Question: What is the best way to join 2" RMC, untreaded to 2 " PVC Schedule 80, unthreaded?We're doing this in a remote area , on an island, and its going to be pretty hard to Bring a heavy pipe threader ou there.Thank you in advance
Okay, joining 2" Rigid Metal Conduit (RMC) to 2" Schedule 80 PVC pipe without threading the RMC in a remote location presents a few challenges. Here's a breakdown of the best options, considering factors like reliability, availability, and ease of implementation given your constraints
Best Option (Most Reliable and Code-Compliant)
RMC Coupling to a PVC Adapter
This is generally the most reliable and preferred method, especially when grounding is a concern.1.
RMC Coupling (Set-Screw or Compression)
Use a 2" RMC coupling designed for joining RMC. Set-screw couplings are typically easier to install in the field without specialized tools compared to compression couplings (which may require a wrench for proper torque).2.
RMC to Female PVC Adapter
This adapter has a threaded end that screws into the RMC coupling and a smooth socket end to which you can glue your PVC pipe. It is a metal threaded fitting with a PVC socket end designed for this purpose.3.
PVC Cement
Use the correct PVC cement for Schedule 80 PVC.
Installation Steps
Slide the RMC coupling onto the end of the RMC pipe. Tighten the set screws securely, or tighten the compression ring (if using a compression coupling). Thread the RMC to PVC adapter into the open end of the RMC coupling. Clean the inside of the PVC adapter socket and the outside of the PVC pipe end with PVC cleaner/primer. Apply PVC cement liberally to both surfaces and quickly insert the PVC pipe into the adapter socket. Twist slightly as you insert. Hold firmly for the recommended time (as per the cement instructions) to allow the joint to cure.
Pros
Strong, reliable connection. Provides grounding continuity (through the metal RMC coupling). Code-compliant in most jurisdictions. Uses readily available parts. Relatively easy to install with basic tools (screwdriver/wrench).
Cons
Requires purchasing specific adapters. RMC couplings, especially set-screw types, must be properly tightened to ensure a secure connection and maintain grounding.
Other Options (With Considerations) Mechanical Coupling (e.g., Gruvlok or Similar)
These are designed to join different types of pipe without threading or welding. They consist of a grooved fitting and a gasket/seal. You would need a special tool to groove the RMC pipe.
Pros
Can join dissimilar materials; doesn't require threading.
Cons
Requires the correct size and type for your application. Grooving tools can be heavy and require power. The reliability of grounding needs to be verified (often requires grounding straps). May be more expensive and harder to source in a remote location.
Direct Burial Rated Heat Shrink
There exist direct burial rated heat shrink products designed for sealing and protecting underground splices and connections. These are thicker than standard heat shrink and provide a waterproof seal.
Pros
Can provide a waterproof seal.
Cons
Not ideal for a rigid mechanical connection.
Note
If you use heat shrink, you still need to bridge the physical gap. Consider using the internal sleeve of an RMC coupling, or a short piece of PVC pipe, to span the connection and provide mechanical strength before applying the heat shrink.
Important Considerations for Your Remote Location
Weight and Portability
Prioritize the lightest and most compact solutions to minimize transport costs and effort. RMC couplings and adapters are relatively small and lightweight.
Tool Requirements
Choose a method that requires minimal specialized tools. Set-screw RMC couplings only need a screwdriver.
Availability of Supplies
Check with local suppliers or hardware stores on the island before you commit to a solution. Make sure you can actually obtain the necessary parts. Order in advance if needed.
Corrosion Resistance
Consider the environment (saltwater, humidity, etc.). Use corrosion-resistant materials or coatings if necessary.
Grounding
Critical. If the RMC is used for grounding, you must maintain grounding continuity across the joint. The RMC coupling and adapter method provides the best path. If using a non-conductive method, use a suitable grounding clamp and bonding jumper to connect the RMC and PVC.
Code Compliance
Check local electrical codes and regulations to ensure your solution is compliant. The coupling and adapter method is generally the most likely to meet code requirements.*
Strain Relief
Support the piping on both sides of the joint to minimize stress on the connection. This is especially important if there is any movement or vibration.
Recommendation
Start by sourcing the
RMC coupling and PVC adapter locally. If they are available, this is the preferred method due to its reliability, grounding capability, and relative ease of installation. If these are not available, the mechanical coupling can be a potential choice but verify availability and that you have the correct tool.Before you start the job, plan your process well, gather all the necessary materials and tools, and consider a trial run if possible. Good luck! Flag for review