Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: AA-8000 rated aluminum (article 310)

User: Nwood505, Location: Santa Fe NM

Asked on: Saturday, May 24, 2025 at 10:36 am EDT
Answered on: Saturday, May 24, 2025 at 10:49 am EDT

Question: Ok there is mention of AA-8000 in NEC 2014with a exception that is very confusing. Article 310 states that USE-2 cable is not required to be AA-8000 rated if they are not marked RHH or RHW-2. So, in 2017 I don’t see any mention of any of this requirement and now in 2020 it’s back again with no exceptions. Well all of my city supply houses are only selling the old USE-2 triplex and in my case 350 USE-2. So yesterday I was shot down by a state inspector for running 250’ of this wire in an open trench. I had called him to discuss this job in preparation before I bought materials with no mention of enforcing the AA-8000 requirement. So, I’ve talked with the head of the state electrical board to plead my case and he says that if they make an exception for me then they will need to make an exception for everyone. Basically Im the first to get slapped with this; the supply houses are freaking out and it’s costing me thousands. One supply house said that the USE-2 exception still stands.Everyone is confused about this including the state and city inspectors.. any feedback is appreciated!

Okay, this is a messy situation, and you're right, it's causing confusion for many people. Let's break down the problem and potential solutions, based on the information you've provided and my understanding of the NEC.

Understanding the AA-8000 Issue



AA-8000 Aluminum Alloy

The AA-8000 aluminum alloy is specifically designed to improve the resistance to creep and relaxation in electrical connections. This is crucial for aluminum conductors, which are more prone to expansion and contraction than copper, leading to loose connections and potential fire hazards.


NEC's Position

The NEC has been moving towards requiring AA-8000 aluminum conductors, particularly for larger sizes, to enhance safety and reliability.

Code Changes

The issue is the inconsistency across code cycles and the seeming disappearance and reappearance of exceptions.

Analysis of Your Situation


The Inspector's Ruling

The state inspector is correct in citing the 2020 NEC requirement for AA-8000 conductors. Since there's no exception listed for USE-2, it technically
is required. The fact that it wasn't mentioned in your pre-job discussion is unfortunate but doesn't change the code.2.

The USE-2 Exception (Past Codes)

You are correct that previous code cycles (particularly 2014) had an exception related to USE-2 that wasn't marked RHH/RHW-2. The logic behind that exception
may have been that the insulation properties of USE-2 provided a certain level of protection, reducing the need for AA-8000. However, that exception is GONE in the 2020 NEC.3.

Supply House Inventory

Supply houses are often slow to update their stock to the latest code requirements. They may be selling what they have in inventory, even if it's no longer fully compliant. This is a common problem and
not a valid reason to disregard the code.4.

Head of State Electrical Board's Position

The head of the state board is right to be hesitant to create an exception on the fly. Doing so sets a precedent and potentially undermines the integrity of the code.

Possible Solutions and Actions


Negotiate with the Inspector (Focus on Connection Methods)

While the inspector is correct on the letter of the code, see if you can work out an alternative that achieves the same safety goal. This is a long shot, but it's worth trying.

Focus on the Connections

Emphasize that you will use
approved and properly installed connectors and terminations designed specifically for aluminum conductors. Provide documentation of these connectors and their listing information (UL, etc.). Show that you'll use anti-oxidant compound (e.g., NOALOX) to prevent oxidation at the connections.

Torque Connectors Properly

Demonstrate that you will torque the connectors to the manufacturer's specifications using a calibrated torque wrench. The inspector might be willing to accept this if you can convincingly demonstrate that you are taking all necessary precautions to mitigate the risks associated with non-AA-8000 aluminum.2.

Seek a Formal Interpretation/Variance (Difficult, but Possible)

Go through the formal channels for requesting a code interpretation or variance from the state electrical board. This is a formal process that requires submitting a written request with supporting documentation. The chances of success are low, as the board is reluctant to create exceptions, but it's worth exploring. This process will take time, so it's likely not a short-term solution.3.

Replace the Wire

(Most likely outcome) This is the most expensive but likely the only truly code-compliant option. Talk to your supply house. They should be willing to take back the non-compliant wire, especially if they misrepresented its compliance. Negotiate the best possible return arrangement. Source AA-8000-rated USE-2 cable from another supplier. Be prepared to pay more and potentially wait for delivery.4.

Document Everything

Keep meticulous records of all communication with inspectors, suppliers, and the state electrical board. Take photos of the cable you purchased, including the markings. Save all receipts and invoices. This documentation will be essential if you pursue a legal claim against the supplier or need to defend your actions later.5.

Advocate for Code Change Clarification

After you've resolved your immediate problem, consider contacting organizations like the NFPA (the organization that publishes the NEC) to request clarification on the AA-8000 requirements for USE-2 cable. Explain the confusion it's causing in the field. This might lead to a more clearly defined rule in future code cycles.

Important Considerations



Safety First

The NEC is designed to protect people and property. While it's frustrating to be caught in a code interpretation issue, remember that the underlying goal is safety.


The Inspector's Authority

The inspector has the final authority to interpret and enforce the code on the job site. It's important to be respectful, even if you disagree. Arguing and becoming confrontational will likely only make the situation worse.

Liability

You, as the installer, are ultimately responsible for ensuring that the work complies with the code.

Recommendations for the Future



Verify Code Compliance Before Purchase

Before buying any electrical materials, always verify that they meet the current code requirements for your specific application.

Consult with Inspectors Early

Continue consulting with inspectors before starting a job, especially if there's any ambiguity about the code. Get their interpretations in writing, if possible.


Stay Updated on Code Changes

Regularly review updates to the NEC and attend training courses to stay informed about changes in the code.*

Choose Reputable Suppliers

Work with reputable suppliers who are knowledgeable about code requirements and sell compliant products.

In conclusion,
while it's frustrating to be caught in this situation, the most likely outcome is that you'll need to replace the wire with AA-8000-rated cable. Explore all other options first, but be prepared to make the necessary investment to ensure code compliance and safety. Don't let the supply house's inventory dictate your code compliance! Flag for review

Previous Question Next Question