Question: Good morning, i'm a builder of industrial control panel in USA and Canada market. We works in many sectors of automation.Typical main control panel with motor in DOL or VFD.Typical we have terminals (field wiring terminals) on din guide and near a copper grounding bar.First question: the cable PE of the motor from field can be connected either din guide (terminal rail) and grounding bar (UL 467) ? or only in din guide?Second question: if the correct connection is the din guide, the other side of terminal must be grounded in grounding bar or is not necessary because the terminal is connect to the din guide that is connect in the plate of the cabinet that is grounded?Standard UL508A 54.10 is not clear for me, i don't know if NFPA79 or NEC is more clear.Example of grounding bar (earth busbar)https://www.gewiss.com/ww/en/products/product.1000001.1006939.GW45566Thanks in advance
Good morning! You're dealing with a crucial and often debated aspect of panel building. Let's break down the grounding requirements for PE (Protective Earth) conductors in your industrial control panels in accordance with UL 508A, NFPA 79, and the NEC.
Understanding the Codes UL 508A
Specifically designed for industrial control panels. It provides requirements for the safe design and construction of these panels. Section 54 addresses grounding.
NFPA 79
Electrical Standard for Industrial Machinery. More focused on the electrical safety of the machine as a whole, including the control panel.
NEC (National Electrical Code), NFPA 70
A broad electrical safety code covering all electrical installations. It's relevant because UL 508A and NFPA 79 often reference the NEC.
Answering Your QuestionsQuestion 1: Can the motor PE cable be connected to either the DIN rail (terminal rail) or the grounding bar (UL 467)?Answer
General Rule
The preferred and generally accepted method is to connect the motor PE conductor to the grounding bar (earth busbar) that meets UL 467 standards. Why the Grounding Bar is Preferred
UL 467 compliance
UL 467 specifically covers grounding and bonding equipment, including grounding bars. Using a UL 467-listed grounding bar provides assurance that it's designed for safe and effective grounding.
Low Impedance Path
The grounding bar provides a dedicated, low-impedance path to ground. This is crucial for quickly and safely clearing fault currents.
Direct Connection
Connecting directly to the grounding bar eliminates potential issues related to the conductivity and reliability of the DIN rail and its mounting.
Code Compliance
While UL 508A allows for grounding to the subpanel, it must be done with components suitable for grounding. Grounding bars offer a guaranteed, tested method.
DIN Rail Concerns
Not a Dedicated Grounding Path
DIN rails are primarily designed for mounting components. While they can be grounded, relying on them as the primary grounding path for a motor's PE conductor is generally not recommended, especially for larger motors. The conductivity of the DIN rail and the connections between sections might not be adequate for fault currents.
Reliance on Mounting
The effectiveness of the DIN rail as a grounding path relies on the electrical continuity between the rail, the mounting hardware, and the enclosure's grounding point. Corrosion, loose connections, or paint can compromise this continuity.
Terminal Block Considerations
If you're using terminal blocks mounted on the DIN rail for the PE connection, the terminal block itself must be rated for grounding and have sufficient current-carrying capacity.
Question 2: If the correct connection is the DIN rail, must the other side of the terminal be grounded to the grounding bar, or is it unnecessary because the terminal is connected to the DIN rail, which is connected to the plate of the cabinet that is grounded?Answer
Because I advocate for the Grounding Bar method This is a moot point, but let's look at it anyway If using DIN rail, the other side of the terminal block MUST be reliably connected to the grounding bar. If you choose to connect your field wiring at the din rail, you must ensure the following: Your DIN rail and terminal blocks are specifically rated for grounding (have the correct symbols) and have the capacity for fault current. The DIN rail itself is bonded to the enclosure with a listed grounding strap. The terminals on the DIN rail are similarly bonded to the DIN rail itself in an electrically sound way.
UL 508A, NFPA 79, and NEC Considerations UL 508A Section 54.10
As you noted, this section is critical. It outlines the general grounding requirements. However, it can be vague.
NFPA 79
Look at Chapter 4, "General Requirements," and Chapter 5, "Supply Circuit Conductors," in NFPA 79. These sections provide more specific guidance on grounding conductors and bonding.
NEC Articles 250 (Grounding and Bonding) and 430 (Motors, Motor Circuits, and Controllers)
These articles are foundational. They detail the general grounding principles and the specific requirements for motor grounding. NEC 250.130(C) is a good reference point for supplementary grounding requirements.
Specific Recommendations1. Use UL 467 Listed Grounding Bars
Always use grounding bars that are UL 467 listed.2.
Dedicated Grounding Conductors
Run a dedicated grounding conductor (PE) from the motor back to the grounding bar in the control panel.3.
Size Conductors Appropriately
Ensure that the grounding conductor is sized according to the NEC (Table 250.122).
4.
Bonding Jumpers
Use bonding jumpers to connect the DIN rail (if used for component mounting) to the grounding bar. This ensures that the rail is effectively grounded.5.
Grounding Terminal Blocks
If using terminal blocks for grounding, use those specifically designed and rated for grounding. They will typically have a grounding symbol on them.6.
Tight Connections
Ensure all grounding connections are clean, tight, and free of corrosion. Use anti-oxidant paste on connections if necessary.7.
Inspect and Test
Always inspect and test the grounding system during panel commissioning to verify its integrity. A ground impedance tester is a valuable tool.8.
Documentation
Document all grounding connections in your panel's wiring diagrams.
In Summary
While UL 508A and other codes might technically permit using the DIN rail as a grounding path under certain, very controlled circumstances, the best practice is to use a dedicated grounding bar that meets UL 467 standards. This provides a more reliable, safer, and code-compliant grounding system for your industrial control panels.