Question: Hi everyone,I'm looking for the requirement for fittings that can be used in Class 2 Division 2.What I found so far isCable conduit with UL 1660 can be used in C2D2e.g ABB PMA CUSWhat I cannot find or identify is the requirment for the fittingsWould UL 1696 or UL 514B fitting sufficient for C2D2?Thanks!Best regards,Bng
Okay, let's break down the requirements for fittings in Class II, Division 2 hazardous locations. You're on the right track, but there are some important nuances.
Understanding Class II, Division 2 (C2D2) Class II
Refers to locations where combustible dust is present.
Division 2
Hazardous concentrations of combustible dust are not normally present in explosive concentrations. However, they might become hazardous: Through infrequent malfunctions. Through accidental rupture or breakdown of equipment. Through abnormal operation. Sufficient dust may be present for flammable or explosive mixtures to be produced.
Key Requirements and Considerations1. National Electrical Code (NEC) - Article 502
This is the primary resource for Class II hazardous locations. You must consult the specific sections within Article 502 for your particular installation.2.
General Requirement for Suitability (NEC 500.8(A))
All equipment in hazardous locations, including fittings, must be approved for the specific Class and Division. "Approved" means acceptable to the Authority Having Jurisdiction (AHJ), and usually requires listing by a recognized testing laboratory (e.g., UL, CSA, FM).3.
Dust-Ignitionproof vs. Dusttight
In Class II, Division 2, equipment must be designed to minimize dust accumulation and prevent surface temperatures that could ignite dust. Here's where it gets tricky:
Dust-Ignitionproof
Typically required for Class II, Division 1. This is a very robust construction to prevent dust from entering the enclosure and to contain any internal ignition. Generally not required for C2D2.
Dusttight
Equipment in C2D2 must be constructed to minimize the entrance of dust.4.
Enclosure Types (NEMA or IEC)
Enclosures provide protection against environmental factors, including dust. For C2D2, you'll typically be looking for enclosures rated NEMA 4 or 12, or IEC 60529 IP5X or IP6X, depending on the specific application.5.
Temperature Considerations (NEC 500.8(D))
This is critical. The surface temperature of any equipment must not exceed the ignition temperature of the specific dust present. The NEC requires marking the maximum surface temperature on equipment in hazardous locations. This is often expressed as a T-code (e.g., T3, T4, etc.). You must know the ignition temperature of the dust you are dealing with.
Specifics Regarding Fittings, Conduit, and UL Standards
UL 1660 (Liquidtight Flexible Metal Conduit)
This standard does not inherently make a conduit system suitable for C2D2. While it's a good starting point for physical protection and liquid tightness, you must ensure the entire system, including fittings, is appropriately rated for the hazardous location.
UL 1696 (Nonmetallic Liquid-Tight Flexible Conduit)
Similar to UL 1660, this covers the conduit itself. You still need to consider the fittings.
UL 514B (Conduit, Tubing, and Cable Fittings)
This standard covers the construction and testing of fittings. A fitting that complies with UL 514B is a good starting point, but it does not automatically make it suitable for C2D2. The listing will indicate its suitability for hazardous locations. You need to look for specific markings or listings indicating suitability for Class II, Division 2 or a specific dust group (E, F, or G).
So, Are UL 1696 or UL 514B Fittings Sufficient?
Potentially, yes, IF... The fittings are specifically listed or marked for Class II, Division 2 use and appropriate for the dust group and temperature rating required for the application. Read the product labeling and specifications carefully!What to Look For on Fittings
Listing Mark
Look for the mark of a recognized testing laboratory (e.g., UL, CSA, FM).
Hazardous Location Marking
Specifically, it should say "Class II, Division 2," and ideally specify the dust group (E, F, or G).
Temperature Code (T-code)
This is crucial! Make sure it's appropriate for the dust ignition temperature.
IP or NEMA Rating
This indicates the enclosure's degree of protection against dust ingress.
Recommendations1.
Consult the NEC (Article 502)
This is the definitive guide.2.
Determine the Dust Group and Ignition Temperature
You must know what dust you're dealing with. Different dusts have different properties.3.
Select Listed Fittings and Conduit
Look for fittings and conduit systems specifically listed for Class II, Division 2, and appropriate for the dust group and temperature.4.
Check the Manufacturer's Specifications
Read the manufacturer's data sheets and installation instructions carefully.5.
Involve a Qualified Professional
Hazardous location installations are complex and potentially dangerous. Work with an experienced electrical engineer or contractor who is familiar with hazardous location requirements.6.
Consider using listed cable glands or cord grips. Cable glands and cord grips are available with specific hazardous location approvals.
Example
Let's say you have a location with Group G combustible dust (grain dust) that has a minimum ignition temperature of 200°C. You would need: Fittings listed for Class II, Division 2, Group G. A T-code that ensures the maximum surface temperature of the fitting is less than 200°C (e.g., T3C, which has a maximum surface temperature of 160°C). An enclosure that meets the dusttight requirements.
In SummaryUsing UL 1660 conduit or UL 514B fittings is a good starting point. However, you must verify that the entire system (conduit and fittings) is specifically listed and marked for Class II, Division 2, and that it meets the dust group and temperature requirements for your application.
Disclaimer: This information is for general guidance only. Always consult with a qualified electrical engineer or contractor for specific applications.* Flag for review