Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: simple service

User: dhsvcs, Location: miami

Asked on: Monday, August 4, 2025 at 3:18 pm EDT
Answered on: Monday, August 4, 2025 at 3:19 pm EDT

Question: I have a transformer feeding a service 80 ft of wire away. It feeds a 200 A meter ( 240/120 v 1 ph ) that feeds a 200 A 30 space 60 ckt home line load center/panel board. The 4/0 cu wire feeding feeding the meter calcs out to 12,000 AIC at the meter. If I install a simple 3r load center with a 22 k main breaker QOM2200VH and 10 K breakers ( HOM ) with a max of 60 A breaker, does the series rating of the main 200 A brkr protect the 10 k aic breakers ? The load center comes as a set with a few breakers, making it a very economical job.. ( outdoor load center Sq D HOM3060M200PRBVP ). For a slot store, though I may add a surge suppressor...Thanx, dhsvcs

Okay, let's break down this scenario and address your question regarding series ratings and the suitability of your proposed equipment.

Understanding the Situation Transformer to Meter

You have a transformer feeding a 200A meter via 80 feet of 4/0 CU conductor.


Available Fault Current

The calculated available fault current at the meter is 12,000 AIC (12 kA).

Meter to Panel

The meter feeds a 200A, 30-space, 60-circuit HomeLine load center (panelboard).


Proposed Load Center/Panelboard

You are considering a Square D HOM3060M200PRBVP outdoor load center which has:

QOM2200VH Main Breaker

This is a 200A main breaker with a 22,000 AIC (22 kA) interrupting rating.


HOM Branch Breakers

These breakers have a 10,000 AIC (10 kA) interrupting rating, and the max breaker you will use is a 60 A unit.

The Question: Series Ratings


You're asking if the 22 kA main breaker (QOM2200VH) "protects" the 10 kA branch breakers (HOM) in the event of a fault current higher than 10 kA, but less than 22 kA. The answer is only yes if the panel is tested and labeled to have a series rating.Key Concepts and Considerations1. Interrupting Rating (AIC)

This is the maximum fault current a breaker can safely interrupt without failing catastrophically. It's a critical safety factor.2.

Available Fault Current

This is the amount of current that could flow during a short circuit at a specific point in your electrical system. It depends on the transformer size, impedance, conductor size, length, and utility source impedance.3.

Series Ratings

A series rating means that the combination of a specific upstream breaker (in this case, the main breaker) and specific downstream breakers (the branch breakers) have been tested as a unit and certified to interrupt fault currents higher than the individual interrupting rating of the downstream breakers. The manufacturer must list the breakers that are compatible and the series rating that applies. This testing is rigorous and expensive.

Analysis of Your Situation
Fault Current vs. Branch Breaker Rating

The available fault current at the meter is 12 kA. Without a series rating, your 10 kA HOM branch breakers would be underrated.


Fault Current vs. Main Breaker Rating

The 22 kA main breaker alone is sufficient.

Series Rating Necessity

Since you've stated the calculated fault current is 12kA, it is greater than the interrupting rating of the HOM breakers, so without a valid series rating that shows that panel can handle the 12kA you
cannot use this panel as intended with just the HOM breakers.

Here's how to address the situation


Verify Series Rating

The most important step!

Carefully check the load center's (panelboard's) labeling and the manufacturer's specifications (Square D) to see if there is a valid, listed series rating for the QOM2200VH main breaker and the HOM branch breakers
specifically for the available fault current at your location (12 kA).
This information is usually found on a sticker inside the panel, or in Square D's documentation. You can also search the UL website for the specific panel model number and see if they have listed the series ratings that apply to it. If a series rating exists

Make sure it is equal to or greater than the available fault current (12 kA). You must use exactly the breakers specified in the series rating (manufacturer and model number). You'll have to document this clearly.

If NO series rating exists, or it does not cover the available fault current

You cannot use this combination of breakers without violating the NEC.2.

Alternative Solutions if NO Series Rating



Use Higher AIC Branch Breakers

Replace the 10 kA HOM breakers with breakers that have a higher AIC rating (e.g., 22 kA). This will be the most straight forward solution.

Current Limiting Breaker

Consider using a current-limiting main breaker (if available) that would reduce the let-through current to a level that the 10 kA branch breakers can safely handle. This needs to be carefully evaluated and documented.


Increase Conductor Size

Increasing the size of the conductors between the transformer and the meter might reduce the available fault current at the meter, but this is unlikely to make a significant difference over only 80 feet. It would need to be recalculated.

Add a Fault Current Limiting Device

Install a fault current limiting device (like a fuse or reactor) upstream of the panel. This is a more complex solution.


Replace the Panel

Choose a load center with a main breaker and branch breakers that all have an interrupting rating of at least 12kA.

Important Considerations
NEC Compliance

Article 110.9 of the National Electrical Code (NEC) requires equipment to have an interrupting rating sufficient for the available fault current at its terminals. Article 110.3(B) also requires that equipment be installed and used according to its listing and labeling.


Safety

Underrating breakers is a serious safety hazard that could lead to equipment failure, fire, or injury.

Documentation

Keep detailed records of your fault current calculations, selected equipment, and any series ratings you are relying on. This is important for inspections and future maintenance.

Surge Suppressor

Adding a surge suppressor is a good idea, especially in residential applications. Make sure it's properly rated for your voltage and current. A whole-house surge suppressor is recommended.

In Summary


The QOM2200VH main breaker itself
can handle the fault current. However, you cannot rely on that main breaker to "protect" the 10 kA branch breakers unless the panel is specifically listed with a series rating for that combination of breakers that is equal to or greater than the available fault current. If no series rating exists, you must* use branch breakers with a higher AIC rating or implement one of the other solutions to ensure safety and NEC compliance. Double-check the panel's labeling and Square D's documentation to confirm the series rating before proceeding. If there is no series rating use breakers that have a 22 kAIC rating. This is for compliance and safety. Flag for review

Previous Question Next Question