Question: Just to be sure, if I use 6-6-8 CU SEU, that can be on a 60 amp breaker for a Tesla charger set at 48 amps and SEU can be used in the 75 ° column and that's good for 65 amps, correct? I'm assuming the difference between SEU, that can be used in the 75° column and Romex has to be used in the 60° column is the insulation?
Let's break down the code requirements and what you're proposing to make sure everything is safe and compliant. You're on the right track, but there are a few crucial points to clarify.
Key Concepts and NEC Rules
Ampacity
The maximum current a conductor can carry continuously without exceeding its temperature rating.
Overcurrent Protection
A circuit breaker protects the wiring from overheating and potentially causing a fire. The breaker's amperage rating should never exceed the ampacity of the wiring.
Continuous Load
A load that operates for 3 hours or more. EV chargers are considered continuous loads. NEC requires you to size the wiring and overcurrent protection at 125% of the continuous load.
Temperature Ratings
Wiring is rated for specific temperatures. You must use the correct ampacity column in the NEC tables based on the lowest temperature rating of any termination point (breakers, receptacles, etc.).
SEU Cable
Service Entrance Cable, Underground. Typically used for the main power feed to a building. SEU cable typically has a 75°C insulation rating.
NM-B Cable (Romex)
Nonmetallic-sheathed cable. Romex cable is typically rated for 60°C.
Terminations
Most breakers and receptacles are rated for 75°C terminations. Always confirm.
Your Scenario (Tesla Charger at 48 Amps)
Continuous Load Calculation
48 amps (charger setting) 1.25 = 60 amps. This means your wiring and breaker need to be rated for at least 60 amps.2.
Breaker Size
You want to use a 60 amp breaker. This is acceptable because it protects the wiring from overcurrent and the 60 amp breaker is sized at 125% of your 48 amp charger.3.
Wire Size and Ampacity
You are considering 6-6-8 CU SEU cable.
75°C Column
Assuming your breaker and receptacle are rated for 75°C connections, then yes, you can use the 75°C column in NEC Table 310.16 (or your local equivalent).
6 AWG Copper
According to the 75°C column in the NEC Table 310.16, 6 AWG copper wire is rated for 65 amps.
4.
Suitability of SEU Cable
You are correct that one of the differences is the insulation. SEU cable is usually rated for higher temperature which allows it to be used in the 75° column.
So, let's put it all together
Charger Setting
48 amps
Breaker
60 amp (Calculated for a continuous load of 60 amps (48 1.25))
Wiring
6-6-8 CU SEU Cable
Temperature Rating
Using the 75°C column.
6 AWG Copper Ampacity
65 amps (exceeds the continuous load requirement)
Yes, in this scenario, using 6-6-8 CU SEU cable on a 60 amp breaker for a 48 amp Tesla charger is compliant with the NEC code if your termination points are rated for 75C.
Important Considerations and Potential Issues
Local Codes and Permits
Always check with your local electrical inspector for specific requirements in your area. They may have stricter rules or interpretations of the NEC.
Voltage Drop
For long runs, calculate voltage drop to ensure the charger receives adequate voltage. Undersized wiring can cause voltage drop, leading to slow charging or even damage to the charger.
Professional Installation
It is highly recommended to have a qualified electrician perform the installation. They will be familiar with local codes and ensure the installation is safe and compliant.
Grounding
Make sure you have a proper grounding conductor run with the circuit. The #8 is likely for the ground wire.*
Mechanical Protection
Protect the cable from physical damage where it is exposed.
In summary, your analysis appears correct, BUT you MUST confirm the temperature ratings of your breakers and the device terminals, and follow all local codes and permit requirements. It is strongly recommended to hire a qualified electrician. Flag for review