Topic: Ground wire too thick

User: erikkwilder, Location: Atlanta, GA

Asked on: Wednesday, June 25, 2025 at 10:00 am EDT
Answered on: Wednesday, June 25, 2025 at 10:21 am EDT

Question: I am wiring a hot tub with a Balboa RS101 control box for 240v. I have 3 6AWG wires (2 hot and 1 neutral) and 1 8AWG ground wire. They are currently run into the hot tub's box. But the stranded ground wire seems to be too thick to fit through the box's pre-drilled hole for the ground wire. What should I do? Should I remove some strands from the ground wire to make it fit? Should I splice a thinner ground wire on to the end of the 8 awg wire?

Absolutely DO NOT remove strands from the ground wire or splice a thinner wire onto it. This compromises the safety and effectiveness of the grounding system, which is crucial for preventing electrical shock.Here's a breakdown of the correct way to address this issue

1. The Right Way: Enlarge the Hole
The Safest and Most Recommended Option

Carefully enlarge the pre-drilled hole in the hot tub's control box to accommodate the 8 AWG ground wire.


Important

Before you do anything, disconnect the power to the circuit.

Use the Right Tool

Use a drill bit or a step drill bit designed for metal. Select a drill bit size slightly larger than the diameter of your 8 AWG ground wire (including the insulation).


Deburr the Hole

After drilling, use a deburring tool or a file to smooth the edges of the hole. Sharp edges can damage the wire insulation over time.

2. Acceptable Alternative (If Enlarger isn't Possible)



Use a Correctly Sized Strain Relief Connector

If the hole is sized for a particular connector, but the 8 AWG wire is too thick to fit
through the connector, replace the connector with one that accommodates the 8 AWG wire. This is more likely an issue with the strain relief fitting, rather than the actual hole.

Important Considerations



Grounding is Critical

The ground wire's purpose is to provide a low-resistance path for fault current to return to the source, tripping the breaker quickly and preventing electrocution.

NEC (National Electrical Code)

Electrical codes require that the grounding conductor be sized appropriately for the circuit. Using a smaller conductor than required is a code violation and a safety hazard.

Why Your Suggestions Are Dangerous



Removing Strands

Reducing the number of strands in the ground wire reduces its current-carrying capacity. In a fault situation, the wire might not be able to handle the current, potentially melting or causing a fire.

Splicing a Thinner Wire

This creates a weak point in the grounding system. The connection between the 8 AWG and the smaller wire could corrode or loosen over time, increasing resistance and reducing the effectiveness of the ground.

Summary:


The
only* safe and proper way to deal with this issue is to make the hole large enough to accommodate the correctly sized ground wire, or replace the strain relief fitting with one that is sized correctly. If you're not comfortable with electrical work, consult a qualified electrician. It's much better to spend the money on a professional than to risk your safety or damage to your equipment. Flag for review