Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Detached building

User: nizak

Asked on: Sunday, July 6, 2025 at 1:49 pm EDT
Answered on: Sunday, July 6, 2025 at 1:49 pm EDT

Question: Would a 6 space MLO panel in a detached garage fed from a house require a main disconnect?Thank you.

Yes, a 6-space MLO (Main Lug Only) panel in a detached garage fed from a house would require a main disconnect at the garage. This is due to the requirements of the National Electrical Code (NEC).Here's a breakdown of why: NEC 225.31 Disconnecting Means. A disconnecting means shall be installed where a feeder supplies a building or structure. NEC 225.32 Location. The disconnecting means shall be installed at a readily accessible location either inside or outside of the building or structure served.* Why a MLO panel needs a disconnect: A main lug only panel does not have a main breaker to serve as a disconnecting means.In short, the NEC requires a readily accessible disconnecting means at the detached garage to cut off power to the entire garage. This is for safety reasons, allowing someone to easily de-energize the garage's electrical system in an emergency or during maintenance.Therefore, you need to install a disconnect switch or breaker (in an enclosure) ahead of the MLO panel in the garage. This disconnect must be rated to interrupt the available fault current. Flag for review

Previous Question Next Question