Question: I have a customer who has an incoming three phase 12.47kV circuit (3 bare phase conductors on crossarms with a static/neutral below the phases) coming into the facility from the utility. The circuit passes through the utility metering point and becomes customer owned (premises wiring) at a customer owned recloser. The circuit (now customer owned) continues into the facility in the same configuration described above feeding many customer owned three phase transformers (with both delta and wye primary connections). There are also single phase transformers for lighting, recloser control power, etc fed by the 12.47kV circuit. It seems to me that the neutral/static is also functioning as the EGC (equipment ground conductor) back to the source. For example, there is no separate EGC for the recloser housing. I am working on a project for which I will be modifying this system and want to understand how this configuration fits into the NEC, especially article 250. I know outside the facility the utility is governed by NESC, but inside the facility NEC is the governing standard. What article in NEC (2023 please) allows for this grounding configuration for a medium voltage pole line circuit?Please let me know if I need to provide further details or clarity.
You've hit on a critical point regarding the transition from utility-regulated NESC to NEC-regulated premises wiring. Let's break down how the NEC 2023 likely applies to this situation, focusing on Article 250.
Key Concepts & How They Apply Premises Wiring
Once the service conductors pass through the customer recloser, they become premises wiring and fall under the jurisdiction of the NEC. (NEC Article 90.2)
Service Point
The NEC considers the connection point on the line side of the utility metering equipment as the service point. This is typically where ownership and responsibility transfer.
Grounded Conductor vs. Equipment Grounding Conductor (EGC)
It's essential to distinguish between the grounded conductor (often called the neutral) and the EGC. The grounded conductor carries neutral current and is intentionally grounded at the source. The EGC provides a low-impedance path for fault current back to the source, facilitating overcurrent device operation and minimizing touch potential. The EGC and neutral can be bonded together, but are not always the same thing.
Relevant NEC Articles (2023)1. Article 250.24 - Grounding Service-Supplied Alternating-Current Systems
This section governs how the service neutral (grounded conductor) must be grounded. It typically requires a grounding electrode system at the service. The grounding electrode system ensures that the grounded conductor is connected to earth, limiting voltage to ground. This is likely handled at the service entrance (recloser location in your case).
250.24(C)(1) - Grounding Electrode Conductor Connection
This covers where you connect the grounding electrode conductor (GEC) to the grounded conductor. It emphasizes that the GEC connection should be made at an accessible location.2.
Article 250.4(A)(1) - Electrical System Grounding
"Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation." This reinforces the need for effective grounding.3.
Article 250.90 Use of Grounding Path
This section explains the path to ground, and refers you to article 250.4(A)(5).
4.
Article 250.4(A)(5) - Conductive Materials That Enclose Electrical Conductors or Equipment
This is a very important section. It states that conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path. This is the article that discusses the path of the EGC.5.
Article 250.184 - Grounding Methods for Alternating-Current Distribution Systems and Equipment. This article pertains to the customer equipment and distribution.6. Article 250.186 - Grounding of equipment on premises. This section allows the effectively grounded system neutral/grounded conductor to be used as the EGC if the conditions of 250.186(A) are met, and 250.186(B) is not violated.
Analysis of Your System
Based on your description, here's a potential interpretation: Neutral/Static Wire
The wire strung below the phase conductors is most likely the grounded conductor for the 12.47kV system. It may also be functioning as the EGC if it meets the requirements of 250.186.
Recloser Housing
If the recloser housing is bonded to the grounded conductor (neutral/static wire) and the grounded conductor is adequately grounded as per 250.24, the NEC may consider this acceptable if the grounded conductor meets the requirements of 250.186. However, it is important to understand if the grounded conductor is sized properly, has adequate fault withstand, etc.
Transformer Connections
Delta-Connected Transformers
With delta-connected primaries, you must have a separately derived system per NEC Article 250.20(D) if you're creating a grounded secondary. The rules of Article 250.30 then come into play for grounding the secondary side of the transformer. A bonding jumper between the transformer case and the grounded conductor is typical.
Wye-Connected Transformers
If you have a solidly grounded wye system you must ground the neutral point as outlined in 250.24 and 250.
20.
Key Questions to Investigate & Verify
Before modifying the system, you must answer these questions:1. Grounded Conductor Size & Integrity
Is the grounded conductor (neutral/static) sized appropriately for the available fault current? Does it have sufficient mechanical strength and fault withstand capability? This is critical. A poorly sized or damaged grounded conductor acting as the EGC is a significant safety hazard.2.
Grounding Electrode System
What is the grounding electrode system at the recloser location? Does it comply with 250.50 and 250.52? Is it adequately maintained?3.
Bonding
Are all metallic enclosures, equipment, and non-current-carrying metal parts properly bonded together and to the grounded conductor as per 250.92?4.
Separately Derived Systems (Delta Transformers)
If delta-wye transformers are used to establish a grounded secondary, is the grounding of the secondary done correctly as per 250.30? Are bonding jumpers installed and sized appropriately?5.
Documentation
Does the existing system have any documentation regarding grounding studies or fault current analysis?6.
Qualified Personnel
Was the original installation designed and installed by qualified personnel in accordance with applicable codes and standards?
Recommendations1. Consult a Qualified Engineer
This is not a DIY project. Engage a licensed professional engineer (PE) with expertise in power systems and grounding. They can perform a thorough analysis of the existing system, verify compliance with the NEC, and design any necessary modifications.2.
Grounding Study/Fault Current Analysis
Have the engineer conduct a grounding study and fault current analysis. This will determine the adequacy of the existing grounding system and identify any potential weaknesses.3.
Consider Dedicated EGC
Depending on the results of the grounding study and fault current analysis, it may be prudent to install a dedicated EGC in addition to the grounded conductor (neutral/static wire). This would provide a more reliable and robust grounding system, especially for critical equipment.4.
Improve Bonding
Ensure that all metallic enclosures and equipment are properly bonded together and to the grounding system.5.
Documentation
Document all changes to the grounding system, including the grounding study, fault current analysis, and details of any modifications made.
Caution: Never assume that an existing grounding system is adequate. Always verify compliance with the NEC and best engineering practices.* Improper grounding can lead to electrical hazards, equipment damage, and even life-threatening situations.By carefully examining the existing system, consulting with a qualified engineer, and implementing appropriate grounding practices, you can ensure that your project is safe, reliable, and compliant with the NEC. Flag for review