Question: Hello,I am looking to install several battery systems on a 600a delta high leg 3 phase service. This means this service has 120/240 with a 208v high leg.The panels within this site I am looking to back up are only 120/240 and do not contain the high leg, they are not 3 phase(although there are 3 phase panels on site).My initial thinking is to install several individual residential 120/240 systems and a battery or 2 to each panel.My concerns are that these systems are designed for a proper 120/240 single or split phase service.Would there be issues with tying them into this service? Each of these panels that will be backed up have 3 wires and a ground-120/240, they each get 2 phase conductors from 2 of the 3 phases in this building's service.Is this truly the same as a split phase 120/240? I would think that those 2 phases are 120 degrees out of sync(being from a 3 phase service) where a standard split phase has 2 conductors 180 degrees out of sync.There will also be solar on site here(say several powerwalls with mods and MCI's on the roof)I am worried that powerwall(or any resi ESS system) will not output PV with the correct sine wave configuration.So far I have reached out to several manufacturers trying to find a solution, the response I've gotten from each so far has been something along the lines of "this should work" or "this could work"Has anyone done this with success?Thank you
You've hit on some critical points. You're right to be concerned; simply assuming a 120/240 single-phase battery system will work seamlessly with a delta high-leg service supplying 120/240 single-phase loads is risky. "Should work" and "could work" are not good enough when dealing with potentially expensive equipment and safety issues.Here's a breakdown of the issues and potential solutions
Understanding the Delta High-Leg Issue
Phase Angle Difference
You're absolutely correct. A standard split-phase 120/240 system has two 120V legs that are 180 degrees out of phase. In your case, the 120V legs derived from two phases of the delta high-leg service are 120 degrees out of phase. This difference, while seemingly minor, can wreak havoc on systems designed for 180-degree phase separation.
Residential System Design
Residential battery systems (like Powerwalls) are designed assuming a perfect 180-degree split-phase. The internal voltage monitoring and control algorithms are built around this assumption.
Potential Problems
Overheating/Inefficiency
The mismatched phase angle can lead to reactive power issues, increased current flow, and overheating of components, especially in the battery inverters.
Harmonic Distortion
The incorrect phase relationship can introduce harmonic distortion into the system, affecting the performance of other sensitive electronic equipment connected to the same service.
Synchronization Issues
If the battery system tries to "synchronize" with the grid during a transfer (or when exporting power), the phase angle difference can cause problems, potentially damaging the inverter or causing it to shut down.
Metering and Control Errors
The system might misinterpret voltage and current readings, leading to incorrect charging/discharging behavior and inaccurate energy metering.
Solar Inverters
Solar inverters feeding the panels backed up by the Powerwall/ESS system will be affected in the same way, they will struggle to put out a correct sine wave when using this service configuration.
Why "Should Work" Isn't Enough
Manufacturer responses of "should work" or "could work" are concerning. This indicates they haven't fully tested or verified the system's compatibility with a delta high-leg service. You need a guarantee or detailed specifications explicitly stating compatibility.
Possible Solutions and Considerations1. Isolation Transformer/Phase Converter (Best Solution, Most Expensive)
The most reliable solution is to install a dedicated phase converter or isolation transformer to convert the 3-phase delta service into a true 120/240V split-phase service for the panels you want to back up. This effectively creates a clean, compatible power source for the residential battery systems. The transformer/converter needs to be sized appropriately to handle the maximum load of the backed-up panels. This adds cost and space requirements, but it eliminates the compatibility issues.2.
Commercial/Industrial Battery Systems (Potentially Acceptable, Still Requires Due Diligence)
Explore commercial or industrial battery systems specifically designed for 3-phase services, including delta high-leg. These systems are built with more robust controls and often have phase angle adjustment capabilities.
Crucially, you must verify that the system can output 120/240V single-phase power suitable for your existing panels. Many commercial systems output 3-phase power only. Even with "compatible" commercial systems, get written confirmation and detailed specifications from the manufacturer.3. Careful Selection of Compatible Equipment (Highest Risk, Requires Extensive Research)
If you're determined to use residential-style systems, you need to meticulously research and test equipment that is known to work with delta high-leg. This will require extreme due diligence.
You'll need to find documentation (application notes, white papers, or direct communication with the engineering team) showing that the system is designed to handle the 120-degree phase angle. Testing is critical. Set up a small-scale test system before committing to a full-scale installation. Monitor voltage, current, temperature, and harmonic distortion carefully. Be prepared to void warranties. Using equipment outside its intended operating parameters may invalidate the manufacturer's warranty.4. Dedicated Single-Phase Service (Possibly Impossible, Requires Utility Coordination)
Explore the possibility of having the utility provide a separate, dedicated single-phase 120/240V service for the panels you want to back up. This may be expensive or not feasible depending on the utility's infrastructure and policies.
Critical Steps to Take
Consult with a Licensed Electrical Engineer (PE)
This is not a DIY project. A PE can perform a load analysis, evaluate the existing service, and design a safe and compliant system. They can also help you evaluate the compatibility of different battery systems.
Contact the Battery System Manufacturers' Engineering Departments
Don't rely on sales reps. Speak directly with the engineers who designed the systems. Ask for detailed specifications and test results related to operation on a delta high-leg service. Get their assurances in writing.
Check Local Electrical Codes and Regulations
Ensure that your proposed installation complies with all applicable codes and regulations. This may require permits and inspections.
Thorough Testing
Whatever solution you choose, thoroughly test the system before commissioning it for regular use. Monitor all critical parameters to ensure safe and reliable operation.
In summary, avoid assumptions. Using residential-style battery systems designed for 180-degree split-phase on a 120-degree derived single-phase supply from a delta high-leg service is a high-risk proposition. A phase converter/isolation transformer is the most reliable solution. If not, very careful planning, research, and testing are essential. Consulting with a qualified electrical engineer is crucial. Flag for review