Question: I'm gunna use tandem breakers for two separate shared neutral branch circuits: By connecting one shared circuit on the first handle of each tandem then the other shared circuit on the second handle of each tandem, so each shared neutral is not on the same phase then tie all four handles with listed ties, identify, bundle, blah, blah, everything MWBCs require... what do you think?

Okay, let's break down your plan and address the potential issues and code considerations. What you're proposing aims to create two Multi-Wire Branch Circuits (MWBCs) using tandem breakers and a handle tie to ensure simultaneous disconnect. Here's a detailed analysis

Understanding the Goal:

The intention is to have two MWBCs that share neutrals, but are fed from different phases to avoid overloading the neutral conductor. Tandem breakers are being used to save space in the panel. Handle ties are essential for safety and code compliance when dealing with shared neutrals.

The Plan (with some elaboration)


Tandem Breakers

Using tandem breakers, which are designed to allow two circuits to occupy a single breaker space.2.

Shared Neutral Circuit 1 (SN1)

Connect the hot wire of the first leg of SN1 to the first handle of one tandem breaker. Connect the hot wire of the first leg of SN1 to the first handle of another tandem breaker.3.

Shared Neutral Circuit 2 (SN2)

Connect the hot wire of the second leg of SN2 to the second handle of one tandem breaker. Connect the hot wire of the second leg of SN2 to the second handle of another tandem breaker.4.

Neutral Sharing

Properly and safely connect the neutral conductor for the first leg of SN1 and neutral conductor for the first leg of SN1. Do the same with the second leg of SN25.

Handle Ties

Mechanically connect all four handles of the tandem breakers together using a listed handle tie. This is crucial.6.

Identification

Clearly identify all conductors associated with each MWBC, including the neutral(s), at the panel and at each outlet box. This means marking the wires with colored tape, labeling, or some other approved method.7.

Bundling

Bundle all conductors of each MWBC together, at least at the panel and in any junction boxes.

Advantages of This Approach (if executed correctly)



Space Savings

Tandem breakers allow for more circuits in a crowded panel.


Balanced Load

By splitting the load across two phases, you minimize neutral current.

Simultaneous Disconnect

The handle tie ensures that all hot conductors of an MWBC are disconnected simultaneously, which is a critical safety feature for working on the circuit.

Potential Problems and Code Compliance Concerns



Breaker Compatibility



Crucial

Make absolutely sure the panel
specifically allows the use of tandem breakers in the locations where you intend to install them. Many panels only allow tandem breakers in certain slots, or not at all. Check the panel's labeling or consult the manufacturer's documentation. Using tandem breakers where they are not permitted is a code violation and a fire hazard.



Handle Tie Listing



Absolutely Critical

The handle tie
must be listed for use with the specific breakers you are using. Do not use generic handle ties. They might not provide a secure and reliable connection. The handle tie must be suitable to connect all four handles together. (Many are only designed for two).

Neutral Connections



Proper Termination

The neutral conductors must be properly terminated at the neutral busbar. Ensure a solid, secure connection. If you need to pigtail multiple neutrals to a single terminal, make sure the terminal is rated for multiple conductors and that you use an approved method (e.g., a wire nut or a listed connector).


Overcurrent Protection



Correct Breaker Size

Make sure each breaker is sized appropriately for the wire gauge and the expected load.


MWBC Requirements



Simultaneous Disconnect

NEC 210.4(B) requires a means to simultaneously disconnect all ungrounded conductors of an MWBC at the point where the branch circuit originates. The handle tie accomplishes this.


Neutral Identification

NEC 200.4(D) and 210.5(C) require proper identification of the neutral conductor(s) and require that if the premises wiring system has a grounded conductor that is required to be identified, ungrounded conductors shall be identified by phase or system.

Local Codes

Always check with your local building department for any specific requirements or amendments to the National Electrical Code (NEC).

Important Considerations & Recommendations



Professional Advice

This is a somewhat complex wiring scenario. If you are not extremely comfortable with electrical work and the NEC, hire a qualified electrician. Electricity is dangerous, and mistakes can be fatal.

Load Calculation

Before adding any new circuits, perform a load calculation to ensure that the service panel and the overall electrical system can handle the additional load.


Detailed Documentation

Keep a detailed record of your wiring, including a circuit diagram. This will be helpful for future troubleshooting and maintenance.

Inspection

Have the work inspected by a qualified electrical inspector.

In summary, your plan
could work, but only if you pay very close attention to all the details, use the correct components, and follow all applicable codes. The key is proper breaker compatibility, a properly listed and installed handle tie, correct neutral connections, and adherence to all MWBC requirements. If you have any doubt, consult a professional electrician.

Disclaimer:
* I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Always consult with a qualified electrician for any electrical work. Improper electrical work can lead to fire, injury, or death. Flag for review