Topic: Running 480V overhead poles for temporary power: wire type etc.?

User: donw, Location: Arizona

Asked on: Friday, June 13, 2025 at 11:26 am EDT
Answered on: Friday, June 13, 2025 at 11:26 am EDT

Question: I am working on a project where they need temporary power run around 1000' or a little more to some portable offices. Since it's temporary, they don't want to get the power company to run power over there, so they are talking about running 480V overhead using private poles. I've never designed a system like this before. What kind of wire? I assume we need a ground, since there will be overcurrent protection at the source. Any other details I may be missing, maybe details about poles and minimum height?

You're right to be cautious and ask questions. Designing and installing a temporary 480V overhead power system requires careful consideration of safety, code compliance, and practical implementation. Here's a breakdown of the key aspects

Disclaimer:

I am an AI chatbot and cannot provide professional engineering advice. This information is for educational purposes only and should not be substituted for the advice of a qualified and licensed electrical engineer. Any electrical work should be performed by licensed and experienced electricians, following all applicable codes and regulations.Key Considerations


Code Compliance (NEC and Local Regulations)

This is the

most critical
factor. Temporary installations still need to meet the requirements of the National Electrical Code (NEC) and any stricter local codes or ordinances. You must consult with your local electrical inspector or authority having jurisdiction (AHJ) before you start any design or installation. They will have the final say on what's acceptable. Expect scrutiny, as temporary power, especially at 480V, raises safety concerns.2. Engineering Design

A licensed electrical engineer should perform load calculations, voltage drop calculations, and conductor sizing to ensure the system can safely and reliably handle the expected load from the portable offices. They will also design the grounding system and specify appropriate protective devices. This is essential to ensure safety and compliance.3.

Load Calculation



Determine the total power demand

Get accurate information on the power requirements of each portable office. This includes lighting, HVAC, computers, appliances, and any other equipment that will be used. Don't underestimate; it's better to overestimate slightly.


Diversity factor

Can you apply a diversity factor? Will all loads be running simultaneously? (Consult with the portable office users).

Account for future expansion

Consider if there's a possibility of adding more portable offices or equipment later.4.

Voltage Drop

At 1000+ feet, voltage drop is a major concern. The NEC recommends no more than 3% voltage drop on feeder circuits and 5% overall (feeder + branch circuits). The engineer will perform voltage drop calculations based on the conductor size, current, and distance. Using a larger conductor than the minimum required for ampacity may be necessary to meet the voltage drop requirements. 480V helps mitigate voltage drop compared to lower voltages.5.

Conductor Selection



Type

Use conductors rated for outdoor use and direct burial if portions will be buried. Common choices include:

Triplex or Quadplex (Aluminum)

These are commonly used for overhead services. They are relatively inexpensive and lightweight. However, aluminum has a higher resistance than copper, so larger sizes may be needed to address voltage drop.


Copper Conductors

Copper has better conductivity than aluminum, allowing for smaller conductor sizes for the same ampacity and voltage drop. However, copper is more expensive. Types like THHN/THWN-2 are suitable when installed in conduit.

Size

The conductor size will be determined by:


Ampacity

The conductor must be rated to carry the calculated load current, plus a safety factor (typically 125% for continuous loads).

Voltage Drop

As mentioned above, voltage drop calculations are crucial.


Insulation

Must be rated for the voltage and environmental conditions (wet/dry, temperature).

Neutral vs. Ground



Neutral

If you are feeding single-phase 120V/240V loads from a 480V source via transformers, you will need a neutral conductor.

Ground (Equipment Grounding Conductor - EGC)

This is
mandatory for safety. It provides a low-impedance path for fault current back to the source, allowing the overcurrent protective devices (circuit breakers or fuses) to trip and clear the fault quickly. This prevents dangerous voltage on exposed metal parts. The EGC can be bare or insulated and must be sized according to NEC Table 250.122, based on the size of the overcurrent protection device.
6.


Grounding System



Source Grounding

Ground the neutral (if present) at the source transformer. Follow NEC 250 guidelines.

Equipment Grounding

As mentioned above, all metal enclosures, equipment, and raceways must be properly grounded.


Ground Rods

Depending on the soil conditions and the size of the system, you may need ground rods at the source and/or at the portable offices. Spacing and resistance requirements are detailed in NEC Article 250. Testing the ground resistance is important.
7.


Poles



Material

Wood, steel, or fiberglass poles are common. Wood poles are often the most cost-effective for temporary installations.


