Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: cord grips for use in class 2 div1 group E

User: JoeWay314, Location: Decatur IL

Asked on: Wednesday, June 25, 2025 at 8:48 pm EDT
Answered on: Wednesday, June 25, 2025 at 8:53 pm EDT

Question: I am working on designing a piece of equipment required to operate in a Class 2, Div. 1 Group "E" area. this piece of equipment is a fixture that will be moved into the area and operated when hazardous dust is present. then when the area is "safe" again it will be moved elsewhere. We have lots of sensors and hydraulic valves that need to be wired into the enclosure. enclosure is cast aluminum, rated specifically for the environment, valves. we will be using a mix of rigid conduit, sealtight conduit and possibly some cord grips. all depending on location of devices in question and ease or ability to route wiring. looking at using killark type cordgrips CG5050s (as an example). any concerns? or things I should watch out for specifically with this wiring setup.

Okay, let's break down the challenges and considerations for wiring your equipment in a Class II, Division 1, Group E environment. You're on the right track with the cast aluminum enclosure and rigid/sealtight conduit approach. Here's a detailed look at potential issues and key things to watch out for

General Considerations for Class II, Div. 1, Group E (Metal Dust)
Explosion Protection

Remember that in Class II, Div. 1, your primary concern is
preventing dust ignition. Dust explosions are nasty, and Group E (metal dusts like aluminum, magnesium, and their alloys) are highly hazardous. Even a small spark or hot surface can trigger an explosion.

Temperature Rating

Everything used must have a temperature rating appropriate for the specific dust you're dealing with. The temperature code (e.g., T3C, T4A) indicates the maximum surface temperature the equipment can reach without posing an ignition risk. Crucially, the temperature rating must be lower than the ignition temperature of the dust. Check the SDS of the metal dust for it's Minimum Ignition Temperature (MIT)

Dust-Tight Enclosure

"Dust-tight" means
absolutely no dust can enter the enclosure under normal operating conditions. This is critical to prevent dust from accumulating inside, where it could be ignited by internal components.

Grounding

Proper grounding is essential to prevent static discharge, which can be a source of ignition.

Listing/Certification

Everything you use (enclosures, conduit bodies, fittings, cord grips, sensors, valves, etc.) must be listed and labeled for Class II, Division 1, Group E. Look for the markings from a Nationally Recognized Testing Laboratory (NRTL) like UL, CSA, ETL, etc. Do not assume something is suitable just because it looks similar to a listed device.

Specific Concerns with Your Wiring Setup
1. Killark CG5050 Cord Grips (and any Cord Grips) Suitability for Group E

Carefully verify that the Killark CG5050 (or any cord grip you choose) is specifically listed and marked for Class II, Division 1, Group E. Many cord grips are suitable for Class II, Division 1, but not necessarily Group E. Group E is often an exception.

Dust-Tight Seal

Ensure the cord grip provides a
positive, dust-tight seal around the cable. The cable diameter must be within the grip's specified range. Install per the manufacturer's instructions, including proper tightening torque.

Cable Type

The cable used with the cord grip must also be suitable for the environment. Look for cable rated for industrial use, resistance to chemicals, abrasion, and temperature extremes. Avoid cable jackets that are prone to cracking or deterioration. It also needs to be rated for Group E environments.2.

Sealtight Conduit
Fittings

Sealtight conduit
must be used with fittings that are listed and marked for Class II, Division 1. These fittings will provide a dust-tight seal between the conduit and the enclosure or other equipment.

Flexibility

Sealtight is often necessary for connecting to moving or vibrating components. However, it's generally less robust than rigid conduit. Ensure it's adequately protected from physical damage.

Grounding

Sealtight conduit
does not provide an adequate ground path. You must install a separate grounding conductor inside the sealtight conduit and bond it to the enclosure and any equipment it connects to.

Material Compatibility

Ensure the sealtight conduit material is compatible with the dust in question. Some materials can degrade in the presence of certain metal dusts.3.

Rigid Conduit
Threaded Joints

All threaded joints in rigid conduit runs must be properly tightened and sealed with a suitable thread sealant (pipe dope) listed for hazardous locations. This ensures a dust-tight seal.


