User: bcbeaver, Location: BC
Asked on: Wednesday, August 6, 2025 at 2:11 pm EDT
Answered on: Wednesday, August 6, 2025 at 2:12 pm EDT
Question: I have an MCC bucket with a 100A breaker & size 3 starter. I have a temporary piece of equipment with MOCP of 80A. Would like to use the existing bucket. Can I size the conductor from MCC to fused disconnect to the equipment MCA with a fused disconnect & 80A fuses located at equipment? Or do I need 100A cable from MCC to fused disc?
Okay, let's break down the NEC requirements for this situation and determine the best and safest approach.
Understanding the Requirements
MCC Bucket
You have an existing MCC bucket with a 100A breaker and a Size 3 starter. This means the bucket is already wired to handle at least 100A continuous.
Temporary Equipment
You have temporary equipment with a Maximum Overcurrent Protection (MOCP) of 80A. This is the maximum fuse or breaker size the equipment manufacturer allows for protecting the equipment. You'll also need the Minimum Circuit Ampacity (MCA) for the equipment. The MCA is the calculated minimum ampacity the conductors feeding the equipment must have.
Key NEC Sections
NEC 430 (Motors, Motor Circuits, and Controllers)
While your equipment may not be exclusively a motor, the principles of motor protection often apply or are used as a guide when dealing with equipment with significant motor loads.
NEC 240 (Overcurrent Protection)
Deals with overcurrent protection for conductors and equipment.
NEC 310 (Conductors for General Wiring)
Deals with conductor ampacity and allowable uses.
NEC 110 (Requirements for Electrical Installations)
General requirements for safety and proper installation.
Analysis and Options
Here's a breakdown of the legality and best practices:1.
Conductor Ampacity from MCC to Fused Disconnect
Minimum Requirement
You MUST size the conductors from the MCC bucket to the fused disconnect based on the larger of the following: The MCA of the equipment. 125% of the motor's full-load current (if a motor-driven piece of equipment) plus the full-load currents of other loads in the equipment. Remember conductors shall be sized to carry the load, but never less than 125% of the continuous load (3-hr or more)
Why Not Just Use the MOCP (80A)? The MOCP is for equipment protection, not necessarily conductor protection. The conductors need to be sized to handle the expected continuous load plus a safety margin. Example
Let's say your equipment has an MCA of 60A. Then, the conductors must be rated for at least 60A.2.
Fused Disconnect at the Equipment
Fused Disconnect's Purpose
The fused disconnect serves two primary purposes: Overcurrent Protection for the Equipment: It provides the specific overcurrent protection required by the equipment manufacturer (the 80A MOCP in your case). Disconnecting Means: It provides a way to safely disconnect power to the equipment for maintenance and troubleshooting.
Fuse Size
You would use fuses rated at no more than the MOCP of the equipment (80A in your case). You can use a lower fuse rating if appropriate based on the actual load and the equipment manufacturer's recommendations.3.
MCC Bucket Breaker (100A)
Acceptable
The 100A breaker in the MCC bucket is generally acceptable if the conductors from the bucket to the fused disconnect are sized appropriately (as discussed above). The 100A breaker provides overcurrent protection for the conductors feeding the equipment.
Exception
If your calculated conductor ampacity requires you to use conductors that are significantly smaller than what is protected by a 100A breaker, there could be a violation of the conductor protection rules. For instance, if you're running a very short run of cable from the MCC to the disconnect (less than 10 feet), you may need to consider a smaller breaker to adequately protect the conductors.
Practical Steps and Recommendations
Determine the MCA
First and foremost, find the equipment's Minimum Circuit Ampacity (MCA). This is crucial! This information should be on the equipment's nameplate or in its documentation.2.
Calculate Conductor Ampacity
Based on the MCA, calculate the required conductor ampacity, considering any additional loads. Ensure the conductors are sized to handle the continuous load safely (at least 125% of the continuous load).3.
Select Conductor Size
Choose a conductor size with an ampacity rating equal to or greater than the calculated ampacity. Consult NEC Table 310.16 (or the appropriate table for your conductor type) for ampacity values. Consider any derating factors due to ambient temperature, conduit fill, etc.
4.
Install Fused Disconnect
Install a fused disconnect at the equipment location.5.
Install Correct Fuses
Install fuses in the disconnect rated at or below the equipment's MOCP (80A).6.
Document Everything
Keep a record of your calculations, conductor size, fuse ratings, and any derating factors used.
Answer to Your Specific Question
You CANNOT simply size the conductor to the equipment's MCA without considering the 125% continuous load rule. The cable needs to be able to handle 125% of the continuous load. You do NOT necessarily need 100A cable from the MCC to the fused disconnect if a lower ampacity is sufficient based on your calculations, and if the conductors are properly protected by the 100A breaker.Example Calculation
Let's say: Equipment MCA = 60A There is no continuous load.Then: Conductor Size: You would need to choose conductors rated for at least 60A. Depending on the conductor type (e.g., THHN), this might require a #6 AWG copper conductor.
Important Considerations
Temporary vs. Permanent
While this is a temporary setup, it MUST still meet all applicable NEC requirements for safety.
Qualified Personnel
This work should be performed by qualified electrical personnel who are familiar with the NEC and local electrical codes.
Inspection
Consider having the installation inspected by a qualified electrical inspector to ensure compliance.
Safety
Always de-energize circuits before working on them and follow proper lockout/tagout procedures.
In summary, prioritize conductor sizing based on the calculated load, including the 125% factor, and then choose the appropriate MOCP fuses to protect the equipment. The 100A breaker in the MCC bucket may* be acceptable, but ensure the conductors are adequately protected. Flag for review