Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Series breakers aic fault clearing

User: Cartoon1, Location: Florida

Asked on: Thursday, August 7, 2025 at 7:23 pm EDT
Answered on: Thursday, August 7, 2025 at 7:37 pm EDT

Question: This area always confused me. The area that confuses me is typically the 3rd breaker. Example below:A: Meter Center with 1600A main service breaker rated 65KAICB: Meters connected with each having 225A breaker rated 22KAICC: Panel being fed from the meter breaker rated 225A MLO, with 10KAIC branch breakers feeding a unit about lets says 50feet away.Question 1: Lets assume 1600A main breaker 'A' is series rated with 225A meter breaker 'B'. Does branch breakers 'C' need to the be also series rated or is that a moot point, since the 10KAIC breaker could technically be anything (assuming there was lower than 5kaic? The 'A' and 'B' will clear out any fault before it gets to 'C'?Question 2: Typically if it is the same manufacturer, for example square 'D'. They have the EZ meter centers, and homeline panels MLO that you connect to in tenants condos type building. Do they all automatically get series rated? The 'A' 'B' and the branch breakers 'C'?Thank you

You've hit on a complex and often misunderstood area of electrical design. Let's break it down with your specific example

Understanding Series Ratings (Short-Circuit Current Rating, SCCR)

Series ratings are about ensuring that a downstream device (like a breaker in panel C) can safely withstand the let-through energy of a fault even if it's theoretically insufficient to interrupt the fault current on its own. It relies on the upstream devices (A and B) to clear the fault faster and with less energy than the downstream device could handle independently.

Question 1: Branch Breakers 'C' and Series Rating Yes, Branch Breakers Need Consideration

The fact that A and B are series rated does
not automatically mean the 10kAIC branch breakers at C are safe. Here's why:

Let-Through Energy Matters

While A and B are supposed to interrupt the fault, they do so after letting some amount of fault current pass through. The branch breakers in panel C still need to be able to withstand that let-through energy. A 10kAIC breaker might not be adequate if the fault current let through by A and B exceeds its withstand capability.

Panel C SCCR

The
entire panel C needs an SCCR at least as high as the available fault current at its line terminals. The lowest-rated component in the panel usually dictates the overall panel SCCR (unless specific tested and listed assemblies exist).

Not a Moot Point

Even if A and B will eventually clear the fault, the immediate surge of current could damage or destroy the 10kAIC breakers in C if they are not rated for the let-through energy.

Higher than 5kAIC

The comment of being technically be anything (assuming there was lower than 5kaic), this is irrelevant as the 10kAIC rating could be severely lower than the KAIC being let-through.


How to Address It


Determine the Available Fault Current

You must calculate or determine the available fault current at the line terminals of panel C (the point where the wires from the meter breaker B land). This requires calculations based on transformer impedance, conductor lengths, and other system parameters.2.

Verify SCCR

Ensure the SCCR of panel C (determined by the lowest-rated component, which may be those 10kAIC breakers) is greater than or equal to the available fault current at its line terminals.3.

Series Rating Tables (or Engineering Judgment)

If the available fault current exceeds the SCCR of Panel C, you may need to use: Manufacturer series rating tables: These tables provide specific combinations of upstream and downstream devices that are tested and listed for series rating. Find a combination where the upstream devices (A and B) are series-rated with downstream devices that include breakers rated at 10kAIC (or the actual rating you have). If manufacturer series ratings are not available, you may have to upsize the breaker at 'C' to a higher KAIC value, but this may cause issues with not being able to fit in the breakers. Consult with an Electrical Engineer with appropriate knowledge and experience.

Question 2: Square D EZ Meter Centers and Homeline Panels
Not Automatic, But Likely

Just because Square D makes both doesn't guarantee automatic series ratings. However, Square D (and other manufacturers) often
design these systems to be series rated to save costs and space.

Key is Documentation

You must consult Square D's documentation (specifically, their series rating tables) to confirm that the specific combination of breakers (A, B, and breakers in panel C) are listed for series rating. Don't assume anything!

Where to Find Series Ratings

Look for:


Square D Digest

This is a comprehensive catalog with series rating information.

Square D Technical Bulletins

They often publish specific bulletins on series ratings.


Square D's Website

They typically have online tools and documentation.

If No Series Rating

If you can't find a listed series rating for your specific configuration, you have the following options:1.

Increase Branch Breaker KAIC

Replace the 10kAIC breakers in panel C with breakers having a higher interrupting rating (e.g., 22kAIC) that matches or exceeds the available fault current at that panel.2.

Current Limiting Devices

Install current-limiting fuses or breakers upstream of Panel C to reduce the available fault current to a level the 10kAIC breakers can handle. This might involve changing the meter breaker B.3.

Change the Panel C.
Consider a Panel with Higher SCCR rating, you may have to upsize the panel as well as the branch breakers, which will result in a costly solution.

Important Considerations and Best Practices



Available Fault Current Calculation is Critical

Don't guess! Accurately calculate the available fault current at each point in the system.

Documentation is Paramount

Keep all series rating documentation (manufacturer tables, engineering calculations) for future reference and inspections.


Consult an Electrical Engineer

For complex projects or when in doubt, consult a qualified electrical engineer. They can perform the necessary calculations and ensure a safe and code-compliant design.

NEC Requirements

NEC Article 110.9 and 110.10 cover interrupting rating and fault current calculations. Make sure your design complies with these requirements.


Field Labeling:
When a series rating is used, NEC 110.22 requires that the equipment be clearly labeled to indicate the specific series combination used.In summary, don't assume series rating just because devices are from the same manufacturer. Verify with manufacturer documentation, perform fault current calculations, and consult with a professional when needed. The goal is to ensure that every component in your electrical system can safely withstand the available fault current. Flag for review

Previous Question Next Question