Height

The height of the poles must be sufficient to provide the required clearance above ground, roadways, and other obstructions. See NEC 225.18 and 230.24 for specific clearance requirements. Generally, you need a minimum of 18 feet of clearance over public roads and driveways, and 12 feet over residential property and other areas subject only to pedestrian or light vehicle traffic. These are minimums, and local codes might require more. Consider future use and potential changes in grade.

Spacing

Pole spacing depends on the conductor sag and the wind load. The engineer will calculate the appropriate spacing to ensure that the conductors do not sag too low or come into contact with each other. Shorter spans are safer and require less tension on the conductors.


Anchoring

Poles must be securely anchored in the ground to resist wind loads and conductor tension. The depth of the pole setting will depend on the soil conditions, pole height, and wind load.

Guy Wires

For end poles and corner poles, guy wires may be necessary to provide additional support.


Pole Top Hardware

Use appropriate insulators, crossarms, and hardware to support the conductors.8.

Overcurrent Protection



Source

Install a properly sized circuit breaker or fused disconnect switch at the source of the power to protect the conductors and equipment.


Portable Offices

Each portable office should have its own overcurrent protection (circuit breakers or fuses) to protect the branch circuits and equipment within the office.

Coordination

The overcurrent protection devices must be properly coordinated to ensure that a fault on one branch circuit does not trip the main breaker at the source.9.

Transformers (Step-Down)



If required

If the portable offices require 120V/240V power, you will need to install step-down transformers at the office locations to convert the 480V to the required voltage.

Location

Transformers can be pad-mounted or pole-mounted.


Protection

Transformers must be protected by overcurrent devices on both the primary (480V) and secondary (120V/240V) sides.10.

Disconnecting Means



At Each Building/Office

You must provide a readily accessible disconnecting means at each portable office to allow for complete de-energization of the electrical system within the office (NEC 225.31).
11.


Ground Fault Protection

While not always required, consider ground fault protection (GFP) on the 480V system, especially if you have personnel working near the energized equipment. This can help prevent dangerous shock hazards.12.

Safety



Training

All personnel working on or near the electrical system must be properly trained in electrical safety.

Personal Protective Equipment (PPE)

Use appropriate PPE, such as insulated gloves, safety glasses, and hard hats.


Lockout/Tagout

Follow proper lockout/tagout procedures when working on de-energized equipment.

Warning Signs

Post warning signs to alert people to the presence of high-voltage equipment.


Clearances

Maintain safe clearances around energized equipment.

Inspections

Conduct regular inspections of the electrical system to identify and correct any potential hazards.13.

Documentation



Drawings

Create detailed drawings of the electrical system, including the location of all poles, conductors, transformers, and overcurrent protection devices.

Calculations

Document all load calculations, voltage drop calculations, and conductor sizing calculations.


Inspection Reports

Keep records of all inspections and any corrective actions taken.14.

Removal

When the temporary installation is no longer needed, develop a plan for removing all equipment and restoring the site to its original condition.

Example Scenario Breakdown

Let's say you need to supply (4) portable offices each with the following: Lighting: 1000 Watts HVAC: 3000 Watts Receptacles: 2000 Watts (general use)Total Load per office: 6000 Watts (6kW). Let's assume a diversity factor of 0.8, so the estimated demand per office is 4.8kW.Total Demand for all 4 offices: 4.8kW 4 = 19.2kW

Calculate Current

Using single phase 480V (you will need to step down to 120/240V at each trailer. The NEC prefers calculated loads to use 125% of the continuous load (lighting and HVAC). Receptacles are not considered continuous loads. 1000W (lights) + 3000W (HVAC) = 4000W 1.25 = 5000W Continuous 2000W (Receptacles) = 2000W Non-Continuous Total Load per office = 7000W 7000W per office / 480V / .8 PF (assuming a .8 power factor for the HVAC) = 18.2 Amps 18.2 Amps/ office 4 offices = 72.8 Amps.

Conductor Sizing

Consult NEC Table 310.16 to find a conductor that is rated for at least 72.8 amps and is suitable for wet locations. Also consider voltage drop. An electrical engineer would determine the appropriate conductor size considering voltage drop over 1000 ft.

Grounding

A ground wire (EGC) must be run with the conductors. Size according to NEC Table 250.122 based on the overcurrent protection device.


Poles

Select poles that are tall enough to meet the minimum clearance requirements of the NEC. Space the poles appropriately based on the conductor sag and wind load.

In Summary:


This project is complex and potentially dangerous. You must involve qualified professionals (licensed electrical engineer and licensed electrician) to ensure a safe and code-compliant installation. Get all necessary permits and inspections. Do not cut corners. The risks associated with high-voltage electricity are too great. Flag for review