Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 12,470/7,200 3ph 4wire Service Switch gear Working space

User: zemingduan, Location: Philadelphia,PA

Asked on: Tuesday, July 29, 2025 at 5:18 pm EDT
Answered on: Tuesday, July 29, 2025 at 5:25 pm EDT

Question: The electrical service from the utility company (Atlantic City Electric) is 12,470/7,200 V 3ph 4wire. We have a 15KV switch gear and then substations transformer to power the building.I got the minimum 6' required working space from NEC NEC 2020 table 110.34 (A) for the switchgear. But the ACE engineer request at least 8 ft clearance in front of the switchgear. He states that to change the 12kv fuses by a qualified electrician, they would use an 8 ft hot stick so the 6 ft clearance is not enough. Is this true? I mean this is not listed in their handbook or NEC. I would like to here some thoughts from you. Thanks!

You're in a common situation: navigating the gray area between the NEC's minimum requirements and utility company's more stringent (and often undocumented) requirements. Here's a breakdown of why the ACE engineer is likely requesting 8 feet and what you should consider

Understanding the Issue
NEC Minimums

The NEC provides the
minimum acceptable clearances for safe working space. It's a baseline.

Utility Requirements

Utility companies, like ACE, often have their own internal standards and policies that exceed the NEC. This is driven by their specific equipment, operating procedures, and internal safety requirements. They are ultimately responsible for maintaining their equipment and ensuring the safety of their personnel.

Hot Sticks and Safety

The use of hot sticks is a critical safety practice for working on energized medium-voltage equipment. The required length of the hot stick dictates the minimum clearance needed to safely operate it.


Fuse Replacement

Replacing 12kV fuses is a common maintenance task that requires working on energized equipment. The ACE engineer's statement is very likely rooted in this specific maintenance activity.

Why 8 Feet is Plausible
Hot Stick Length

8-foot hot sticks are common for working on 12kV equipment. The length of the hot stick,
plus the electrician's arm reach and any necessary maneuvering space, translates directly into the required working clearance.

Comfort and Safety Margins

Even if a 6-foot hot stick could technically be used, an 8-foot clearance provides a greater margin of safety, reduces the risk of accidental contact, and allows for more comfortable and controlled movements.

Company Policy/Training

ACE may have a policy that
requires the use of 8-foot hot sticks for 12kV fuse replacement, regardless of the specific equipment configuration. This policy may be driven by their internal training and safety procedures.

Specific Switchgear Design

The specific design of your switchgear could also contribute to the need for additional clearance. For example, if the fuses are recessed or require awkward maneuvering, an 8 ft clearance may be needed.

What to Do
1. Direct Communication with ACE

This is the most important step. Specifically ask the ACE engineer to provide the specific reason for the 8-foot requirement. Ask if there is any specific policy or standard they are using. Be polite and respectful while asking. Don't just argue about the NEC. Acknowledge their experience and ask for clarification.2.

Document Request

Politely request a written document or reference (if one exists) outlining their 8-foot clearance requirement for this specific type of equipment and service. This is important for your own records and for future reference. If they don't have a specific document, try to get something in writing (email is fine) that explains the basis of their requirement (e.g., "For 12kV fuse replacement on this type of switchgear, we require an 8-foot clearance to accommodate the use of an 8-foot hot stick as per our internal safety procedures.").3.

Review ACE's Handbook (Again)

Even if you already checked, look at ACE's service requirements handbook again. Check online if needed. Sometimes these requirements are hidden in sections about maintenance or safety.4.

Negotiate (Carefully)

If the 8-foot clearance presents a significant design or cost challenge, explore if there are potential compromises. However, be very cautious about challenging a utility's safety requirements. Some possibilities to discuss (only after understanding their reasoning):

Alternative Equipment Configuration

Is there an alternative switchgear configuration or fuse design that might reduce the required clearance without compromising safety? (Unlikely, but worth asking.)


Remote Fuse Replacement

Could fuses be replaced remotely using specialized equipment (again, unlikely for this voltage level, but ask the question)?

Shorter Hot Sticks with Specific Justification

Only if you have extensive experience and can demonstrate that a shorter hot stick is safe and adequate for the task, could you propose using a shorter hot stick with a detailed safety plan. This is generally not advisable unless you have very strong expertise and the ACE engineer is willing to consider it.*5.

Prioritize Safety

Ultimately, safety is paramount. If ACE insists on the 8-foot clearance, it's generally best to comply. Challenging a utility company's safety requirements can be difficult and potentially risky.

In Summary


While the NEC provides minimums, the utility company's requirements often dictate the final design, especially when it comes to safety and maintenance procedures. Engage in direct communication with the ACE engineer to understand the reasoning behind their 8-foot clearance requirement, and document their explanation. Prioritize safety and be prepared to comply with their request, unless you can demonstrably prove that an alternative solution is equally safe. Flag for review

Previous Question Next Question