User: 618electrician, Location: St. Louis
Asked on: Monday, August 4, 2025 at 4:16 pm EDT
Answered on: Monday, August 4, 2025 at 4:16 pm EDT
Question: ON a commercial building' new service 2020 NEC do i need a grounded bridge and a surge protector . ????????????????????????????????????????????????????????
Let's break this down according to the 2020 NEC.
Grounded (Main Bonding) Jumper
Yes, you absolutely need a grounded (main bonding) jumper. This is a fundamental requirement for grounding the electrical system. The main bonding jumper connects the equipment grounding conductor (EGC) to the grounded conductor (neutral) at the service equipment. This creates a low-impedance path for fault current back to the source, allowing overcurrent protective devices (like circuit breakers) to trip and clear a fault. NEC Article 250 covers grounding and bonding requirements. Section 250.24(C) specifically addresses the connection of the grounded conductor to the grounding electrode. Section 250.28 covers the main bonding jumper in detail. Purpose
Safety! It's critical for safety during a fault condition. Without it, dangerous voltages could appear on metal parts of the electrical system.
Surge Protective Device (SPD)
2020 NEC Article 230.67 requires surge protection for all services supplying dwelling units. This means that a surge protector is required for dwelling units. The same surge protection requirements do not extend to commercial buildings. However, it is still good practice to install an SPD on a commercial building's new service.
Summary Grounded (Main Bonding) Jumper
Required by NEC Article 250.
Surge Protective Device (SPD)
Not strictly required by the 2020 NEC for commercial buildings.
Important Considerations
Local Amendments
Be aware that your local jurisdiction (city, county, or state) might have amendments to the NEC. These amendments could make surge protection mandatory for commercial buildings in your area. Always check with your local electrical inspector.
Equipment Sensitivity
Consider the types of equipment that will be used in the commercial building. Buildings with sensitive electronic equipment (computers, servers, medical equipment, etc.) would benefit significantly from surge protection.
Cost vs. Benefit
Evaluate the cost of installing surge protection compared to the potential cost of damage from surges. A properly installed SPD can prevent costly damage to equipment.
Types of SPDs
There are different types of SPDs, including Type 1, Type 2, and Type 3. The type of SPD you need will depend on the location of the SPD in the electrical system.
Disclaimer: This information is for general guidance only. It is essential to consult the latest edition of the NEC, all applicable local codes and regulations, and to consult with a qualified and licensed electrician to ensure compliance and safety for your specific installation. I am an AI Chatbot and not an electrician or code official. This is not a substitute for professional advice. Flag for review