Question: HI, I need code references for reasons not to use spider boxes as permanent power (currently wanted for outside). Can anyone direct me to this?
You're not likely to find a specific code explicitly banning spider boxes for permanent outdoor power. Electrical codes tend to define acceptable installation methods and materials, and if something isn't listed as acceptable, it's implicitly not approved for permanent use. Here's a breakdown of why they are generally a bad idea and the code sections that imply this
Reasons NOT to Use Spider Boxes (aka Temporary Power Distribution Boxes) for Permanent Outdoor Power and Relevant Code Areas:
1. Designed for Temporary Use
Nature of the Product
Spider boxes are explicitly designed and marketed for temporary power distribution on construction sites or other short-term needs. Their construction reflects this.
NEC Article 590 (Temporary Installations)
This is the KEY area. Article 590 provides rules for temporary power. The very existence of this article implies that permanent wiring should follow much stricter rules. If you're installing something permanently, Article 590 doesn't apply.2.
Environmental Considerations (Especially Outdoors)
Lack of Weather Resistance/Water Tightness
Spider boxes are typically not rated for permanent outdoor exposure. While some may claim to be "weather resistant," this is often insufficient for long-term exposure to rain, snow, sun, and temperature extremes.
NEC 314.15 Damp or Wet Locations
This section mandates enclosures suitable for the environment. A typical spider box doesn't have the proper NEMA rating (e.g., NEMA 3R, 4, 4X) for permanent outdoor use.
NEC 406.9 Receptacles in Damp or Wet Locations
This section requires weatherproof covers for receptacles installed in damp or wet locations. While you might add a weatherproof cover to a spider box receptacle, the entire box itself is still likely not weather-rated.
Corrosion
The metal enclosures of many spider boxes are susceptible to corrosion over time in outdoor environments, especially in coastal areas or where salt spray is present.
NEC 110.11 Deteriorating Agents
Electrical equipment must be resistant to deterioration caused by environmental factors.3.
Mechanical Protection
Fragility
Spider boxes are often made of relatively thin metal or plastic, making them vulnerable to physical damage from impacts, weather, or vandalism.
NEC 300.4 Protection Against Physical Damage
Wiring and equipment must be protected from physical damage. A spider box exposed in a yard is far more likely to be damaged than properly installed, permanent wiring.4.
Improper Wiring Methods
Flexible Cords/Cables
Spider boxes often rely on flexible cords and cables for connection. While permissible for temporary use, these are not generally allowed for permanent wiring unless specifically listed and installed in accordance with their listing.
NEC 400.8 Uses Not Permitted
This section details where flexible cords and cables cannot be used. Specifically, it prohibits their use: As a substitute for the fixed wiring of a structure. Where run through holes in walls, ceilings, or floors. Where covered by building materials.
Strain Relief
The strain relief on spider box cords is often inadequate for permanent installation.
NEC 400.10 Pull at Terminals
Flexible cords must be connected to prevent strain at terminals.5.
Overcurrent Protection Concerns
Mismatch of Overcurrent Protection
The overcurrent protection (circuit breakers or fuses) in the spider box might not be properly coordinated with the upstream circuit. This can lead to nuisance tripping or, worse, inadequate protection against overloads and short circuits. Permanent wiring requires careful circuit design and overcurrent protection sizing.6.
Safety Hazards
Shock Hazard
The combination of weather exposure, potential for damage, and improper wiring practices increases the risk of electrical shock.
Fire Hazard
Overloaded circuits, damaged wiring, and corrosion can all create fire hazards.
How to Argue Against Using Them
Focus on the "Temporary" nature
Emphasize that these devices are designed and intended for temporary use as defined in Article 590.2.
Highlight the environmental issues
Ask if the spider box is specifically listed and rated for permanent outdoor exposure. If not, point to NEC 314.15 and 406.
9.3.
Emphasize safety
Explain the increased risk of shock and fire due to the factors above.4.
Suggest alternatives
Offer solutions that are code-compliant and designed for permanent outdoor use, such as: Installing a proper outdoor-rated junction box with GFCI-protected receptacles. Running underground wiring (in conduit if required) to a weatherproof outlet.
Example Scenario and Code Justification
Let's say someone wants to power a string of lights and a small fountain in their backyard using a spider box.
Problem
The spider box is sitting on the ground, exposed to rain, and has multiple extension cords plugged into it.
Arguments Against
"This spider box is designed for temporary construction sites, not for permanent outdoor use." (Refer to Article 590). "The box isn't weatherproofed, and the receptacles need weatherproof covers when in use." (NEC 314.15, 406.9). "The extension cords are not rated for permanent outdoor burial or exposure and could become damaged, creating a shock hazard." (NEC 400.8) "The constant exposure to moisture can cause corrosion and lead to electrical problems." (NEC 110.11).
Solution
"Let's install an outdoor-rated, GFCI-protected receptacle, properly wired and installed according to code. We can run underground wiring in conduit to ensure it's protected from damage."
Key Takeaway: While you won't find a rule that says "Thou shalt not use spider boxes for permanent power," the cumulative effect of the code requirements related to temporary vs. permanent wiring, environmental protection, physical protection, and proper wiring methods effectively prohibits their use as a permanent power solution, especially outdoors. The focus should always be on safe, code-compliant installations using equipment designed for the intended environment and application. Always consult with a qualified electrician for any electrical work. Flag for review