Question: What the title says.I am replacing inverters on a legacy system.New inverters are Sunny Tripower X-30-US with 3 MPPTs each.The negatives for 3 strings are combined at the array into a single #8 AWG PV wire comig to the INV...........while (most of) the positives are individual (#10 AWG) for each string.Can I wire 2 positives to one MPPT and the third to another MPPT, while "splitting" the common negative across both MPPTs?(wire single common negative to both MPPTs with MC branch circuit "Y" connector AKA splitter or jumper)I know this can be done with paralleled source circuits, but not sure about MPPTs.OPTION 2:More details:Panel Imp is 8.68A (3 strings at 8.68 A = 26 A combined)INV MPPT max DC input of 24 A operating.So I guess I could wire it to a single MPPT but because there is ony on other neagtive lead.......I would only use 2 of 3 MPPTs on the INV. Not sure if that is a huge waste or none at all?
Let's break down your situation and the options
Understanding the Issues
MPPT Mismatch
MPPTs (Maximum Power Point Trackers) are designed to independently optimize the power extraction from each string. Connecting multiple strings with different characteristics (due to shading, panel degradation, or slight variations in manufacturing) to the same MPPT can result in suboptimal performance. The MPPT will track the average power point, which might not be ideal for any individual string.
Current Capacity
Your biggest constraint is the inverter's MPPT current limit of 24A. You have three strings at 8.68A each, totaling 26.04A. This exceeds the MPPT limit if combined into a single MPPT.
Negative Wire Size
The shared #8 AWG negative wire is a concern. It needs to be appropriately sized for the combined current of all three strings.
NEC Compliance
All wiring practices must adhere to the National Electrical Code (NEC) and any local amendments. Specifically, pay close attention to wire ampacity, overcurrent protection, and grounding requirements.
Analyzing Your OptionsOPTION 1: Splitting Positives and Negative Across MPPTs (Your Original Idea)
This is NOT recommended and likely violates safety and electrical code. Why it's problematic
MPPT Dependence
MPPTs operate as independent DC-DC converters. "Splitting" the common negative across multiple MPPTs can create unpredictable current flow and potentially damage the inverter. The inverter's internal circuits are not designed for this type of configuration.
Unbalanced Currents
Even if the strings were perfectly identical (highly unlikely), there would be no guarantee that the current would be distributed equally between the MPPTs. This could overload one MPPT while underutilizing the other.
Safety Concerns
It is impossible to ensure correct current flow and safe operation, and any such configurations would void the inverter's warranty and UL listing.
NEC Violation
It would likely violate NEC article 690, "Solar Photovoltaic (PV) Systems" specifically regarding wiring methods and equipment usage.
DC Ground Fault Detection
Your inverter relies on measuring the differential current of DC+ and DC- in order to detect a ground fault. When you "split" the common negative, this is no longer possible.
OPTION 2: Combining All Strings into a Single MPPTNOT RECOMMENDED due to exceeding current limitations. Why it's problematic
Current Overload
3 strings at 8.68A each, which is a total of 26.04 A. Since this is more than the max DC input, wiring these to a single MPPT could damage the inverter or cause it to operate inefficiently.
MPPT Underutilization
You're correct that you'd only be using 2 of the 3 MPPTs. While not inherently a problem (the inverter should be able to operate with unused MPPTs), it does mean you're not taking full advantage of the inverter's capabilities.
A BETTER SOLUTION
To make the most use of the existing wires you can do the following: Combine 2 strings in parallel This gives you an Imp of 17.36A (2 x 8.68 A) and a voltage equal to that of one string. Connect them to a single MPPT. As the amperage is lower than 24A you should be able to connect them to a single MPPT on the inverter. Connect the remaining string to a second MPPT. As the amperage is lower than 24A you should be able to connect them to a single MPPT on the inverter. Leave one MPPT unused This should be fine.
Important Considerations
Professional Installation
Solar PV installations are complex and potentially dangerous. I strongly recommend that you hire a qualified and licensed solar installer to perform the work. They will have the knowledge and experience to ensure that the system is installed safely and correctly, and that it meets all applicable codes and regulations.
Warranty
Incorrect wiring can void the inverter's warranty.
AHJ Approval
The final installation will need to be inspected and approved by your local Authority Having Jurisdiction (AHJ).