User: emiller233, Location: pittsburgh, pa
Asked on: Monday, June 16, 2025 at 7:17 pm EDT
Answered on: Monday, June 16, 2025 at 7:20 pm EDT
Question: What is the proper way to ground an immersion tank heater when using EMT & LFMC for the conduit? EMT until we get near the heater, EMT to LFMC fitting, and then a short piece of LFMCAll fittings are cUL Listed for both conduit types.The immersion heater MFGR says we must use high-temperature wire for it. So, looking to use something like the wire below and the conduit as the ground.High-Temperature Stranded Wire, Silicone-Coated Fiberglass Outer Insulation, 14 Gauge
Okay, let's break down the proper grounding procedure for your immersion tank heater setup using EMT and LFMC, keeping in mind the high-temperature wire requirement and code compliance.
Understanding the Requirements NEC 250.4(A)(5)
Requires equipment grounding, ensuring a low-impedance path for fault current to return to the source. This is crucial for safety and proper operation of overcurrent devices (circuit breakers or fuses).
NEC 250.118
Lists acceptable equipment grounding conductors. EMT is specifically mentioned.
NEC 250.102(E)
Addresses sizing equipment grounding conductors.
NEC 250.130(C)
Allows the use of the equipment grounding conductor for grounding equipment near the load side of the circuit.
NEC 348.60
Addresses grounding of Flexible Metal Conduit (FMC) and Liquidtight Flexible Metal Conduit (LFMC). Specifically, it states that an equipment grounding conductor (EGC) shall be installed where flexibility is required after installation. Note: There is an exception if the LFMC is used as an EGC but the requirement to have a listed EGC fitting, LFMC no longer than 6', and is not connected to over 20A. The exception is not recommended as the LFMC may not always perform as expected.
Step-by-Step Grounding Procedure1. EMT as the Primary Grounding Path
The EMT conduit serves as your primary equipment grounding conductor from the panelboard to the point where you transition to LFMC. Ensure all EMT connections are tight and use appropriate fittings (cUL Listed for grounding). Use grounding locknuts or bushings as needed, especially at enclosures or boxes. Penetrating-type locknuts are preferred because they bite into the metal of the box.2.
Transition to LFMC
Crucially Important: Install an Equipment Grounding Conductor (EGC) Inside the LFMC. This is the most important step. Run a correctly sized insulated grounding conductor (green or green with yellow stripe) inside the LFMC along with your high-temperature power conductors. The size of this EGC must be determined based on the overcurrent protection device protecting the circuit (see NEC 250.122). A table is provided in the NEC. Use cUL Listed fittings at both ends of the LFMC that are suitable for both EMT and LFMC. Make sure they are rated for grounding as well.3. Connecting the EGC
At the EMT/LFMC Junction Box
Connect the EGC to the metal box in the junction box using a grounding screw or grounding clip. Ensure the box is properly grounded by the EMT system.
At the Immersion Heater
Connect the EGC to the grounding terminal provided on the immersion heater.4.
High-Temperature Wire
Your choice of high-temperature, silicone-coated fiberglass wire is appropriate for the immersion heater environment. Make sure the wire is rated for the voltage and amperage of the circuit. Connect the high-temperature wire to the power conductors inside the junction box using appropriate splices (e.g., crimp connectors, wire nuts rated for the temperature).
Important Considerations and Best Practices Local Codes and AHJ (Authority Having Jurisdiction)
Always consult your local electrical codes and the AHJ for specific requirements in your area. They may have additional rules or interpretations.
Tight Connections
Ensure all connections are clean and tight. Loose connections are a major cause of grounding problems and can create a fire hazard.
Strain Relief
Ensure the LFMC is properly supported and strain-relieved to prevent stress on the connections.
Documentation
Keep records of all wiring, grounding, and testing for future reference.
Testing
After installation, use a multimeter or a ground impedance tester to verify the integrity of the grounding system.
Professional Installation
If you are not fully confident in your ability to perform this work safely and correctly, hire a qualified electrician. Electrical work can be dangerous.
Example
Let's say your immersion heater is on a 20-amp circuit. Based on NEC 250.122, you would need at least a 12 AWG copper equipment grounding conductor (the green wire) inside the LFMC.
Why This Method is Important Safety
Provides a reliable low-impedance path for fault current, minimizing the risk of electric shock.
Code Compliance
Meets the requirements of the NEC (National Electrical Code).
Performance
Ensures proper operation of overcurrent devices.*
Longevity: A well-grounded system is less susceptible to corrosion and other issues that can lead to equipment failure.By following these steps, you can create a safe and code-compliant grounding system for your immersion tank heater. Remember to prioritize safety and consult with a qualified electrician if you have any doubts. Flag for review