User: AC\DC, Location: Florence,Oregon,Lane
Asked on: Wednesday, August 6, 2025 at 1:54 pm EDT
Answered on: Wednesday, August 6, 2025 at 1:54 pm EDT
Question: Attached is a diagram—— the fire alarm told me shut trip and fire alarm are reversed—- I have not made it out to see what the guys landed. But 5-9 should be the 120 volt shut trip - and the power monitoring should be 1 and7 since it’s just a contact that drops off once shut trips to then trigger alarm
Okay, I understand the situation. Based on your description and the diagram you provided (which I cannot see directly, but I'm relying on your description of it), here's a breakdown of what you're saying and what to check
Your Claim:
The fire alarm system is reporting that the "Shut Trip" and "Fire Alarm" wiring connections are reversed. Terminals 5 & 9 should be connected to the 120V Shut Trip. (This is the circuit that, when energized, holds the shutoff device open and when de-energized closes the shutoff device.) Terminals 1 & 7 should be connected to the Power Monitoring/Fire Alarm signal. (This is a normally closed contact that opens when the shut trip circuit de-energizes, indicating a fire alarm condition. This opening then triggers the fire alarm system.)Understanding the Logic Shut Trip (120V)
The shut trip solenoid/device requires 120V to stay open (holding the system in a normal, running state). When this power is removed (due to a fire alarm or other emergency), the solenoid/device releases and the system shuts down.
Power Monitoring (Fire Alarm Signal)
The fire alarm system monitors the 120V shut trip circuit indirectly. It does not directly see the 120V. It uses a
normally closed contact that's wired to open when the 120V shut trip circuit is de-energized. This opening signals the fire alarm system that a shut-down event has occurred (presumably due to a fire).
Troubleshooting Steps (Assuming You Can Access the Wiring)1. Verify 120V at Terminals 5 & 9
Use a multimeter to carefully measure the voltage between terminals 5 and 9. You should see 120VAC (or whatever the specified shut trip voltage is). If you DON'T see 120V
Check the breaker or fuse feeding the 120V shut trip circuit. Is it tripped or blown? Verify the power is present at the source feeding terminals 5 & 9. Work back through the wiring to find where the power is lost.
If you DO see 120V
Proceed to the next step.2.
Simulate a Shut Trip and Verify Alarm Signal
Carefully disconnect the 120V wiring from terminals 5 & 9 (SAFELY!) This simulates the shut trip de-energizing. Be prepared for the system to shut down.
Check the fire alarm system's panel
Does it now indicate a fire alarm or shut-down condition? If not, there's a problem with the wiring or the signaling contact.
With the 120V wiring disconnected, use an ohmmeter to check the continuity between terminals 1 and 7. You should see an open circuit (very high resistance) indicating the contact has opened. If you still see a closed circuit (very low resistance), the contact isn't working properly. It may be stuck closed.3.
Verify Continuity When Shut Trip is Energized
Reconnect the 120V wiring to terminals 5 & 9. The system should return to its normal running state.
With the 120V wiring connected, use an ohmmeter to check the continuity between terminals 1 and 7. You should see a closed circuit (very low resistance) indicating the contact is closed in the normal state. If you see an open circuit now, the contact is not properly closed in the normal state.4.
Confirm Wiring Based on Testing
Based on the results of the above tests, determine if the wires are indeed reversed.
If they are reversed, carefully swap the wiring connections so that: Terminals 5 & 9 are connected to the 120V shut trip. Terminals 1 & 7 are connected to the fire alarm system's input that monitors the shut trip status.5.
Test After Correction
After correcting the wiring, repeat steps 2 and 3 to confirm that the fire alarm system now correctly signals a fire alarm when the shut trip circuit is de-energized.
Important Safety Notes
Lockout/Tagout
Before working on any electrical circuits, ALWAYS follow proper lockout/tagout procedures to ensure the circuit is de-energized and cannot be accidentally energized.
Qualified Personnel
This troubleshooting should be performed by qualified and experienced electricians or technicians who understand electrical safety and the operation of fire alarm and shut trip systems.
Live Circuits
Be extremely careful when working near live circuits. Use appropriate PPE (personal protective equipment) and tools.
Documentation
Consult the system's documentation (wiring diagrams, manuals) to confirm the correct wiring connections.
Fire Alarm System Testing
After any changes, fully test the fire alarm system to ensure it is functioning correctly and that all alarm signals are being received properly. This often involves a formal fire alarm inspection and certification.
Communication
Communicate clearly with the fire alarm monitoring company and the facility's maintenance team throughout the troubleshooting and repair process.
In summary: The key is to systematically verify the voltage at the shut trip terminals, simulate a shut trip, and confirm that the power monitoring/fire alarm contacts are behaving as expected (normally closed, opening when the shut trip de-energizes). The ohmmeter is your friend! Good luck! Flag for review