User: wwhitney, Location: Berkeley, CA
Asked on: Wednesday, May 28, 2025 at 12:28 pm EDT
Answered on: Wednesday, May 28, 2025 at 12:29 pm EDT
Question: Say I have a 2000' long 2-wire #12 Cu 120V branch circuit for a very small load, 1A. #12 Cu is 2 ohms/kft per Chapter 9 Table 9, so the round-trip resistance is 8 ohms, meaning the voltage drop is only 8V, which may be acceptable. Does the NEC permit protecting this circuit at 20A?At 8 ohms and 120V, the AFC at the far end is at most 15A. So a fault there will never trip a 20A OCPD, you'll just indefinitely have a 2000' long 1800W heater. Is there an NEC section that requires the circuit to be designed to avoid this outcome?Thanks,Wayne
You've correctly identified the potential problem with using a 20A breaker on such a long run with a small load. While the voltage drop might be acceptable according to some standards, the NEC is concerned with safety, especially regarding fault currents and potential for fire.Here's a breakdown of the relevant NEC considerations:1. Voltage Drop (NEC 210.19(A)(1) Informational Note 4 and 215.2(A)(3) Informational Note 2)
While not mandatory for branch circuits, the NEC provides recommendations on voltage drop. Typically, a maximum of 3% voltage drop for branch circuits and 5% for feeders is considered ideal. In your case, the voltage drop is approaching the 7% mark so it warrants further examination.2.
Overcurrent Protection (NEC 240.4)
This is the crucial section. While 240.4 allows for overcurrent protection based on ampacity, it doesn't override other safety considerations.
3.
Fault Current Interruption (NEC 110.9 and 110.10)
These sections are critical and directly address your concern.
110.9 Interrupting Rating
The overcurrent protective device must have an interrupting rating sufficient for the available fault current at its location. This is generally not a problem for standard breakers in residential/commercial settings.
110.10 Circuit Impedance, Short-Circuit Current Ratings, and Other Characteristics
This is the key section. It states that the overcurrent protective devices, circuit impedance, component short-circuit current ratings, and other characteristics shall be selected and coordinated to permit the circuit protective devices used to clear a fault such that the equipment damage is minimized and the occurrence of a fire or shock hazard is minimized.Your scenario directly violates 110.10. Because the fault current at the end of the 2000' run is only 15A, a 20A breaker will not clear the fault. This means a persistent, high-resistance fault could lead to overheating, insulation breakdown, and potentially a fire. You're essentially creating a long, low-wattage heater. The breaker will simply never trip, allowing the problem to persist.4.
240.4(D) Protection of Flexible Cords and Fixture Wires
While this mainly focuses on flexible cords and fixture wires, it highlights the NEC's concern about protecting conductors against overcurrent. This is relevant because your #12 wire is effectively acting as a very long, fixed "flexible cord" in this scenario.
Why a 20A Breaker Isn't Acceptable
The fundamental issue is that the 20A breaker is sized far too large for the fault current available at the end of the long run. It will not provide adequate protection against a ground fault or short circuit. A breaker that allows 15A to flow continuously into a high-resistance fault without tripping is a fire hazard.
Solutions
Reduce the Overcurrent Protection
Use a breaker with a lower trip rating, such as a 15A breaker. However, you need to ensure that the 15A breaker will interrupt a fault at the far end of the run. Based on your calculations, the fault current is 15A, so you would need an OCPD rated lower than 15A to reliably clear a fault.2.
Increase the Wire Size
Use a larger wire size (e.g., #10 or #8) to reduce the resistance and increase the fault current at the load. This would allow a 20A breaker to trip in a fault situation. Calculate the required wire size using the NEC voltage drop formulas (Chapter 9, Table 8) and verifying that the fault current at the load will be high enough to trip the OCPD within a reasonable time.3.
Add a Local Overcurrent Protective Device
Install a smaller overcurrent protection device closer to the load (e.g., at a subpanel or using a fused disconnect). This provides localized protection against faults at the end of the long run.4.
Consider AFCI/GFCI Protection
An Arc Fault Circuit Interrupter (AFCI) breaker might trip on a high-resistance arcing fault, but it's not guaranteed and relies on the specific characteristics of the arc. A Ground Fault Circuit Interrupter (GFCI) would protect against ground faults, but not necessarily against a short circuit. AFCI/GFCI supplement overcurrent protection; they do not replace it.
In summary, while the voltage drop might be considered acceptable according to some guidelines, the NEC prioritizes safety. Using a 20A breaker on a 2000' run of #12 wire with a 1A load is unsafe because it creates a situation where a fault current can persist without tripping the breaker, potentially leading to overheating and fire. You must ensure that the overcurrent protection device will reliably clear a fault at the load, as required by NEC 110.10. Choose a breaker size and wire gauge combination that guarantees fault clearing. Flag for review