Question: NEC 2020 - Continuous loadsThere are exceptions to the 125% factor when using 100% rated overcurrent protection for feeders (215.3) and branch circuits (210.20 (A) ) allowing 100% continuous load on the device.I've always interpreted that to include the service disconnecting means but cannot find validation in the code. If my interpretation is correct, where is it in the code?Or do you disagree?(208Y/120V service, Bolt-lock fused switch, not that that matters.)Thanks
You're correct to be cautious. The NEC does not explicitly allow the same 100% continuous load application for service disconnecting means that it does for feeders (215.3) and branch circuits (210.20(A)) when using 100% rated overcurrent protection devices. This is a common misconception.Here's the breakdown: Branch Circuits (210.20(A))
Explicitly allows 100% loading with 100% rated OCPD.
Feeders (215.3)
Explicitly allows 100% loading with 100% rated OCPD.
Service Disconnecting Means (230.70)
No explicit 100% loading allowance, even with 100% rated OCPD.
Why the difference?
The rationale for this difference is rooted in safety and system resilience. Service equipment is the entry point for power and, therefore, the critical point of protection for the entire electrical system. Applying the 125% factor here provides an additional margin of safety to account for unforeseen circumstances, potential future load growth, and the overall importance of maintaining service continuity. While 100% rated breakers are tested and listed to carry 100% of their rated current continuously, service equipment is subject to additional environmental and installation variables.
Where the confusion might come from
General Load Calculations
Article 220 provides the general requirements for calculating branch-circuit, feeder, and service loads. The continuous load requirement is part of this calculation, but it doesn't override the specific requirements for service equipment. You still need to account for continuous loads at 125% when calculating the overall service load, regardless of the OCPD rating (with a few exceptions as noted below).2.
Applying Feeder Rules to Services (Incorrectly)
Because service conductors are often treated similarly to feeders in many respects, it's easy to assume the 100% rated breaker allowance also applies. However, it does not.
Key Code Sections & Considerations
230.42 (Service-Entrance Conductors)
Requires service conductors to have an ampacity not less than 125% of the continuous loads, plus the noncontinuous loads.
230.90 (Overcurrent Protection)
Generally requires service overcurrent protection to be sized not less than the calculated load per Article 220.
230.71 & 230.72 (Number of Service Disconnecting Means)
If you have multiple service disconnects, the sum of their ratings must not be less than the calculated load.
Exceptions and clarifications
230.42(B)
Ampacity of ungrounded conductors based on conductor size and table.
In summary
You
cannot apply the 100% continuous load allowance (available for feeders and branch circuits) to the service disconnecting means even if you're using 100% rated overcurrent protection. You must* apply the 125% factor for continuous loads when calculating the minimum size of the service conductors and the service overcurrent protection. This is a critical distinction often overlooked.Always consult with a qualified electrical engineer and your local AHJ (Authority Having Jurisdiction) for specific interpretations and compliance in your area. Flag for review