While you say it's not a "corrosive" environment, even normal humidity can accelerate galvanic corrosion. If there are any airborne salts (e.g., near the coast) or industrial pollutants, the risk increases significantly.
Surface Area
The larger the surface area of the more noble metal (stainless steel) relative to the less noble metal (galvanized steel), the faster the corrosion will occur on the galvanized steel.
Moisture Traps
Design the installation to avoid creating moisture traps where water can accumulate between the metals. Provide adequate drainage.
Code Compliance
Ensure all materials and installation methods comply with applicable electrical codes and regulations.
Recommendations
Prioritize Isolation
Focus on physically isolating the dissimilar metals with durable, non-conductive barriers.2.
Consider Alternatives
Explore alternative materials for strapping and support that minimize the galvanic corrosion risk.3.
Detailed Specifications
Clearly specify the materials, coatings, and installation methods to the contractor.4.
Regular Inspections
Establish a routine inspection and maintenance program to check for corrosion and address any issues promptly.5.
Document Everything: Keep detailed records of the materials used, the installation methods, and any maintenance performed.By taking these precautions, you can minimize the risk of galvanic corrosion and ensure a long-lasting and reliable electrical installation. Remember, proper planning and attention to detail are key to success. Flag for review