Topic: Generator factory wiring

User: wallacewayne, Location: Texas

Asked on: Wednesday, August 6, 2025 at 8:21 pm EDT
Answered on: Wednesday, August 6, 2025 at 8:22 pm EDT

Question: I bought a used older 11 kw generac generator and noticed that the conductors feeding the 50 amp breaker looked to be very small. Like #10 at most...maybe even smaller. Is this normal?Thank you

No, that is absolutely NOT normal and is a significant fire hazard. You should correct this immediately.Here's why: 11kW Generator Output

An 11kW generator at 240V can produce a substantial amount of current. To determine the approximate current, we can use the following calculation:
Watts / Volts = Amps 11,000 Watts / 240 Volts = Approximately 45.8 Amps (This is a simplified calculation; the actual current may be slightly higher depending on the generator's power factor)

Breaker Size

A 50-amp breaker is designed to protect the circuit from overcurrent. This means it's intended to trip and disconnect the circuit if the current exceeds 50 amps for a sustained period.

Wire Ampacity

Wire ampacity refers to the maximum amount of current a conductor can safely carry without overheating. #10 AWG copper wire typically has an ampacity of only around 30-40 amps, depending on the insulation type and installation conditions. #12 is even less, around 20-25amps.


The Problem

If the generator is actually producing close to its rated output, the #10 (or smaller) wire will be overloaded. This can lead to:

Overheating

The wires will get hot. This heat can melt the insulation, creating a short circuit.


Fire Hazard

Melted insulation and short circuits are a major fire hazard.

Voltage Drop

The undersized wires will cause a significant voltage drop, especially under heavy load. This can damage connected appliances and equipment.


Nuisance Tripping

The breaker may trip frequently, even if the generator isn't fully loaded, due to the increased heat in the wiring.

What to Do


Immediately Stop Using the Generator

Do not operate the generator until the wiring issue is corrected.2.

Consult a Qualified Electrician

You absolutely need a licensed and experienced electrician to assess the situation and make the necessary repairs.3.

Wire Size Calculation

The electrician will calculate the appropriate wire size based on the generator's output, the breaker size, and the distance of the run. For a 50-amp breaker, you'll likely need at least #6 AWG copper wire, and potentially #4 AWG depending on distance and local codes. The electrician should consult the National Electrical Code (NEC) or local electrical codes to determine the correct size.4.

Inspect the Wiring

The electrician should carefully inspect the entire wiring run for any signs of damage, overheating, or improper connections.5.

Proper Installation

Ensure that the wiring is properly installed in conduit or raceways (as required by code) and that all connections are tight and secure.

Important Considerations



Aluminum Wire

If aluminum wire is used, it must be sized larger than copper for the same ampacity. An electrician can determine the proper aluminum wire size.

Conduit Fill

Be mindful of conduit fill requirements. You can't stuff too many wires into a conduit, as this can reduce the wires' ability to dissipate heat.


Grounding

Ensure proper grounding of the generator and the electrical system.*

Local Codes

Electrical codes vary by location. Ensure that the installation complies with all applicable local codes and regulations.

In summary, the undersized wiring is a serious safety hazard. Get a qualified electrician involved immediately to correct the problem before you use the generator.