Question: Hey guys, my client wants me to go Indiana (12 hours away) to finish a 400 kw generator install. Just trying to get a rough game plan. As you can see, it's a 2000A Siemens switchboard with a Pringle switch. Anyone happen to be familiar with these Siemens switchboards? Questions:1. Is there metering below the service disconnect ? Doesn't seem like there's much room under there. There is an instrument meter on the exterior so it's definitely not metered at the transformer spades.2. Any idea what fuse type this is likely to have? Service is 120/208 I suspect this is grossly oversized and may down grade it to make it easier.3. Transfer switch is not service rated. Would have to intercept load side bussing. Can't think of anything else to do besides remove bussing between the load side of the switch and the distribution section and put lugs on. Seems like this isn't an uncommon thing, how is this typically done? Do manufacturers offer kits for this?Thanks

Okay, let's break down this Indiana generator install and address your questions. Going in prepared is crucial for a smooth, safe, and cost-effective project.

General Considerations Before You Start



Single Line Diagram

Absolutely essential. Get one from your client
before you travel. It will save you hours on site and help prevent mistakes.

Siemens Documentation

Call Siemens Technical Support directly. Have the switchboard model and serial number ready. They can often provide drawings, schematics, and maintenance manuals. They will likely ask about AIC ratings, available fault current.

Safety

This is a
live switchboard. Wear proper PPE, including arc-flash rated clothing, gloves, and face shield. Ensure you have a qualified spotter and a documented lockout/tagout procedure. Verify equipment grounding.

Permits & Inspections

Confirm all necessary permits are in place and the local inspector's requirements. Ask your client.

Load Bank Test

Plan for a load bank test after the generator is installed. This verifies the generator's performance under load and helps identify any potential issues.


Commissioning

Ensure proper commissioning of the generator and transfer switch, including setting all parameters according to manufacturer specifications.

Communication

Maintain clear communication with your client and any other contractors involved in the project.


Coordination Study:
Is a new coordination study needed due to the addition of a generator? AIC Study: Is a new AIC study needed?Addressing Your Questions


Metering Location



Limited Space

You're right, space under the service disconnect in these older Siemens boards can be tight.

External Metering

The external meter is a strong indicator that the utility metering point is upstream of the service disconnect, possibly at the transformer. This is common.


Internal CTs (Current Transformers)

Look closely inside the switchboard above and below the service disconnect. There may be current transformers (CTs) already installed for the external meter. These are donut-shaped devices that clamp around the busbars. If present, these CTs are feeding the external meter. It's less likely that there is another set of CTs below the main disconnect.

If Not Metered Below

If there's no metering below the main disconnect, the client will need to add it if they want to measure generator output. This will require adding a metering module
within the switchboard or installing a separate metering cabinet.2.

Fuse Type and Sizing



Physical Inspection

The only way to know for sure is to open the Pringle switch (when de-energized!) and read the fuse labels.

Common Fuse Types

Typical fuses for this type of service could be:


Class L

Large, bolted fuses for high ampacity.

Class RK1 or RK5

Cartridge-style fuses with higher interrupting ratings.


Class J

More compact cartridge fuses with good interrupting ratings.

Oversizing

It's
very common for fuses to be oversized. This is often done to prevent nuisance tripping, but it defeats the purpose of overcurrent protection.

Downsizing Considerations



Calculate Load

Perform a
thorough load calculation based on the connected equipment.

NEC Requirements

Adhere to NEC Article 240 for overcurrent protection requirements.

Coordination Study

A coordination study is crucial before downsizing fuses. This ensures that the fuses will properly coordinate with downstream protective devices (circuit breakers) in the distribution panel(s). Without coordination, you could have a cascading failure where the main fuses blow instead of a branch circuit breaker.


Fuse Amperage Rating
: The fuse amperage rating must be equal or greater than the available fault current. Fuse Type: Fuse type is crucial, and you should not change fuse types without knowing the reason why the present fuse type was selected. Labeling: Fuse labeling must include the amperage, voltage, interrupting rating, fuse class, and any other relevant information. Document

Keep meticulous records of any changes to fuse sizes or types.3.

Transfer Switch Installation (Non-Service Rated)



Interception on Load Side

You are correct, intercepting the load-side bussing is the standard approach when a non-service-rated transfer switch is used.

Methods



Bussing Removal and Lugs

This is the most common method.1.

Isolate

Completely de-energize and lockout/tagout the entire switchboard. Double-check with a meter.2.

Remove Bussing

Carefully remove the section of bussing between the Pringle switch and the distribution section.3.

Drill and Tap

Drill and tap the remaining bussing to accept appropriately sized lugs. The lug size must match the wire size of the transfer switch output conductors.4.

Install Lugs

Install high-quality lugs and torque them to the manufacturer's specifications.5.

Connect to Transfer Switch

Connect the transfer switch output conductors to the lugs.

Mechanical Tap Connectors (e.g., Polaris Connectors)

Less desirable, as they may take up more space. It is important to ensure all electrical connections are properly torque when using mechanical tap connectors.


Bus Duct Tap Boxes

If there is a readily available space and the existing busbar configuration allows, you could install a bus duct tap box to connect the transfer switch. The tap box provides a safe and code-compliant way to tap into the existing busbars.

Manufacturer Kits

Sometimes manufacturers offer kits for specific switchboard models, but they are rare, especially for older equipment. Call Siemens and ask! They might have suggestions or even an obsolete part that can help.

Custom Fabrication

In some cases, a custom busbar adapter may need to be fabricated by a qualified metal shop.

Important Considerations



Ampacity

Ensure the lugs, connectors, and wiring are all rated for the full ampacity of the generator output.

Clearances

Maintain proper clearances within the switchboard.


Support

Provide adequate support for the new conductors and any additional components.

Professionalism

The finished installation should look clean, professional, and meet all applicable codes.


UL Listing
: Any modifications to the switchboard may void the UL listing, so be sure to verify with Siemens. Torque: Use torque wrenches and torque every connection to the manufacturer's specifications. Thermography Inspection: After the system has been energized and under load, perform a thermography (infrared) scan of all connections to identify any hot spots that may indicate loose or improperly made connections.

Additional Tips



Take Pictures

Document
everything with pictures before you start. This will be invaluable for reassembly and troubleshooting.

Bring Extra Parts

Carry a selection of commonly used lugs, connectors, and hardware. A trip to a supply house 12 hours away is a killer.

Plan for the Unexpected

Be prepared for unforeseen issues, such as damaged equipment or unexpected wiring configurations.


Contingency Plan

What happens if you can't get the generator online and have to leave? How will you leave the site?*

Sleep
: Driving 12 hours and working the same day is a bad idea. Plan to sleep.This is a complex project, so take your time, plan carefully, and prioritize safety. Good luck in Indiana! Flag for review