Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Disconnect required?

User: nizak, Location: Florence,Oregon,Lane

Asked on: Friday, June 13, 2025 at 3:36 pm EDT
Answered on: Friday, June 13, 2025 at 3:46 pm EDT

Question: Is a Main disconnect needed for a 6 space MLO panel in a detached residential garage fed from the house?Brain fart…..

Yes, a main disconnect is needed in the detached garage.NEC 225.31 requires a disconnecting means to be installed at the detached building. This is so you can de-energize the entire building in an emergency or for service.Since you are using a MLO (main lug only) panel, you will need to install a separate disconnect switch (breaker or fused) ahead of the panel. This disconnect must be readily accessible to occupants of the detached structure.Think of it this way: the MLO panel is just a junction box with breakers. It has no way to shut off power to the entire garage. Flag for review

Previous Question Next Question