Topic: Low resistance path to eart

User: kjroller, Location: Dawson Mn

Asked on: Tuesday, June 17, 2025 at 11:15 am EDT
Answered on: Tuesday, June 17, 2025 at 11:16 am EDT

Question: Is the reason your grounding grid generally needs to be under 25ohms because if you have a ground fault the breaker will not trip because it picks up a very low fault current when resistance is higher?

Yes, your understanding is on the right track. The goal of a low-resistance grounding grid (typically specified at 25 ohms or less, though specifics can vary by code and application) is directly related to ensuring that overcurrent protection devices (like circuit breakers or fuses) operate quickly and reliably during a ground fault.Here's a more detailed explanation: Ground Fault

A ground fault occurs when an energized conductor accidentally comes into contact with a grounded metallic surface (like a metal enclosure, equipment frame, or conduit).


Purpose of Grounding

The grounding system (including the grounding electrode system, grounding conductors, and equipment grounding conductors) provides a low-impedance path for fault current to flow back to the source (transformer or service).

Ohm's Law and Fault Current

Ohm's Law (Voltage = Current x Resistance) is crucial here. The amount of fault current that flows is directly related to the voltage and inversely related to the resistance of the fault path. If the grounding system has a
high resistance, the fault current will be low.

Breaker Operation

Circuit breakers are designed to trip when they detect a certain level of current flowing through them for a specific amount of time. Breakers have an instantaneous trip function, and a time-delay trip function. Ground fault protection breakers usually have a very low current threshold that they will trip at.

The Problem with High Ground Resistance

If the grounding grid resistance is too high, the resulting fault current might be
insufficient to:

Actuate the overcurrent protection device quickly.
The breaker might not trip immediately, or might not trip at all, allowing the fault to persist. Clear the fault before dangerous voltages develop on exposed metallic parts. If the fault current is limited by high resistance, the voltage on the faulted equipment can rise to a dangerous level relative to ground, creating a shock hazard for anyone who comes into contact with it. Why 25 Ohms (or Lower)? The 25-ohm threshold (or other specified value in codes) is generally considered a maximum acceptable resistance to ensure that enough fault current will flow to trip the overcurrent protection device quickly and safely. Lower resistance is generally better, as it provides a more robust fault current path. Keep in mind that specific requirements and acceptable resistance values can vary based on local electrical codes (like the NEC in the US), the type of equipment being protected, and the specific application.

In Summary

A low-resistance grounding grid is essential to:1.

Provide a low-impedance path for fault current.
2. Ensure sufficient fault current flows during a ground fault.3. Enable overcurrent protection devices (breakers or fuses) to trip quickly and reliably, interrupting the fault.4. Minimize the risk of electrical shock hazards by preventing dangerous voltage rises on equipment.

Therefore, the 25-ohm (or lower) requirement is directly linked to safety and the proper operation of overcurrent protection. Flag for review