Grounding

Rigid conduit can provide a ground path if properly installed, but it's always best practice to include a separate grounding conductor inside the conduit, especially in hazardous locations.

Conduit Bodies

Use conduit bodies (e.g., LB, LL, LR) that are listed and marked for Class II, Division 1.4.

Enclosure
NEMA Rating vs. Hazardous Location Rating

A NEMA rating (e.g., NEMA 4, NEMA 12) is not the same as a hazardous location rating. The enclosure must be specifically listed and marked for Class II, Division 1, Group E.

Entry Points

Ensure all entry points into the enclosure (conduit entries, cord grip entries, etc.) are properly sealed and dust-tight.


Gasket Integrity

Inspect the enclosure gasket regularly to ensure it's in good condition and provides a proper seal. Replace it if it's damaged or deteriorated.

Breather/Drain Fittings

If the enclosure requires breather/drain fittings, they
must be listed for Class II, Division 1.5.

Sensors and Valves
Listing/Marking

As stated before, the valves and sensors must be listed and marked for Class II, Division 1, Group E, and have an appropriate temperature code.

Wiring Methods

Follow the manufacturer's instructions for wiring the sensors and valves. Use appropriate wiring methods (e.g., explosion-proof connectors, sealed fittings) to maintain the integrity of the hazardous location rating.


Intrinsic Safety (IS)

Consider using intrinsically safe (IS) sensors and valves, especially if the devices have complex internal circuitry. IS devices limit the energy available in the hazardous area, reducing the risk of ignition. If you use IS devices, you'll need to use IS barriers and follow the IS wiring guidelines carefully. This can simplify the wiring requirements within the enclosure.6.

Grounding and Bonding
Equipment Grounding Conductor (EGC)

Run an EGC (ground wire) inside all conduit (rigid and sealtight) and connect it to all metal parts of the equipment (enclosure, sensors, valves, etc.).


Bonding Jumpers

Use bonding jumpers to ensure electrical continuity between all metal parts of the equipment, especially across any joints that might loosen over time.

Grounding Electrode System

Connect the equipment grounding system to a suitable grounding electrode system (e.g., ground rod, building steel).7.

Documentation and Maintenance
Hazardous Location Drawings

Create detailed drawings showing all wiring, conduit runs, and equipment locations. These drawings should be kept up-to-date and readily available.

Inspection and Maintenance

Implement a regular inspection and maintenance program. Inspect all wiring, conduit, fittings, enclosures, and equipment for damage, corrosion, loose connections, and dust accumulation. Repair or replace any defective components immediately. Keep a log of inspections and maintenance activities.


Training

Ensure all personnel who operate or maintain the equipment are properly trained on hazardous location safety procedures.

Specific Recommendations
Consult with an Expert

I
strongly recommend consulting with a qualified electrical engineer who is experienced in hazardous location design and installation. They can review your design, ensure compliance with all applicable codes and standards (NEC Article 502), and provide valuable guidance.

Detailed SDS Review

Obtain and thoroughly review the Safety Data Sheet (SDS) for the specific metal dust you're dealing with. Pay close attention to the ignition temperature, minimum ignition energy, and other relevant safety information.

Consider Intrinsically Safe (IS) Solutions

As mentioned above, using IS sensors and valves can significantly simplify the wiring requirements and reduce the risk of ignition.


Minimize Cord Grips

Use cord grips only where necessary. Rigid conduit provides the most robust and reliable protection.

Example Scenario & Questions


Let's say you have a hydraulic valve that needs to be connected to the enclosure.1. Valve Listing

Is the valve itself listed and marked for Class II, Div. 1, Group E with an appropriate temperature code?2.

Connection Method

How will you connect the wiring to the valve? If it has a threaded entry, you can use an explosion-proof conduit fitting. If it requires a cable, you'll need a Group E-rated cord grip.3.

Cable Choice

What type of cable are you using? Is it rated for the environment, including resistance to the metal dust and any chemicals present?4.

Grounding

How are you ensuring proper grounding of the valve?

In summary, operating electrical equipment in a Class II, Div. 1, Group E environment requires meticulous attention to detail and strict adherence to all applicable codes and standards. Thorough planning, proper selection of components, and regular inspection and maintenance are essential to ensure a safe and reliable operation.
Flag for review

Previous Question Next Question